GE 239 Motor Protection Relay RTD Alarm

11/27/2007 5:52 AM

Please let know which terminal to jumper(to bypass) & clear alarm able to start the motor, Because the motor protection relay 239 having RTD faulty alarm (Motor stator winding thermistor is normal and operating temperature is in between the insulation class). Thank you.

#Terminal for RTD connection are use :

T48 to T57

Best Regards

Chan KK

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#1

Re: GE 239 Motor Protection Relay RTD Alarm

11/27/2007 9:46 AM

Could u be more specific? Pl mention motor rating, Voltage.You are mentioning RTD and then next line thermistor .Both are different though both are used for protecting the motor against overheating.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Associate

Join Date: Nov 2007
Posts: 44
#2
In reply to #1

Re: GE 239 Motor Protection Relay RTD Alarm

11/27/2007 11:39 PM

The motor is reted at 410kw , 3.3kv (3 set of RTD MOTOR WINDING) and protect by GE 239 motor protection relay.

Best Regards

Chan KK

Register to Reply
Associate

Join Date: Nov 2007
Posts: 44
#3
In reply to #2

Re: GE 239 Motor Protection Relay RTD Alarm

11/28/2007 12:07 AM

The motor is reted at 410kw , 3.3kv (3 set of RTD MOTOR WINDING) ABB motor and protect by GE 239 motor protection relay.

Best Regards

Chan KK

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: GE 239 Motor Protection Relay RTD Alarm

11/28/2007 4:39 AM

This is nothing to do with motor ratings, and voltage.It is purely setting on the relay to bypass the alarm event.

Best would be go through the manual of GE motor protection relay or the service Engineer of GE who is familiar with these relays.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Associate

Join Date: Nov 2007
Posts: 44
#5
In reply to #4

Re: GE 239 Motor Protection Relay RTD Alarm

11/28/2007 5:47 AM

Dear Ramvinod

Thank for fit back and I have ratify the problem was the underground cable connect between the protection relay & motor RTD having high resistance. Temporary lay cable on surface :

1, Put the HT switchgear at test position, apply 120Vac test supply.

2. Remove the RTD & connect up the resistance bank to the temporary cable, increases & decreases the resistance the switchgear was trip at high resistance.

3. Connect back the RTD and test run the motor & return to service

Best Regards

chan KK

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: GE 239 Motor Protection Relay RTD Alarm

11/28/2007 11:45 AM

Um, didn't anyone else see the problem as I do?

Unless there is a semantics issue here, you are apparently attempting to install a Thermistor in the motor to an RTD input on the relay. They are two different things. The 239 has, as standard, a separate Thermistor input on terminals 21 and 22. If you are using a motor thermistor, that is where you must connect it.

If you ordered the RTD option and do NOT install any RTDs, you must first slap yourself silly for wasting money, then go in to programming and disable all of the RTD inputs, otherwise it will trip on failed RTD.

Hey, isn't that what you are getting!?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#7
In reply to #6

Re: GE 239 Motor Protection Relay RTD Alarm

11/28/2007 1:02 PM

Great ! Experience speaks !

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Associate

Join Date: Nov 2007
Posts: 44
#8
In reply to #6

Re: GE 239 Motor Protection Relay RTD Alarm

11/29/2007 5:33 AM

Dear JRaef :

The ABB motor is come with 3 set of RTD connection ,is provide addition protection for the motor insulation breakdown of the stator winding due to overheating failure.

The the GE 239 motor protection relay also design for the RTD input connection from terminal T49 to T57 ,no need to install addition Thermistor for the motor overheating protection is wasting money.

Best Regards

Chan Kum Kong

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9
In reply to #8

Re: GE 239 Motor Protection Relay RTD Alarm

11/29/2007 11:34 PM

I know what motor RTDs are for and I know how a 239 works for crying out loud. I was trying to help.

Quoted from your original post...

"Motor stator winding thermistor is normal and operating temperature is in between the insulation class"

That said to me that you have a thermistor, not RTDs. Now you say they are RTDs, not a thermistor. Make up your mind.

If you make erroneous statements, you get the answers you deserve.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 9 comments