rating of induction motor

11/25/2007 9:17 AM

hi friends.....

when i try to calculate ampere rating of induction motor ..it is not calculated by the formula p=1.732*V*I*p.f..... & value of ampere calculated is not matched as written on rating plate.

the motor has given its kw , ampere , p. f. , efficiency...

is there any factor which i need to consider for it ...

plz help

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
India - Member - Electrical Energy

Join Date: May 2007
Location: Tamilnadu
Posts: 57
#1

Re: rating of induction motor

11/25/2007 9:45 AM

Is it Three Phase or Single Phase ?

Register to Reply
Anonymous Poster
#11
In reply to #1

Re: rating of induction motor

09/23/2009 11:09 AM

both

Register to Reply
Power-User

Join Date: Oct 2007
Location: Hartwell Georgia N34* 56.770 / W83* 35.431
Posts: 222
Good Answers: 1
#2

Re: rating of induction motor

11/25/2007 10:37 AM

If I understand, the ampere rating is given on the name plate.

Try these: kW = I x E x 1.73 x PF / 1000 (Must be three phase since you use 1.73)

HP = I x E x 1.73 x Eff x PF / 746 (If you need HP)

The amperage on the name plate is at full load.

Good luck,

James

__________________
" adapt, improvise, overcome "
Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#3
In reply to #2

Re: rating of induction motor

11/25/2007 1:31 PM

Hastings,

Don't you need to use the efficiency for the KW version as well? I had a motor recently that was:

6.3 KV, 257 Amp, 0.85 PF, 0.945 eff, which resulted in a power of

6.3*257.0.85*0.945*1.732= 2252KW.

Register to Reply
Power-User

Join Date: Dec 2006
Location: Vietnam
Posts: 153
#4

Re: rating of induction motor

11/26/2007 2:26 AM

Hi Sandeep,

I think that, you don't need recalculate the ampere rating of induction motor.

Just use the ratted current of Motor manufacturer, and try to use the famous manufacturer e.g. Siemens, Fuji, Mitsubishi, AEG,.....

Best regard.

__________________
Nature is unlimited, human's knowledge is limited
Register to Reply
Member

Join Date: Nov 2007
Posts: 5
#5

Re: rating of induction motor

11/26/2007 7:44 AM

Actually as per my knowledge at the name plate they given the output power.

so,

i=(p)/(1.732*V*p.f*effi).

If it is true/false for you reply to me

Register to Reply Off Topic (Score 5)
Anonymous Poster
#6

Re: rating of induction motor

11/26/2007 9:01 PM

Hi ,

Few months ago , i also got the same problem while caluculating the amp rating of induction motor. what i concluded is we must take the factor of efficiency .If u get the correct answer plz let me know at pavan5ee@gmail.com . plz.

have a nice day .

pavan.

Register to Reply
Associate

Join Date: Nov 2007
Posts: 29
#7
In reply to #6

Re: rating of induction motor

11/29/2007 10:12 AM

Hi friends, this is d induction motor rating provided on nameplate= 5 kw , current 9.2 a , v= 400+-10 , eff. 86 percent , p.f =0.92 , rpm=2880. now we use d formula den p = 1.732#400#9.2#0.92. d value of p is not comes to 5 kw. plz prove it.

Register to Reply
Power-User

Join Date: Oct 2007
Location: Hartwell Georgia N34* 56.770 / W83* 35.431
Posts: 222
Good Answers: 1
#8
In reply to #7

Re: rating of induction motor

11/29/2007 10:33 AM

Yes. looks good.

5857 using only PF, 5037 with eff factored.

James

__________________
" adapt, improvise, overcome "
Register to Reply
Associate

Join Date: Nov 2007
Posts: 29
#9
In reply to #8

Re: rating of induction motor

11/30/2007 12:49 AM

OK james, it means i have to consider eff. can u tell me wat r d other equipments in which we need to consider dis eff. like in case d.g sets we didt consider eff. to calculate current. in their rating kva , voltage, current r required eff. is not y it is ? plz clerify

Register to Reply
Power-User

Join Date: Dec 2006
Location: Vietnam
Posts: 153
#10
In reply to #7

Re: rating of induction motor

11/30/2007 1:29 AM

Yes It is approximate.

Pmotor=√3*U*I*cosφ(PF)*µ(Eff)=1.732*400*9.2*0.92*0.86=5043W=5.04KW.

Therefore value in nameplate is 5KW.

And can you try again: Siemens motor with 400V three phases, 8.2A, 4KW, Cosφ=0.83, µ=85%, 1440 rpm.

And please don't recalculate something, that were standardized. Three phases Induction Motor is one of them.

__________________