Air Flow Calculation

12/06/2007 12:28 AM

Is there any formula or relation to find out the air flow rate when only the blower motor HP and RPM is known? Static pressure of the duct is not known.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Sep 2007
Location: Reno, NV (USA)
Posts: 608
Good Answers: 66
#1

Re: Air flow calculation

12/06/2007 3:04 AM

These are the governing equations that I am aware of.

For fans and blowers:

HP = Volume (cfm) x Head (inches of water)

6356 x Mechanical Efficiency of Fan

Or

HP = Volume (cfm) x Pressure (lb. Per sq. ft.)

3300 x Mechanical Efficiency of Fan

Or

HP = Volume (cfm) x Pressure (lb. Per sq. in.)

229 x Mechanical Efficiency of Fan

For purpose of estimating, the eff. of a fan or blower may be assumed to be 0.65.

Note: Air Capacity (cfm) varies directly with fan speed. Developed Pressure varies with square of fan speed. Hp varies with cube of fan speed.

__________________
Aequam memento rebus in arduis servare mentem.
Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#2

Re: Air flow calculation

12/06/2007 4:05 AM

Short answer - No.

RPM is irrelevant as for a given fan duty it could be a big impeller going slow, or vice versa (assuming it is a fan, your ref to a duct rather than pipe suggests it is).

Even if you knew the static pressure it wouldn't help unless you know it up and downstream of the fan. Then you have the ΔP across the fan and can estimate flow from power. You need to know or assume fan efficiency and if you're measuring motor input power, motor efficiency.

Cheers.....Codey

__________________
Give masochists a fair crack of the whip
Reply
Guru

Join Date: May 2007
Location: Ohio. USA
Posts: 578
Good Answers: 30
#3

Re: Air Flow Calculation

12/07/2007 8:59 AM

I agree with the above posts and I would like to add some other thoughts.

Obviously the air flow rate is dependent on the differential pressure the fan is generating. If the system is operating, the pressure in the duct can be measured with a manometer. The "velocity pressure" can be measured with a "pitot tube". This can give you duct velocity. These instruments are inexpensive.

A commercial ventilation handbook will help you estimate the back pressure in a given duct system since pressure or velocity changes in duct work is well documented and repeatable.

__________________
Everything I know about opera I learned from Bugs Bunny
Reply
Guru
Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Brecksville, OH
Posts: 1621
Good Answers: 18
#4

Re: Air Flow Calculation

12/07/2007 10:22 AM

While the formula and relationships for blowers are available, I suspect the best place to get the fan curves are from the manufacturer.

__________________
"Consensus Science got us into this mess, then why can't it get us out?" : Rephrase of Will Rogers Comment
Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#5
In reply to #4

Re: Air Flow Calculation

12/07/2007 12:18 PM

If you can't find the manufgacturer's fan curve, get a fan curve of an equivalent fan from a differennt manufacturer. Depending on the accuracy needed this might be close enough for estimating purposes. (+/-20%)

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.