DeviceNet Problems

12/04/2007 3:04 AM

Hei guys,

I am having some problem here with my Kuka Robot.

I have incorporated some sensors in my KRC2 (KR16 robot controller). It is using DeviceNEt with 4I/4O. I previous hooked some solenoid valve to it's output. That was working fine. Recently I fixed some fiber sensors and limit switch to it's Input.

Advice from the manufacturer was I should use a PNP fiber sensor rather than a NPN fiber sensor. If I am to use NPN sensor that I should fix an additional relay to it. Therefore, I changed my sensor to PNP. Initially the sensors were operating fine. No problem at all. Then the 3rd day, the fuse attached to the PLC input power (24VDC) burnt. I checked with the kuka guys and they said that there is a short circuit in my connection.

But I can't actually find out any problem in my wiring.

Can someone pls tell me what could have gone wrong, and what are the things that I should check to prevent the reoccurring of the fuse burn.

I am more concern that there might be bigger damage to the controller itself.

I really appreciate your help on this. An advance thank you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: DeviceNet Problems

12/10/2007 12:09 AM

Greetings,

Is the fuse that is failing an input or output fuse? Or is it the PLC common power supply?

Are you using a common power supply for your entire system?

Pretty much all PLC inputs are optically coupled to the field device and only require a minimum of amperage (microamps or milliamps) therefore they do not need to be and normally are not fused in most applications.

The only way an input device could cause a power supply fuse to fail is if there is field or terminal wiring that is "cross-wired" (shorted) to a separate voltage source other than that which is normally referenced and used by the PLC.

The ampacity of most PLC outputs are limited by the OEM manufacturer usually with an on-board fuse (surface-mounted or in-line board mounted), so the output(s) should not be causing your power supply fuse to fail.

If the on-board fuses are failing, the field device or wiring is shorted or grounded or it requires more current than the PLC output is rated for.

Also, if the output power is shorted to an external voltage source of a higher magnitude, the on-board fuse and/or the common power supply fuse will fail.

If all of your wiring is clear of shorts and grounds and it is not mixed with any external power source(s) and the power supply fuse is failing, you need to check the current (power) rating of your power supply against the total amperage your field devices require.

To do this, go into the field, interogate all field devices attached to your PLC outputs, record the amperage requirements of each device, add all of the recorded ampacities, and compare that number to the rating of your power supply.

If the power supply current rating value (number) is lower than the total amperage required by your field devices, install a larger power supply with at least 10% headroom (higher ampacity rating). Example: If your field devices pull a total of 4.5 amps then install a power supply with at least 5 amps of capacity.

If you are going to be expanding your I/O in the future, calculate the circuit loading for future expansion device requirements and compensate by upgrading the power supply to meet all of your requirements. That way you only have to pay for the upgrade cost one time.

Hope this helps,

Shockhiscan

Register to Reply
Active Contributor

Join Date: Dec 2007
Posts: 13
#2
In reply to #1

Re: DeviceNet Problems

12/10/2007 1:24 AM

Thank you for your lengthy explanation.

Will be checking for ampere surge.

Just one additional question. If there is a short in the circuit, definitely the fuse will blow immediately after connection right?

What happened here previously was, it was running fine for about 4 days all of sudden the fuse just blow. Lucky the PLC didn't smoke.

Can this be a short circuit phenomena? However, will be checking on the total amperage?

Thanks.