motor

11/15/2007 1:27 AM

why Neutral is not used in motor?

Pls send an answer as early as possible

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: motor

11/15/2007 2:44 AM

In a single phase motor you required neutral.

In a 3 phase motor you don't required natural, due to vector sum of 3 phase is zero. Hence there is no return path required.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: motor

11/15/2007 4:50 AM

A 3-phase motor connected in 'delta' does not need a neutral wire. If it were connected in 'star' then a neutral wire would be needed.

http://en.wikipedia.org/wiki/Three-phase_electric_power

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#3
In reply to #2

Re: motor

11/15/2007 11:19 AM

<in 'star' then a neutral wire would be needed.>

STAR POINT IS INTERNAL.

Neutral is not connected to any motor I have seen.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#4
In reply to #2

Re: motor

11/15/2007 11:28 AM

I must respectfully disagree with you on this one. Even when a motor is connected in star configuration, no neutral wire is required. The phase windings are connected at the center of the star, but no external connection is needed at this point. In fact, most industrial motor control centers are supplied by a transformer using a delta-connected secondary, eliminating the possibility of a neutral connection.

The purpose of the neutral conductor in a 3 phase system is to provide a return path for imbalance of the current in the phase conductors. There will be no significant imbalance in a properly operating motor, as the winding configuration provides uniform field density through 360° of rotation. If there were a phase current imbalance (due to a bad connection, winding, etc), the motor would experience unbalanced torque, resulting in improper operation and possible damage.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Commentator
Egypt - Member - Ahmad Samak

Join Date: Sep 2007
Location: Alexandria, Egypt
Posts: 86
Good Answers: 1
#6
In reply to #2

Re: motor

11/15/2007 4:54 PM

As post 3 and 4

Neutral is not connected to any motor I have seen.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#5

Re: motor

11/15/2007 12:22 PM

Depends on what type of motor you are referring to.A lv 3 phase motor can run on Delta so no neutral is required. In HT motors which almost always have their stator in star connection have a separate terminal box for neutral which is brought out.In star connected lv motor neutral normally not brought out.having a neutral depends upon the type of winding connection and whether required to be brought out depends upon the degree of protection.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply Score 1 for Good Answer
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); MUKULMAHANT (1); nesubra (1); pwr2thepeople (1); PWSlack (1); Samak (1)

Previous in Forum: VFD's and Cabling   Next in Forum: Temperature Rise within a Switchboard: How to Derive a Formula?

Advertisement