02/16/2021 3:05 AM
What is Step Load / Step kVA in DG sets?
Re: Step Load / Step kVA in DG Sets
02/16/2021 6:53 AM
This refers to how sensitive your equipment is to voltage/frequency dip on start-up...In choosing a generator it's important to take into account the starting requirements of the types of loads you will be supplying...
"Maximum Allowable Step Voltage Dip...
Since a generator set is a limited power source, voltage and frequency excursions will occur during transient loading events. The key is to select a generator set size that will limit these excursions to an acceptable level for proper load performance. As the maximum allowable starting voltage dip is reduced, the size of the recommended generator set increases.
If the maximum allowable starting voltage dip is less than 15%, the recommended generator set may be very large for the connected load. Some loads are more sensitive to voltage dip than others.
It is recommended to choose the most sensitive load in your project to establish the maximum allowable voltage dip while the loads are starting.
Note that for the majority of loads, maximum allowable voltage dip defaults at 35%. For North America, the maximum allowable peak voltage dip for fire pump loads defaults at a fixed 15%, and for medical imaging loads it defaults at a fixed 10%.
See also Loads Overview.
Maximum Allowable Step Frequency Dip
Since a generator set is a limited power source, voltage and frequency excursions will occur during transient loading events. The key is to select a generator set size that will limit these excursions to an acceptable level for proper load performance. As the maximum allowable frequency dip is reduced, the size of the recommended generator set increases. If assigning an overall maximum allowable frequency dip for the project in the project parameters, choose the load most sensitive to frequency dips to set the maximum allowable frequency dip.
https://powersuite.cummins.com/PS5/PS5Content/HTML/common/Binary_Asset/docs/PowerSuite5.pdf
02/16/2021 3:49 PM
Matthew 7, 7.