01/05/2022 11:18 PM

I am using Fluke Energy Analyzer Model Number 434-II and I am monitoring the Voltage on the main Bus rated for 600VAC

I see that for every point on the time line there is a Max, Minimum and average,How do I make sense of this and which one I use for comparing to see if the Voltage is fluctuating or stable.

Register to Reply
Pathfinder Tags: Three Phase AC Voltage
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Fluke Energy Analyzer AC voltage Measurement

01/06/2022 12:15 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#2

Re: Fluke Energy Analyzer AC voltage Measurement

01/06/2022 4:06 AM

From the graph it is evident that the <...Voltage...>:

  • Is not terribly <...stable...> on a second-by-second basis
  • Is <...stable...> over a 4h period

which is exactly what one might expect as loads come on and drop off, the effects of splurge, etc..

A description of the perceived problem that the equipment is being used to overcome would be helpful to the forum.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Sep 2016
Posts: 975
Good Answers: 9
#3

Re: Fluke Energy Analyzer AC voltage Measurement

01/06/2022 11:05 PM

have somebody qualified to read it for you Happy New Year everyone!

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1394
Good Answers: 107
#4

Re: Fluke Energy Analyzer AC voltage Measurement

01/07/2022 12:30 AM

You need to look at the current to see if the load is moving the voltage or if the variation comes from the source. You use the high resolution data to find that out. You don’t say what the sample time period is, so it is difficult to know if you are looking at harmonic distortion or variation at system frequency. As asked by PWSlack, why you are looking at this would be helpful for targeted guidance.