Previous in Forum: Roasted Coffee Bean Storage   Next in Forum: Wattmetric Relay/Torque Limiter emi 365w in Overhead Crane
Protection Relay
08/19/2021 5:18 PM
Dear all
We have feeder protection relay REF542plus the Alarm signal (coil error card1 II) it
is appeared on the the LCD display screen for the relay.when i check the manual for
relay I didn't notice this signal, but I noticed another signal, which is (trip coil
supervision) alarm.Please if anyone has worked on this relay can help me and tell
me are these two alarm is same
thanks for all
Pathfinder Tags: Protection relay
Re: protection relay
08/19/2021 7:04 PM
Yes I believe those are one in the same...
..."Some alarms might not be reset before the cause that generated it has been removed. For example, an alarm due to an error in the tripping circuit (coil supervision) cannot be reset before the tripping coil is replaced. Whereas an alarm generated by a trip of a protection function is normally reset with this procedure.(pg 30)"...
https://library.e.abb.com/public/960b5634f68f6509c12577500036873b/REF542plus_om_755869_ENg.pdf
08/20/2021 5:00 PM
thank you for your replay
please have you any idea about the philosophy of trip circuit supervision in REF542plus
relay
thanks
08/20/2021 5:14 PM
In your circumstances I can't say, use your best judgement...
08/21/2021 5:23 PM
Trip circuit supervision is to ensure that all of the necessary resources are present to actually trip the breaker if called for. It is an old concept dating back to at least the 1960s, where a very small load, ie a resistor & lamp are placed in series with the trip coil of the breaker. If a fuse opens or a loose terminal opens the tripping circuit, then you have advance knowledge that when the time comes to trip the breaker, it isn’t going to work(the light goes out). This, in US, is often a white indicating lamp.
So if you paid good money to purchase a $70,000 circuit breaker, wouldn’t you want to know if it wasn’t going to protect your power system?
These diagnostics are not foolproof, a bad connection could show a good circuit but might not carry enough current to actually trip the breaker open, for example, but better than waiting until you really need the breaker to trip.
Re: Protection Relay
08/26/2021 9:37 AM
henry98 (1); PWSlack (1); rwilliams (1); SolarEagle (2)