Best place to locate a power factor correction capacitor

12/23/2022 10:19 AM

Consider a scenario where you have 24 small 1 hp motors, that all start and stop at the same time by a single main contactor.

Each motor has a solid state relay for running the motor

They are on a single machine where all motors must start simultaneously.

Is it more efficient,in terms of reactive current,to put a large appropriate sized capacitor on the load side of the main contactor,or a smaller appropriately sized capacitor at each motor.

I think it will be better at each motor,but an engineer argues that it will not make any difference.

I understand that it would be cheaper with one large capacitor installed at the main,and I can understand his point,so I would like a second opinion on this.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9912
Good Answers: 1141
#1

Re: Best place to locate a power factor correction capacitor

12/23/2022 12:10 PM

The reactive current has to flow between the motors and the capacitor or capacitors. A capacitor has a leading power factor and a motor a lagging power factor, and upstream of that, the two cancel out to result in a lower current.

So ideally, you would want the capacitor as close to the motor as possible, but it may well not be worth the additional cost.

Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#6
In reply to #1

Re: Best place to locate a power factor correction capacitor

12/26/2022 10:35 AM

Yes! Distributing capacitors close to each motor will reduce the wiring resistance that handles both reactive and real currents. Thus less power loss will happen from just heating wires.

Also the parasitic values of real capacitors (ESR and ESL) will come into play. Capacitors distributed to one for each motor will typically result in a net lower Equivalent Series Resistance (ESR) than having one larger capacitor attached to the whole machine.

Since this is an already existing machine, space for these capacitors may not be available at each motor.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Best place to locate a power factor correction capacitor

12/23/2022 3:06 PM

There might be some corrective action needed according to distance of capacitor bank from motors...

..."Q: The manual for the my motor says to keep the capacitor at least 10 cm from the motor. Is there a maximum distance?

A: No, there is not a published maximum distance. However, anything within 1 m or so should be fine. Much farther than that, and we get away from the designed 90 degree electrical phase shift that the capacitor was sized for, since the wire itself has inductance and capacitance. As a result, the motor runs less efficiently, and therefore hotter.
Long wire runs also results in voltage drops. That would mean that the capacitor phase would have less torque (proportional to the square, or up to 2.5 power, of the voltage drop)"...

So I would try to keep the capacitors close to the motors , and use a power analyzer when testing system, check power factors under expected operating conditions for each motor...

https://www.power-electronics.co.nz/blog/power-factor-correction-understanding-the-issues/

...."The general expression for power factor is given by

{\displaystyle {\mbox{power factor}}=P/P_{a}}
{\displaystyle P_{a}=I_{rms}V_{rms}}

where {\displaystyle P} is the real power measured by an ideal wattmeter, {\displaystyle I_{rms}} is the rms current measured by an ideal ammeter, and {\displaystyle V_{rms}} is the rms voltage measured by an ideal voltmeter. Apparent power, {\displaystyle P_{a}}, is the product of the rms current and the rms voltage.

If the load is sourcing power back toward the generator, then {\displaystyle P} and {\displaystyle {\mbox{power factor}}} will be negative."...

https://en.wikipedia.org/wiki/Power_factor

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#3

Re: Best place to locate a power factor correction capacitor

12/24/2022 5:04 AM

A potential problem I see with the large common capacitor for all of the motors is if the main contactor is switched on and off and on again before the bleeder resistor on the capacitor has discharged the capacitor fully. A sudden interruption of the power like a glitch,could possible do the same thing without an anti-short cycle timer.

This could result in a large amount of current to the capacitor,possibly overloading the wiring to the capacitor or damage to the capacitor.

This is another reason for locating the capacitors at the motor.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 808
Good Answers: 65
#4

Re: Best place to locate a power factor correction capacitor

12/24/2022 5:38 AM

Having been involved not with motors but with a very large bank of triple fluro lights way back in an office block. Firstly the engineer in charge of design thought he would use non power factor corrected lights in the setup of over 300 lights.

