Hi..
I'm working in a new facility plant, and i have a constant problem with my HVAC control system. Let me describe my situation a bit.
In my plant, there are a 2 AHU system that serves the office area, lets call it AHU#1 & 2; an another 1 AHU#3 serves the Mirco Lab, another AHU #4 serves the Analytical Lab. The HVAC specialist design the office AHU #1 & 2 to control the supply air temp setpoint on the duct supply side. While AHU#3 & #4 that serves the Lab, they design to control the return air temp setpoint only at the return duct side.
The problem now I'm having, is the Micro & Analytical Lab temp seems to be in the "hunting" state, and the actual supply air temp reading can swing widely from 16deg to 23deg!!! This is undesirable for us!! As we are always facing condensation problem!!!
Is there anything wrong with the AHU#3 & #4 Motor VFD ramp up / down time setting?? They have set to 25sec... while AHU#1 & #2 set to 100sec...
Or the problems lies with the BMS "Building maintenance Software" system??? The PID loop not set correctly???
Another confusion is that why for the lab, they control the return air temp instead of the supply side??? Won't this cause hunting problem, if there is no heat load in the lab during weekend?? They can't answer me cos' the Main HVAC Consultant give them the requirements, and i have no access to the consultant as yet...
Many Thanks...