earth fault

05/30/2022 4:35 PM

dear all

on three phase busbar we have a surge capacitor on each phase ,when earth fault

happened between one phase and earth the. voltage on the phase which earthed

become near to zero but the surge capacitor on this phase exploded,my question is

why surge capacitor exploded while the voltage near to zero.

thanks

Register to Reply
Pathfinder Tags: Earth fault
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: earth fault

05/30/2022 6:10 PM

..If a high voltage greater than rated capacity is applied across capacitor, its dielectric strength will break down and eventually capacitor will explode. .. Electrolytic capacitors fail due to leakage or vaporization of the electrolyte inside. This can be caused due to heating in operation.....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
3
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#2

Re: earth fault

05/31/2022 12:26 AM

Maybe the capacitor was the earth fault. How is the system grounded? Maybe the ground fault started as an arcing ground fault and generated high enough voltages on restrike to exceed the BIL of the capacitor.

Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: earth fault

05/31/2022 7:07 AM

GA

Another possibility is some extraneous object striking the <...capacitor...> unintentionally, thereby causing internal damage and the <...earth fault...>, perhaps?

It's a little difficult to see from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2019
Posts: 29
#4
In reply to #3

Re: earth fault

06/01/2022 2:25 AM

Thanks everyone for the reply

the earth fault was due to potential transformer failure on busbar

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: earth fault

06/01/2022 5:36 AM

Then that is <...why surge capacitor exploded...>.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6
In reply to #4

Re: earth fault

06/01/2022 6:07 AM

Surge Capacitor failure is most likely due to over voltage in the same phase.

When an earth fault occurs in one phase, the voltage of the other two phases (unfaulted phases) rise temporarily. Depending on how fast the protection isolates the fault, it is possible for the surge capacitor to fail.

Failure of capacitor in the same phase as the faulted one, I can't think of.

__________________
Raghunath
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#7
In reply to #4

Re: earth fault

06/02/2022 1:45 AM

Normally the protection for a potential transformer, a high voltage current limiting E Class fuse, would clear a fault way way way before you would exceed the BIL rating of your surge capacitor. Surge capacitors applied on effectively ungrounded systems have a minimum rating line to line voltage, so that a ground fault would not impress high voltage on the device. It is possible your switchgear designer did not account for a fault during (unusual) ungrounded operation, and the surge capacitor voltage rating is too low.

There has been a similar question asked before, but never has the question of the power system grounding method been answered. If the bus section with the PT has no ground when the generator breaker is open, then the fault may have started as a ground fault, but had to escalate to phase to phase, as is often the case, before protective equipment cleared the fault.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#8
In reply to #2

Re: earth fault

06/02/2022 8:45 PM

Yes, it makes more sense when you switch cause and effect, GA.

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: