instrumentation earth

10/05/2022 12:57 PM

In our cement factory, two types are earth pits are prepared.One type is called Electrical earth.The other type is called Instrumentation earth.Instrumentation controls like PLCs and panels are connected to Instrumentation panel.Please explain me why Instrumentation earth is required and what are the items to be connected to this. What are the disadvantages if Instrumentation earth is not seperately maintained.

Thanks and Regards,

NVRSrinivas

Register to Reply
Pathfinder Tags: earthing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: instrumentation earth

10/05/2022 2:24 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
2
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#2

Re: instrumentation earth

10/05/2022 8:12 PM

To summarize the link Solar Eagle provided which is very good reading, separating the instrument earth from the electrical (safety) earth helps reduce electrical noise noise problems with sensitive electronics (instruments/process control) caused by noise sources such as motor inverters/drives or any other power conversion equipment especially those with switching converters.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: instrumentation earth

11/18/2022 6:31 AM

Because a fault on the power equipment earth/ground lead is going to be enormous in comparison with the capability of instruments to withstand, were they connected to it.

Instruments can’t withstand several tens of kiloamps. Something approaching a volcanic eruption would be expected were one to try.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply