How to improve the rating of a relay switch

10/15/2022 11:49 AM

For a radio control relay switch, the maximum output voltage to be 250VAC and the current to be 4A. I want to run an equipment with 220V and 4KW. What should I do?

Can I use this relay swith to control another higher rating relay switch without allowing any current flowing into this relay circuit?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: How to improve the rating of a relay switch

10/15/2022 12:07 PM

I use these switches to control different equipment....

https://www.amazon.com/220v-remote-control-switch/s?k=220v+remote+control+switch

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#2

Re: How to improve the rating of a relay switch

10/15/2022 11:44 PM

You can connect a 20A rated contactor, 2 pole or 1 pole, your relay switch will likely have a good enough rating for an inductive ac load to operate the contactor. The only caveat is the nature of your 4kW load, resistive, inductive, ac or dc. The coil to operate the contactor can be rated 220Vac, so the same power that you need to switch can be used to operate the contactor. Air conditioning compressor contactors are easily obtained and fairly lightweight, and should be good for your purpose.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Aug 2010
Posts: 208
#3
In reply to #2

Re: How to improve the rating of a relay switch

10/16/2022 12:19 AM

Thanks.

My case is the running circuit to be normally kept closed. The radio control device is a wireless Emergency stop button. What should I do?

Register to Reply
Power-User

Join Date: Aug 2010
Posts: 208
#4
In reply to #3

Re: How to improve the rating of a relay switch

10/16/2022 12:39 AM

Can an auxillary reply solve my problem?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #3

Re: How to improve the rating of a relay switch

10/16/2022 1:25 AM

An emergency stop button should be a manual operation....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #5

Re: How to improve the rating of a relay switch

10/16/2022 1:54 AM

An emergency stop button is not part of the control circuit, it cuts all power to the device...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#21
In reply to #7

Re: How to improve the rating of a relay switch

10/19/2022 5:31 PM

Then there’s the problem sourcing the 1200A 4000 volt 3 phase button for your coal pulverizer motor...,

Register to Reply
Guru
Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Brecksville, OH
Posts: 1621
Good Answers: 18
#20
In reply to #5

Re: How to improve the rating of a relay switch

10/19/2022 1:39 PM

I Totally Agree.

__________________
"Consensus Science got us into this mess, then why can't it get us out?" : Rephrase of Will Rogers Comment
Register to Reply
2
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#6
In reply to #3

Re: How to improve the rating of a relay switch

10/16/2022 1:36 AM

Usually, an emergency stop circuit will remove power when the actuating device fails, which in your case would require the radio signal to be on all the time. However, this may not suit your needs. You can purchase a maybe more expensive contactor, that can be reversed to have normally closed power contact, so when you apply power, the contact opens. Or an auxiliary relay with a normally closed contact could be used (as you mention) to provide a normally closed contact to keep the contactor closed, which would then interrupt the coil (actuating) circuit of your main contactor.

You still need to determine if the load is resistive or inductive, ac or dc, in order to select the correct power contactor, and decide if you need 2 pole or 1 pole circuit interruption. The coil voltage could be the same as the power system voltage, but it may not be a quick stock item to have a 220Vac or dc coil, and the contactor voltage could end up being as high as 600V, so the size may be bigger than you expect.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9
In reply to #6

Re: How to improve the rating of a relay switch

10/16/2022 11:43 AM

What happens when the contactor fails?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#10
In reply to #9

Re: How to improve the rating of a relay switch

10/16/2022 12:22 PM

It depends on whether the coil circuit opens or the contacts weld, one is OK, the other not so good. It’s all a statistical crap shoot

Contacts failing to make, armature stuck by chemical reactions or foreign bodies in the air, spring fracture, these are some of the perils we encounter. And PN junctions fused open or closed are worrisome when you apply solid state relays...

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#11
In reply to #10

Re: How to improve the rating of a relay switch

10/16/2022 12:44 PM

That's why emergency stop switches are always manual and cut all power to the equipment...a switch that cannot be depended on to work without exception, is not viable...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#14
In reply to #11

Re: How to improve the rating of a relay switch

10/16/2022 9:53 PM

One person’s definition of emergency stop can easily be another person’s minor inconvenience. With no understanding of what the perils are, and what constitutes an emergency, any of the solutions could easily be perfectly acceptable. In some cases, the measures taken to provide redundant control methods can actually reduce the reliability of the installation, or, as I have witnessed, created more dangerous situations than the original measure was intended to prevent.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#16
In reply to #11

Re: How to improve the rating of a relay switch

10/17/2022 1:46 AM

Emergency Stop Switches rarely cut all power to any piece of equipment. In many cases, power must stay on to ensure the equipment stops or ceases movement as quickly as practical, that movement determined to be dangerous. In other cases, Emergency Stop Switches can also operate as pilot devices to cause the interruption of power by devices suitable for the task at hand, such as 480V or 4160V 30A and up circuits, unsuitable for manually operated buttons.

In one production line of coordinated roller drives, significant damage to the inverters occurred due to multiple operations of ‘safety’ equipment interrupting power to the line, where the buttons were used to make it safe to enter the machinery, because they were easy and accessible. The designer incorrectly assumed that immediate power removal was the safe state, and had no concept of how the equipment would operate in practice.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#24
In reply to #11

Re: How to improve the rating of a relay switch

10/25/2022 10:24 AM

Ideally, an <...emergency stop...> circuit needs to be 2-stage reset; one wouldn't want the equipment to restart immediately on releasing the button and a 2-stage reset makes the restart a deliberate act.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Dec 2019
Posts: 160
Good Answers: 14
#12
In reply to #3

Re: How to improve the rating of a relay switch

10/16/2022 2:29 PM

SE is correct. An emergency stop function has to be a manually operated device in the circuit to be controlled. You can't rely on something controlled remotely because you can't be certain the path between the operator and the device being controlled is guaranteed to be failsafe.

Register to Reply
Power-User

Join Date: Aug 2010
Posts: 208
#13
In reply to #12

Re: How to improve the rating of a relay switch

10/16/2022 9:44 PM

Can be in both manual and remote

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#15
In reply to #13

Re: How to improve the rating of a relay switch

10/16/2022 10:05 PM

https://machinerysafety101.com/2009/03/06/emergency-stop-whats-so-confusing-about-that/

Even if you have a cat2 requirement for e-stop, reliability is held to a higher standard...and contact points fusing together is a well known frequent failure of contactors, so I should think that provision for this possibility must be addressed...so possibly redundancy is the answer here...this together with an aggressive preventive maintenance schedule should pass muster....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: Dec 2019
Posts: 160
Good Answers: 14
#19
In reply to #13

Re: How to improve the rating of a relay switch

10/18/2022 11:09 PM

I respectfully disagree: The definitions I find all imply the E-Stop must be located where the potential danger is viewable. The following imply this as well:

SOT 13850

ISO 13850 is a British standard for safety of machinery, which

• 4.4.2

An E-Stop device shall be located at each operator control station, except where the risk assessment indicates that this is not necessary, as well as at other locations, as determined by the risk assessment. It shall be positioned such that it is readily accessible and capable of non-hazardous actuation by the operator and others who may need to actuate it. Measures against inadvertent actuation should not impair its accessibility.

https://vdocument.in/emergency-stop-system.html?page=1

“1. EMERGENCY STOP SYSTEM

4. Location They should be positioned for easy access by the operator or anyone who may need to use them, however, they should not be located where their use could endanger the user. Remember that the person using the emergency stop may not necessarily be the person in danger! It may, therefore, be prudent to position an emergency stop near an adjacent machine, or machine zone in the case of a complex system, giving the neighbouring operator the opportunity to stop the machine if the operator gets into trouble. Where this is done, the zone of effectiveness of the Emergency Stop must be clearly indicated to avoid confusion.”

Remote shutdowns are just that, remote. But they aren't E-Stops they are remote shutdowns. The idea is an operator has to have a continuous view of the area where the danger exists says he's present and not remotely so.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22
In reply to #3

Re: How to improve the rating of a relay switch

10/24/2022 7:21 AM

<...wireless Emergency stop button...>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#23
In reply to #3

Re: How to improve the rating of a relay switch

10/24/2022 9:04 AM

Emergency stop switches are not allowed to be remote controlled.

They must be hard wired with nothing in between it and the main power to the circuit.It is the first switch in the control circuit.

All emergency stop switches must be in series with each other in the same control circuit.

You can have stop switches that are remote,but not Emergency Stop Switches.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#25
In reply to #23

Re: How to improve the rating of a relay switch

10/25/2022 5:14 PM

If all the emergency stop switches are in series, how do you make each and every one be the first in the circuit?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Aug 2010
Posts: 208
#26
In reply to #25

Re: How to improve the rating of a relay switch

10/25/2022 11:25 PM

https://store.clearpathrobotics.com/products/wireless-e-stop

Register to Reply Score 1 for Off Topic
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#8

Re: How to improve the rating of a relay switch

10/16/2022 7:16 AM

You just want to amplify the power handling capacity of your present control system which can easily be done without altering your remote control...

I think you can easily implement the changes on the remote controlled side by using your present remote control radio to control the existing 4A relay that in turn will drive either an added 4KW contactor relay or a solid state relay at the remote site to drive the remote equipment..

__________________
vsar
Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#17

Re: How to improve the rating of a relay switch

10/17/2022 2:29 AM

Just get a bigger switch.

Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#18

Re: How to improve the rating of a relay switch

10/17/2022 9:26 AM

I got three options for the moment.

First, use your relay to control a MCB actuator that trips an MCB of desired size.

Second, use your relay (if it does not latch) to control a more powerful latch relay.

Third, if your relay can (be made to) latch, control a contactor.

I will let you know if I get more ideas.

Good luck

__________________
The time is ......now
Register to Reply Score 1 for Good Answer
Register to Reply 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: