11KV Switchgear Design

11/27/2007 9:08 AM

I am going to design a 11KV switchgear. The switchgear has two incoming lines equipped with VCB's and one bus-coupler. The incoming VCB's will be N.C and the bus-coupler will be N.C in normal operation. In the absence of voltage on any incoming the dead incoming VCB will be switch-off and the bus-coupler VCB Will be switched-on automatically. By voltage restoration the return will be done manually not automatically. There is not any 11kV motor as outgoing feeder, only 11/0.42KV transformers and downstream switchgears exist as outgoing. I have considered an U/V relay for each incoming before VCB and an U/V relay for each half-busbar. My client requested to consider another U/V relay or use of two-step U/V relay on each half-busbar, but I don't know why? Does anyone know more about this matter or a good link? Can anyone help ma about two-step U/V relays?

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#1

Re: 11KV Switchgear Design

11/28/2007 2:00 AM

With the single UV relay if you switch on the bus coupler there will be much problem provided your incomers are designed to work parallel. That means even if for a very small interval of time both the feeders may be simultaneously ON and should not cause any damage due to the delay in operation of the relay contacts . If that is not the case then you should go for double relay operation for switching of bus coupler.

Register to Reply
Associate

Join Date: Sep 2007
Posts: 49
Good Answers: 1
#3
In reply to #1

Re: 11KV Switchgear Design

11/28/2007 3:30 AM

Please note that two incomers are not designed to work parallel and so no synchronizing check relay is considered. Two of Three circuit breakers are closed at the same time.

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2

Re: 11KV Switchgear Design

11/28/2007 2:31 AM

This is called auto change over scheme.

I have done many such schemes for reputed installations in india.

It is enough to have two Under voltage relays on incoming sides of 11 kV VCB.

But suitable logic circuitary to be developed for tripping and closing and interlock two incomers and one buscoupler.You can use some timers and auxiliary relays to achieve this or a simple PLC will serve the purpose.For further help please send email.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2009
Posts: 3
#12
In reply to #2

Re: 11KV Switchgear Design

06/09/2009 8:54 AM

Dear Sir,

Now a days i m doing work on this project, i mean 11KV automatic trasnfer switch.

i need some help. if you send me latest design/drawing of 11KV Automatic Changover switch, i will very thank full to you. it will helpfull for me, you know taht ATS module are usualy use for Main AC & Generator, but in this case both supply are A.C Supply Form different Grid Station. And in ATS OR AMF Module DC Supply 12VDC OR 24VDC is necessary for operation. But in this case we have no Battery supply.

What is solution of this problem & which type of PLC/Module will suitable for this Circuit.

Kindly Send me Breaf Answer and Design

Thnanks.

Best Regards!

Waseem

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#13
In reply to #12

Re: 11KV Switchgear Design

06/10/2009 1:06 AM

Reputed ATS are available.Try Cummins. ATS is not only for mains and DG set. ATS can be used for any two different sources of supply. When you use ATS , PLC is not required since ATS has got built in control logic. For control supply you can achieve from PT of the incoming supplies. ramesh

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Off Topic (Score 5)
Anonymous Poster
#16
In reply to #2

Re: 11KV Switchgear Design

12/07/2009 7:50 AM

Dear sir,

we need quotation for VCB panel type . Please give your best prices & delivery time

PLEASES FIND ATTCHMET FILE

No.

Description

Qty

1

IN DOOR TYPE 11KV,400A,25KA, SINGLE VCB PANAL BORD 1NOS.
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: May 2016
Location: Ahmedabad
Posts: 21
#18
In reply to #16

Re: 11KV Switchgear Design

06/13/2016 5:49 AM

For any type of information related to vcb panels and other power automation solutions. feel free to contact us on mv@highvoltindia.com

__________________
Control Panels India
Register to Reply Off Topic (Score 5)
Anonymous Poster
#4

Re: 11KV Switchgear Design

11/28/2007 7:07 AM

I am sorry, but I think you intended to say that the bus coupler is normally open and the two incoming feeders normally closed, is it ?

In automatic transfer, it is important to check if the transfer will occur by connecting the other feeder to a dead bus.

Therefore, your client probably has the fear that the bus is not dead during the transfer interval. This may be because he has any synchronous machine connected to the bus or the system foresees an UPS connected to the secondary of a voltage transformer.

In this case, it is advisable to have voltage detector relays in each bus.

Please note that you do not actually need to use undervoltage relays, because the purpose of the detector is to check if the bus is dead or not.

Regards

Register to Reply
Associate

Join Date: Sep 2007
Posts: 49
Good Answers: 1
#5
In reply to #4

Re: 11KV Switchgear Design

11/28/2007 8:29 AM

Yes, the bus coupler is normally open and the two incoming feeders are normally closed. But there is not any motor directly to switchgear.

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#6
In reply to #4

Re: 11KV Switchgear Design

11/28/2007 8:40 AM

I think these feeders supply power to 11 kV transformers.Once 11 kv supply fails,the Incoming LT supply to LT board through ACB can be made to trip so that back feeding from UPS through transformer will not take place and it will be definetely dead bus.

One has to gothrough complete scheme and philosphy of operation of VCBs and ACBs before we conclude the provision of undervoltage/ no voltage relays and no of relays etc.

I had suggested for a simple system.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Anonymous Poster
#15
In reply to #6

Re: 11KV Switchgear Design

09/06/2009 4:55 AM

DEAR SIRS, WE HAVE THE PLEASURE TO INTRODUCE OUR COMPANY AS WELL KNOWN IN KUWAIT , AS GENERAL TRADING AND CONTRACTING DEALING , OUR MAIN DEALING IS WITH MINISTRY OF ELECTRICITYA ND WATER AS WELL AS KUWAIT OIL COMPANY WHICH WE HAVE WITH THEM GOOD CONTACTS. THERE IS PREQUALIFICATION TO QUALIFY THE COMPANIES OR MANUFACTURERS WHO ARE DOING 11KV SWITCH GEAR, 11KV SWITCH BOARD, AND 11KV COMPLETE DISTRIBUTION . SO , IF YOU ARE WILLING TO PARTICIPATE AND REGISTER YOUR COMPANY AS QUALIFIED MANUFACTURER , THEN YOU ARE REQUESTED TO SEND US YOUR COMPANY PROFILE TO ENABLING US TO PURCAHSE THE PREQUALIFICATION DOCUMENT. FOR YOUR IDEA, IF YOUR COMPANY QUALIFICATION ACCEPTED BY MINISTRY OF ELECTRICITY AND WATER , THEN YOUR COMPANY WILL BE REGISTERED OFFICIALLY FOR THIS PROJECT . WE WILL APPRECIATE TO RECIEVE YOUR REPLY TODAY . AWAITING YOUR RPELY. THANK YOU Z.DAHMASH

Register to Reply Off Topic (Score 5)
Associate

Join Date: Sep 2007
Posts: 49
Good Answers: 1
#7

Re: 11KV Switchgear Design

11/28/2007 9:35 AM

Dear Friends,

11KV incoming feeders will be supplied from two synchronized sources by client.

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#8
In reply to #7

Re: 11KV Switchgear Design

11/29/2007 6:48 AM

I had sent the sketch giving brief circuit.Please confirm receipt and give your feedback.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Anonymous Poster
#9
In reply to #8

Re: 11KV Switchgear Design

11/29/2007 7:30 AM

Many Thanks

I have received your sketch.

Register to Reply
Anonymous Poster
#10

Re: 11KV Switchgear Design

03/22/2008 10:32 PM

Two stage UV schematic is used as reacceleration scheme. Generally reacceleration schemes are used for individual motors depending upon their importance. normally it works like this:

If a bus voltage dip causes all motors to drop and the full voltage comes back within certain short time (stage-I) some of the essential motors should start automatically. If the delay is more (stage-II) then only some of the motors to start automatically. for a longer delay all motors to drop completely and restart requires complete reset.

Kamalakar

Register to Reply
Anonymous Poster
#11

Re: 11KV Switchgear Design

10/23/2008 8:58 AM

could someone show me how to design a basic switchgear system

Register to Reply
Anonymous Poster
#14

Re: 11KV Switchgear Design

07/04/2009 3:07 AM

Second relay client is asking for to ensure no voltage on the dead bus. Capacitive voltage may exist on the dead bus. To sence no voltage another undervoltage having setting 0-10% is required.

Register to Reply
Member

Join Date: Aug 2010
Posts: 7
#17

Re: 11KV Switchgear Design

08/03/2010 4:05 AM

CR4 Admin: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Register to Reply 18 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abbas (3); Anonymous Poster (7); highvoltpower (1); ramvinod (4); shirlly chen (1); V.I.Abraham (1); waseem17pk (1)

Previous in Forum: GE 239 Motor Protection Relay RTD Alarm   Next in Forum: Difference betwen Namur and Reed Sensor

Advertisement