Risk of operation in power plant

11/25/2007 6:50 AM

Recently the commissioning part of our company started a new project in a gas turbine power plant with six individual power generation units, each 160 MW.

Each power unit includes one auxiliary medium voltage switchgear to supply internal consumptions. Also common switchgear is considered for power plant common consumers and a long interconnection cable (approximately 700 m) between each MV and common panel for emergency using. This interconnection path is used instead of incoming units when their incomings can not be energized via normal path.

One day, the head of electrical commissioning group called the office engineers to help. He said," we can not run unit 2 switchgear via normal path, and we have decided to use interconnection of common switchgear. But when we close the related circuit breaker, its relevant sensitive earth fault trips it".

The setting of mentioned relay is similar to the other same relays in output feeders and it is adjusted at 2 A ( in primary side ) for all sensitive earth fault; because that medium voltage system is resistance grounded with maximum 10 A earth fault currents. Also all those earth fault relays are connected to special core balance current transformers.

He said they have never had any problem with other output feeders. They didn't have enough time, and wanted permission to increase the setting of earth fault relay in commissioning duty. They knew well this activity may be accompanying a great risk.

Can you take that risk of operation?

BEST REGARDS

MSJ

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#1

Re: Risk of operation in power plant

11/26/2007 12:11 AM

Sometimes you have to take risks but you always have to do it intentionally, knowing the possible consequences. I would do so. But you also have to do anything to reduce the time running the plant on abnormal conditions.

__________________
Aged man is not old man...
Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: Risk of operation in power plant

11/26/2007 5:19 AM

Having checked that hyperlinked website, I can now see where some of the "Impossible Questions" are coming from....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Reply to Forum Thread 2 comments

Previous in Forum: Earth Leakage relays & their use in AC system   Next in Forum: rating of induction motor

Advertisement