S Drives running hours

11/21/2007 3:30 PM

For easier collecting of running hours for our equipments i put an analoge meter feeds from the brake contactor. but when compared with r825 (reading parameter for SIEMENS SIMOVERT drives runing hours (Days/Hours/Seconds)) the result is totally different.

the drive has running hours nearly twice the analog counter.

does any one knows where is the gap?

(it is hoist drive in a crane)

thx

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#1

Re: S Drives running hours

11/21/2007 11:04 PM

Fraud by the re[air ccompany? who does routine service after a certain number of hours of operation, or someone invoices you for machine operated hours?

I am not sure if this is what you imply. You seems to imply that one means of measuring the operating hours gives you about half the time of the other.

I then wonder who gains in this? Why do you need to measure these hours?

WGAS

__________________
Per Ardua Ad Astra
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2

Re: S Drives running hours

11/22/2007 12:05 AM

I think you have connected the analog hour meter to the brake contactor, which means the analogue meter will get input only when brake contactor is on.For you to get the total hours run you should connect the analog meter to the main contactor.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Oct 2007
Location: Hartwell Georgia N34* 56.770 / W83* 35.431
Posts: 222
Good Answers: 1
#3

Re: S Drives running hours

11/22/2007 8:05 AM

Ramvinod is correct. You may need to observe the controls as they operate and parallel the main contactor coil circuit. When it energizes, your counter energizes.

Good luck,

James

__________________
" adapt, improvise, overcome "
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4

Re: S Drives running hours

11/28/2007 9:36 AM

Generally speaking... on most cranes or hoists, to release the brake you have to energize it, so that it will fail safe and hold the loads on the failure of the control system. So putting an hour meter across the brake contractor is more then likely a valid approach.

The difference in the two recorded times is more then likely from the fact that your analog meter records, "moving" time where as the drive may record "power on time" and will record the passage of time even when the motor is not moving.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5
In reply to #4

Re: S Drives running hours

11/28/2007 9:50 AM

Can you elaborate , i could not understand properly

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #5

Re: S Drives running hours

11/28/2007 11:32 AM

By connecting only to the brake contactor, the ETM (Elapsed Time Meter) is accumulating time only when the drive is allowing a move, i.e. the brake is released. In most hoist drives, the drive must energize the motor prior to releasing the brake so that the load does not drop while the drive is attempting to create enough torque to stop it. In fact, if the load is already moving (dropping), the motor may be unable to create enough torque to overcome the inertia! So the motor is energized while to brake is still engaged, the drive goes through a routine as it determines the proper output algorithm to maximize torque so as to hold the load, then the brake is released and the drive is in firm control. It is called a "torque proving" command. The difference as far as the ETM is concerned then is the difference between run-time of the drive and movement-time of the load, because by being tied to the brake release, it is only tied to the movement-time.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

aurizon (1); hastingselectric (1); JRaef (1); North of 60 (1); ramvinod (2)

Previous in Forum: facts contol   Next in Forum: question on impulse voltage

Advertisement