How to Achieve Power Factor Improvement??

12/01/2007 1:08 PM

Hi..all

I always read about power factor improvement, but i dun understand in reality how to achieve it...In a typical factory setting, which has its own HT (22Kv & 6.6kv) and LV (415V) transformer supply; and with all its equipment like motors, pumps, air compressor, chillers, HVAC, process equipment, etc... how can we improve the power factor??

Does every equipments (chiller, pumps, motors, etc) comes installed with power factor improvement design incorporated already by the manufacterers?? Or did we need to design this and install power factor improvement equipment in the power panel??

We are using ABB switch gear.. also in reality, does PF always less than 1; even after improvement?? Thanks all..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#1

Re: How to Achieve Power Factor Improvement??

12/01/2007 10:33 PM

Waterlucky, Step 1. Find your existing pf on peak load conditions. A good powermeter at the source will help you in this. Step 2. Find the necessary capacitors ( kvar) required for the improvement (say to 0.95). No, the OEM will not supply you PF correction capacitors for the equipment unless specified by you in order. Good luck

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: How to Achieve Power Factor Improvement??

12/02/2007 7:21 AM

Hello waterlucky,

"also in reality, does PF always less than 1; even after improvement??"


The cost of attaining Power factor of greater than 0.95 is not economically practicable.

Regarding where to instal PF correction equipment, in an installation, please see my earlier answer here:

http://cr4.globalspec.com/comment/145220/Re-DG-running-at-unity-power-factor

If you need further help, please reply....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Aug 2007
Posts: 86
Good Answers: 2
#3

Re: How to Achieve Power Factor Improvement??

12/02/2007 10:47 AM

With the exception of discharge and fluoresecent lighting,which are already fitted with the correct power factor correction capacitors,most other plant will not have or be offered with power factor correction.

Local distribution boards and motor control centres at 415V are the most common place to site power factor correction capacitors,with automatic controls and contactors to switch in capacitors as required.Overcompensation must be avoided as most suppliers charge for lagging or leading pf,and there can be serious technical problems as unity pf is approached near a load.

As has been pointed out unless there are other reasons for improving power factor,e.g.supply or generation capacity,the charge made by suppliers for low power factor must be balanced against the cost of installing and maintaining pf correction.Capacitors these days only seem to last at max 5 yrs.

Manufacturers of pf capacitors will often give you a free survey,and propose a plan for capacitors and controls throughout your plant.

I hope that I have not just restated what is in other respondents links,if I have I apologise to them.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#4

Re: How to Achieve Power Factor Improvement??

12/02/2007 11:20 AM

You can go in for a centralized capacitor bank on the HV or individual capacitors on major equipments or capacitor banks at each of the unit substation bus bars on LV.HT capacitor will workout cost wise better.But if your diversity factor is high u may go in for LV at each unit substation.A clear solution can be be tried if we know ur power distribution arrangement.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: How to Achieve Power Factor Improvement??

12/02/2007 4:03 PM

Your equipment will not come with pf correction unless you specify it to do so. From now on, make that your standard purchase specification for new motorized equipment, that way the vendors of the equipment will take responsibility to ensure proper application without damage.

There are three basic design philosophies to pf correction. Bulk correction, At-Load correction and Dynamic correction.

Bulk correction is the least expensive from an initial cost of installation, but can often be the most expensive when equipment damage and downtime are factored in over the long run. Bulk correction makes 2 assumptions; 1) Your plant loading is static, in other words, you can design a system for your existing load profile and it will not vary to any great degree so that capacitance is not being switched in and out too often. You have a mildly variable load process, i.e. you make some specific product or have a process that does not change much during the day, loads are not switched on and off very often and you don't have uncontrolled inflow to deal with; 2) Your equipment is not sensitive to harmonics, voltage spikes and capacitive resonance issues that come along with bulk correction. you can tolerate a major even such as the failure of a bulk cap that will be seen by the entire system and you can tolerate having a leading power factor when the bulk system is too slow to react. In modern facilities, most of these issues WILL be a problem. For example, many variable speed drives can be affected by resonance with upstream capacitors and create extreme harmonics that do damage to other equipment; electronic controls can be damaged by spikes that occur when capacitors are switched on and off as your load changes; overcorrection can lead to line voltages that are out of tolerance for electronic controls and/or PC power supplies, etc. etc.

At-Load correction is the better way to go. This means that you add capacitors to each piece of equipment that presents a lagging power factor to your overall system, but incorporated with whatever is turning it on and off so that it is off-line when the equipment is off-line. So capacitance is added to the system only when needed and there is no chance of over correction (creating a leading power factor). Each individual load can/must be investigated for whether or not PFC capacitors are appropriate, for example Soft Starters must NEVER have capacitors on-line until they are done ramping. Or can adding capacitors damage other nearby systems, i.e your HVAC system may have sensors that would be affected by switching on capacitors etc. etc. Lastly, if a capacitor fails there is little chance of it affecting your entire plant, as it would in bulk correction, because once you switch that load off, the caps are off-line as well. At-Load correction is more expensive that bulk, but not as expensive as Dynamic on small installations.

Dynamic correction is when you use what is called a "condenser", typically a synchronous motor running either on your largest continuous load, or by itself connected to nothing. For example, lets say you have a large air compressor that is critical to the operation of your process; no matter what else is going on, the compressor is always running. You would put a synchronous motor on that compressor and a control system that would monitor your entire facility's power factor, then alter the field voltage of the synch. motor controller to run that motor in a leading power factor, dynamically correcting the lagging pf contribution of all of your other loads. Some people do this even if they don't have a large continuous load to run, because it can be less expensive on large existing installations where retrofitting At-Load correction becomes cost prohibitive. Dynamic correction then is very similar to Bulk correction, but does not come with the risks of voltage spike damage from switching capacitors in and out, failure of the capacitors themselves or resonant interaction with other equipment.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#6

Re: How to Achieve Power Factor Improvement??

12/02/2007 5:08 PM

Power factor has raised its wearisome head again in recent years. In the good-old bad-old days equipment manufacturers regarded power factor as a SEP - someone elses problem. Actually this was OK - you knew where you stood. PFC was simply an economic problem and easy to financially justify. Utility companies charged you for bad PF = saving per year = payback. Done.

Technology then gave us the 'smart' sampling electricity tariff meter. Utility companies were overjoyed at charging their customers per minute, per day, per week, per month, per season, per kW, per kVA, per fuel surcharge, per 'just for the heck of it'. Financial modelling becomes mind boggling - even the utilties themselves have trouble recommending a tariff. That suits them just fine.

PF starts to improve. Flourescent lighting (yes and even halogen lighting) gets high frequency ballasts with PF=0.99, big induction motors get first soft start then variable speed drives, CRT displays disappear from the desktop and even big servers become leading power factor. Utility companies don't care - they just increase one of the other 'pers' listed above to maintain profit.

Now however we have to deal with all the harmonics the electronic devices listed above now generate. Earth and neutral cables start to overheat due to all the happy currents harmoniously bouncing around the power system. These are tricky devils to eliminate and will engage in all sorts of oscillating gyrations with PFC banks, whose capacitors are so overjoyed at the attention they will happily explode with delight and bring down your building with them. (A recent project was a pumping station where the capacitors literally evaporated. Luckily so quickly the fire did not spread. We measured over 25% THD, where the nominal would be 2%. The higher the frequency, the lower the capacitor impedance...).

So PFC calculations are tough. Extensive protection devices are required to protect your precious kVAR, and as mentioned in a previous post they tend not to last too long. Expensive inductors are required as filters too. In all my current projects, I do not specify PFC outright. I wait for a few seasons of electricity bills and then buy time on the CIAs fastest supercomputer to see if it's worth all the hassle. 9/10 nowadays - just pay the utility charge. Sad but true.

+

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply
Power-User

Join Date: Dec 2006
Location: Vietnam
Posts: 153
#7

Re: How to Achieve Power Factor Improvement??

12/03/2007 1:23 AM

Our factory is operation for 12 years, with ABB power factor control unit(you can set Pf index value) and now it is well operated. Therefore, please contact to your electric room maker of designer for best solution. And mention to your electric distributor law: with Pf=? you have to penalty or return electric fee.

Of course you must refer to above conferences.

Good luck!

__________________
Nature is unlimited, human's knowledge is limited
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#8

Re: How to Achieve Power Factor Improvement??

12/03/2007 2:04 PM

The answers above are all good. Another option, if your factory uses synchronous motors, is to over-excite the field of the synchronous motor. This produces an effect similar to installing capacitors. One major advantage of this design is that the motor field can be easily controlled to maintain a constant power factor (selected for the most economical compromise between cost of electricity and cost of equipment). It also avoids the power quality problems (harmonics) which frequently occur when capacitors are switched in & out of service.

"also in reality, does PF always less than 1; even after improvement??"

Power factor can equal 1 (called unity power factor), but not exceed it. Mathmatically, power factor is the cosine of the angle between voltage & current. A cosine value can never be greater than 1.0. Increasing the capacitance effect beyond unity results in again lowering the power factor and reducing efficiency.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Associate

Join Date: May 2007
Location: Houston, TX
Posts: 39
#9

Re: How to Achieve Power Factor Improvement??

12/05/2007 9:07 AM

The company that I work for specializes in energy conservation projects. For the large facilities that we have done worldwide, placing properly sized capacitors as close to the load as possible is one easy fix to reduce the PF charge the utility company imposes. Most of the reputable Caps are put in parallel so if one should fail your equipment is just back to the way it was. In the whole project, Caps usually show a payback of just a few months and we have been implementing them for over 20 years, so its not anything new or experimental.

__________________
How is it that my measurement of 8" is different than hers?
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: