MCB characteristic at high voltage

12/01/2007 1:08 AM

Can any body tell that what effect at MCB characteristic at high volt?

In current I am using MCB at operating voltage is 230/415. In case the operating voltage is on MCB is 460,500,600…1000 than MCB can work on not if yes can tell me that what effect its characteristic?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: MCB characteristic at high voltage

12/01/2007 7:05 AM

This will fail.

The MCB is designed to work at designed voltage level.If higher voltage is applied it will fail due to insulation.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Active Contributor
Engineering Fields - Engineering Physics - New Member

Join Date: Nov 2007
Location: NOIDA, INDIA
Posts: 21
#9
In reply to #1

Re: MCB characteristic at high voltage

12/04/2007 3:40 AM

GOOD ANSWER SIR....

Register to Reply Off Topic (Score 5)
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2

Re: MCB characteristic at high voltage

12/01/2007 11:41 AM

Every electrical has itsoperating voltage level.Why would u like to have this MCB operating at high voltage when there are specific breakers for those applications. As informed there will be a flash over .

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Commentator
India - Member - Electrical Energy

Join Date: May 2007
Location: Tamilnadu
Posts: 57
#3

Re: MCB characteristic at high voltage

12/02/2007 3:02 AM

Refer cherecteristics from supplier catlog.

Register to Reply
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#4

Re: MCB characteristic at high voltage

12/02/2007 9:31 AM

Due to the ignorance shown by your question, I am sorry I have to point out to you that it is not wise to play with this equipment. Not only your safety is at stake but their are always people around you and / or in the building.

What would you feel like if your building burns down due to your handy work and 3 fireman died trying to save you out of this burning building?

Let it go and contract a proper electrician with qualifications.

Register to Reply
Commentator

Join Date: Aug 2007
Posts: 86
Good Answers: 2
#5

Re: MCB characteristic at high voltage

12/02/2007 9:56 AM

I think you are all missing the point of the enquiry.

The enquirer is asking if he can use MCBs marked with a higher voltage rating than the ones in service.

The answer is 'YES'. The voltage marked indicates the voltage up to which the device can be used,.i.e. a figure of merit. The voltage rating has no effect on the current characteristics as the device works on current only.One caveat, AC only.Dont mix AC and DC breakers.

In general some of the respondents are adopting an unfortunate attitude of 'if you have to ask the question then you do not know enough to safely employ the answer'. We will be even more likely to blow ourselves up if you have discouraged us from asking questions.

Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#6
In reply to #5

Re: MCB characteristic at high voltage

12/02/2007 10:32 AM

Summary:

Questioners should use

  • Short sentences
  • Seperate the Question from other( his own) advice/comment.

He could have asked like this:

" My factory is wired 50Hz 3phase+neutral =415/240V

All my MCB's have markings of" Max 480V"

I have some Spare MCB'S with markings "Max.800VAC"

Can I use the latter for some new machine at my factory?I shall make sure that load Amperes will be within what is marked on MCB label.

Register to Reply
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#7
In reply to #5

Re: MCB characteristic at high voltage

12/02/2007 10:42 AM

"In general some of the respondents are adopting an unfortunate attitude of 'if you have to ask the question then you do not know enough to safely employ the answer'. We will be even more likely to blow ourselves up if you have discouraged us from asking questions."

Since when is advising somebody to use a qualified electrician instead of employing a new found knowledge with possible dire consequences a discouragement for asking questions?

Your world is upside down my friend. You ask, you get answers. It is up to the reader to act upon this info or not. If he or she was afraid to ask but did not know and STILL went ahead and blew themselves up, you would blame us for having discouraged them!

You sound like you are a member of the new politically correct brigade, and just in case you hadn't noticed, not many here like that brigade very much.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: MCB characteristic at high voltage

12/02/2007 4:51 PM

It's really all a moot point. I know of no MCB's (Miniature Circuit Breakers) that are rated for any voltage higher than 690V and those are rare. Most MCB ratings stop at 415Y230V anyway.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply