Current-Carrying Capacity for Copper Tube

12/03/2007 6:49 AM

Pl. let me know the Current Carrying Capacity for 37.5 mm OD Copper Tube with a wall thickness of 3 mm.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2006
Location: New Jersey U.S.A.
Posts: 1114
Good Answers: 38
#1

Re: Current Carring Capacity for Copper Tube

12/03/2007 6:57 AM

In what situation would you need a copper tube to conduct electricity?

__________________
The last fight was my fault. My wife asked "What's on the TV?" I said "Dust!"
Reply
Participant

Join Date: Dec 2007
Location: Jammu & Kashmir (India)
Posts: 2
#2
In reply to #1

Re: Current Carring Capacity for Copper Tube

12/03/2007 7:03 AM

I want use this tube as a moving blade for 33Kv Double Break Isolator.

__________________
With due Regards. Rohit Luthra
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #2

Re: Current Carring Capacity for Copper Tube

08/21/2024 10:29 AM

That's madness.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2006
Location: New Jersey U.S.A.
Posts: 1114
Good Answers: 38
#3

Re: Current Carring Capacity for Copper Tube

12/03/2007 7:48 AM

These are normally solid copper sometimes nickel plated. I don't think a copper tube would last long. Possibly cause failure and short when most needed.

There are many manufacturers that can sell you properly rated mechanisms for your function. Don't jury rig your power supplies with inadequate isolators.

Catastrophies are inevitable!

__________________
The last fight was my fault. My wife asked "What's on the TV?" I said "Dust!"
Reply
Participant

Join Date: Dec 2007
Location: Jammu & Kashmir (India)
Posts: 2
#4
In reply to #3

Re: Current Carring Capacity for Copper Tube

12/03/2007 7:56 AM

Sorry to intrupt you dear, but when we talk of HT electricals then we have to follow the designs offered by the Power Department. The Tube I'm using as per the requirement of my customer but I want to Re- confirm that the stuff they are asking is really stand for the load?.

__________________
With due Regards. Rohit Luthra
Reply
Anonymous Poster
#9
In reply to #4

Re: Current Carring Capacity for Copper Tube

12/04/2007 10:43 AM

the current caring capacity for a given section depends ultimately on the thermal stability of the material(which depends on the other hand on the maximum temperature that can be attained by the material in condition of proper running of the eqiupment). The copper tube has some geometrical dimentions that you know. Also it has electrical resistance. for a given current the tube will dissipate an amount of power in a form of heat.So the tube will tend to heat up as the current rises. eventually you will need to calculate how much the tube is allowed to heat up, then to calculate the power that reaches the limit of the thermal stability, and knowing the power dissipated in the tube and the electrical resistance of the tube you can calculate the maximum current.

good luck

Reply
Power-User
Hobbies - Fishing - New Member

Join Date: Feb 2007
Location: Suva Fiji Islands
Posts: 229
Good Answers: 3
#14
In reply to #4

Re: Current Carring Capacity for Copper Tube

12/12/2007 12:10 AM

The most sensible thing to do is to use the size of tube the customer specified. This way you wont get into trouble if it doesnt work. However copper tube is better for HV than solid copper as the electrons travel on the surface. The hollow tube also helps in cooling. Hollow tube is widley used for Bus Bars The only reason it is not used for HV cabling is we cant work out how to make it flexible.

__________________
"Multa ferunt anni venientes commoda secum, Multa recedente adimiunt". (The years as they come bring many agreeable things with them; As they go they take many away).
Reply
Guru

Join Date: Oct 2006
Location: New Jersey U.S.A.
Posts: 1114
Good Answers: 38
#5

Re: Current-Carrying Capacity for Copper Tube

12/03/2007 9:30 AM

Our power systems isolation bars are solid copper about 1.5 inches x 1/4". Our switchers are 2 inch solid copper. We are rated for 10MVA but operate around 4.5MVA. Don't know if this helps much but most I've seen or worked with were solid.

Sorry for the misunderstanding. Don't deal much in MM tube.

__________________
The last fight was my fault. My wife asked "What's on the TV?" I said "Dust!"
Reply
Power-User

Join Date: Apr 2007
Location: n. Switzerland
Posts: 133
Good Answers: 6
#10
In reply to #5

Re: Current-Carrying Capacity for Copper Tube

12/04/2007 10:49 AM

Sorry Charsley, but you should know a bit more before replying.

1.5" copper bar = toy systems.

Copper and/or aluminum tubing is routinely used in high voltage transmission, esp in GIS. Our standard inner conductor dia was about 14 cm, carrying 2-4 kA. (much larger tubes for higher voltage systems & for e.g. generators)(becuse of lower voltage, higher current..)

Also tubing is more efficient from the standpoint of skin effect...yes, it makes a difference even at 50/60 Hz.

To answer the question: calculate the 'flux area' (i.e. the area of a thin slice through the tube of the tube, then you can calculate the current carrying capability (there is tons of stuff in the web...if the application is for AC - alternating current - remember to use a forumla for it, it will have a correction factor for skin effect. Write again if you can't find any compensating factor.

ciao RFg

__________________
Regards, RF_guy
Reply Off Topic (Score 5)
Power-User

Join Date: Jan 2007
Location: UK S.Northants
Posts: 485
Good Answers: 19
#6

Re: Current-Carrying Capacity for Copper Tube

12/03/2007 1:01 PM

pi d^2 /4 @ 37.5 = 1104.5 mm^2 - same for 31.5 (37.5 - (2*3) ) = 325 mm^2 csa of copper, does that help?

Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#7

Re: Current-Carrying Capacity for Copper Tube

12/04/2007 1:45 AM

Dear Guest, If you slit a copper tube ( legthwise) and flatten it it would be a sheet of 3 mm thickness and 37.5 X pi width. so, your cross sectional area is 3 X 37.5 X 3.14 = 353.25 sqmm. I will leave it here, since current carrying capacity will lot of other variables. Good luck

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Reply
Participant

Join Date: Dec 2007
Posts: 2
#8

Re: Current-Carrying Capacity for Copper Tube

12/04/2007 6:16 AM

Use the National Electrical Code book or any Electrical Standards use in your country. Look for the Current Capacity of a Copper Bus Bars as related to your copper tubing design.

Reply
Participant

Join Date: Oct 2007
Posts: 2
#11

Re: Current-Carrying Capacity for Copper Tube

12/04/2007 1:10 PM

1 if u bend the coppere tube 3 times,, even straightening it out,, it gets too hard

u will have to pass a flame of a butaine torch over it a little to get it soft again

2 the service of the surface area is the electron conducting zone; or, the outside and the inside skin, if it had skin ,, is the only place the valance electrons let go and travel and grab again.

inside and outside area is conductive the thick area inside the wall doesnt conduct.. its more conductive to conduct copper fuzz, or chopped up thin hairs of copper than the tube.

r u trying to conduct static or moving, kinetic electricity,, is this for a tesla device or a townsend brown device. ... if it is a townsend brown device,, a grav cap,, ur on the right track.

Reply
Anonymous Poster
#12

Re: Current-Carrying Capacity for Copper Tube

12/10/2007 9:20 AM

I would be very worried about the heat build up. As an electrician I was taught that when making up (high amperage) connections, to be careful not to allow air pockets because heat could build up and deteriorate the connector.

Reply
Power-User

Join Date: Apr 2007
Location: n. Switzerland
Posts: 133
Good Answers: 6
#13
In reply to #12

Re: Current-Carrying Capacity for Copper Tube

12/10/2007 10:50 AM

If the calculations have been done correctly, and there's enough copper to carry the flux (& sufficient surface area on the contacts in connectors etc.) it won't get hot...

cheers

RF_G

__________________
Regards, RF_guy
Reply
Anonymous Poster
#15

Re: Current-Carrying Capacity for Copper Tube

12/05/2008 4:33 AM

The load current should be not more than 900A-1000A. There is not formulary for this tube busbar unit area capacity, as the current density is not even with the skin effect. We know this result by experience and test.

Reply
Anonymous Poster
#16

Re: Current-Carrying Capacity for Copper Tube

03/17/2009 7:00 PM

Orient heaters as shown and torque hardware uniformly to 30 in-lbs. Test to confirm that heaters are held firmly in place.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17

Re: Current-Carrying Capacity for Copper Tube

08/21/2024 10:29 AM
  • Temperature?
  • Orientation?
  • Pressure?
  • For how long?
  • Etc.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 18 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); charsley99 (3); chaterpilar (1); coconutpete (1); dgcabasa (1); HUX (1); PWSlack (2); RF_guy (2); Rohit Luthra (2); subcommander (1)

Previous in Forum: Metal Detector   Next in Forum: Back-up Generator Problem

Advertisement