Fire Pump Pressure Head

11/26/2007 8:06 AM

what is the maximum acceptable pressure head for the fire pump selection as per nfpa

__________________
Sami
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Fire Pump Pressure Head

11/26/2007 8:40 AM

In 1991 the new fire pump at a factory in Dagenham was well capable of delivering 135psi. Unfortunately for the individual carrying out the commissioning, for the factory fire prevention manager, for the fire/security operations manager, for the shift fire/security operations supervisor and for the site utilities maintenance engineer looking on, the cast-iron water mains of some vintage beneath one of the site's main road surfaces were not. Said another colleague shortly after the event: "It was just like Thunderbirds - you know, when the Mole brakes through!" Also a 12" Table D flange is only rated to 100psi when new and the bolts were well rusty.....

"Memories are made of this sweet-sweet, the memories you gave to me".....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Nov 2007
Location: QATAR or EGYPT
Posts: 15
#3
In reply to #1

Re: Fire Pump Pressure Head

11/27/2007 12:48 AM

Thank you for your response.

But as per NFPA-14 FOR FIRE STANDPIPE, THE MAX. PRESSURE HEAD FOR FIRE PUMP SHALL NOT EXCEED 350 PSI FOR STANDPIPE.

__________________
Sami
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bridgeport, New Jersey, USA
Posts: 109
Good Answers: 6
#2

Re: Fire Pump Pressure Head

11/26/2007 9:34 AM

Varies. This from a Google search:

[quote]

NFPA 20:3-2.1, 1999 edition states "Pumps shall furnish not less than 150 percent of rated capacity at not less than 65 present of total rated head. The shutoff head shall not exceed 140 percent of rated head for any type pump.

[quote]

Took me longer to cut'n'paste this response than it did to search Google. Suggest you try same for more depth.

__________________
"For a successful technology, reality must take precedence over public relations, for Nature can not be fooled." - Richard Feynman
Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#4

Re: Fire Pump Pressure Head

11/27/2007 8:43 AM

I would be surprised if there is a hard and fast number. Your design should dictate the pressure you need, move on from there.

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Active Contributor

Join Date: Nov 2007
Location: QATAR or EGYPT
Posts: 15
#5
In reply to #4

Re: Fire Pump Pressure Head

11/27/2007 9:12 AM

Any how, thank you

my design is require 420 psi

so for this reason i am asking for the max. pressure required as per nfpa

(NFPA-20 DOES'T MENTIONED ANYTHING, BUT NFPA-14 SAY 350 PSI)

__________________
Sami
Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#6

Re: Fire Pump Pressure Head

11/27/2007 9:42 AM

Is the fire pump a diesel drive or is it electric? Are you providing a fire system for public fire department access in a building or is it something different?

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Active Contributor

Join Date: Nov 2007
Location: QATAR or EGYPT
Posts: 15
#7
In reply to #6

Re: Fire Pump Pressure Head

11/27/2007 3:32 PM

The application is high rise building and we can use one deisel & one electric.

(N.B THE ONLY AVAILABLE SPACE FOR FIRE WATER TANK IS AT BASEMENT FLOOR)

__________________
Sami
Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#8
In reply to #7

Re: Fire Pump Pressure Head

11/27/2007 4:04 PM

I think your options are limited since you are dealing with a hose/sprinkler assembly, the way I read my "googled" items says that you need to observe the 350 psig limit. Are you putting the pumps in series and still require the 420 psi on one of the pressure circuits? Something like this:

I'm not a fire system expert, particularly in buildings, but maybe this will put you on the right path. If you're already doing this, how about 3 pumps in series? Maybe use VFDs to stay away from the PRVs as well, I read that too, although I'm not sure how that jives with NFPA 14.

__________________
Money doesn't talk, it screams in your face.