However the current drawn from the circuit caused the multiphase breaker to trip. His remedy was to put in a bank of capacitors in an enclosure at the main switchboard however the circulating currents caused the cable to overheat and in the end we had to install 3 capacitors in each light, cheapness was costly in the end.

It is better to install the capacitors right at the motor. Are you sure that the capacitors don't serve a main purpose as a capacitor start, capacitor run unit. Or do they even provide a split phase system to enable the motor to start like a ceiling fan.

Having a large capacitor may appear economical but what happens when it fails and it will with the inductive/capacitive currents causing excessive ripple voltage. A case in point I have an AC welder with power correction capacitors of the correct voltage, ripple, capacity and heat value but they failed. when one fails the others are detrimentally effected. As a case in point the capacitors, amputee type, cost an arm and leg, from a major brand name all failed in succession leading to the breaker tripping.

In your case if one capacitor on a motor fails you have only lost 1/24 of the correction where as if a large one fails or loses quality, as they do and who ever checks them after installation with a capacity meter, all your correction is compromised and the supply current will go up. Ah yes the engineering solution tempered by a bean counter.

As in the case of the lighting bank corrected, the draw was 0.2A uncorrected it went to 0.8A per tube.

__________________
Hare today, goon tomorrow!
Register to Reply
Power-User

Join Date: Feb 2020
Posts: 482
Good Answers: 7
#5

Re: Best place to locate a power factor correction capacitor

12/25/2022 3:54 PM

Does a cap really remove reactance? Or only the measurement of it. Maybe the best location for power factor cancellation......is at the money meter.

Can a motor rotate without reactance? Does any tuned circuit, cancel the magnetic field of the coil?

A tuned circuit has the maximum amount of reactance. The maximum amount of apparent power. But we don't measure it, it measures as true power. A cap only changes the timing of the reactance. For the money meter.

__________________
Light is only half of what you think it is.
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7

Re: Best place to locate a power factor correction capacitor

12/28/2022 1:31 AM

I would go with the option of one large capacitor placed after the Power contactor just before 24 sets of cables are taken out to individual 1HP motors.

This will be economical from the procurement, installation as well as maintenance point of view.

With capacitor in circuit, the contactor will not see the reactive part of the motor current and thus may work at a little lower than its rating, working cooler and giving better life.

It is the practice to size the Power contactor for total current without the capacitor compensation (so that the facility can work even if capacitor develops problem in service and needs to be disconnected).

__________________
Raghunath
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Best place to locate a power factor correction capacitor

12/30/2022 5:20 PM

If the installation already exists and there is no penalty charge on the incoming tariff for low power factor, then the best place to put the <…power factor correction capacitor…> is on eBay.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9

Re: Best place to locate a power factor correction capacitor

01/12/2023 9:15 AM
  1. If the motors must all start together, Why a solid state relay for each motor?
  2. Regulations/Codes for 1 hp motors require an overload relay/contactor/local emergency stop in my experience, an integrated unit local to motor is often used. A local capacitor may ease the spares provision and avoid main contactor/cable rating raised by uncompensated current.
  3. Single or 3 phase not stated, SSR suggests 1 phase. Voltage not given - supposing 230 volt 1 ph suggests 100 amps for main contactor & cables, no p.factor compensation may increase main cable/contactor size. Do you allow for disconnect of single P.f. bank [fault] and operate with higher current?
  4. Capacitors required appear to be ~35 microfarad//motor. These may be easier to get and cost less all-together than cap. 24 times value.
  5. You will have to design /make control & protection/housing for a common cap. bank. Motor maker may offer integral cap. option.
  6. With 24 motors located unknown distance apart, you may subdivide circuits & p.f. caps?

67model

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10
In reply to #9

Re: Best place to locate a power factor correction capacitor

01/12/2023 10:14 AM

There is actually a slight sequential delay in the web operation,the exit end starts a few milliseconds before the rest and the rest start in sequence from the exit towards the entrance.This prevents backlash and maintains tension on the roll.

Each station or access point has an E Stop hard wired that bypasses all software.

The E stops have redundant contacts.

Tension,speed, and current sensors on each motor detect a slow or stopped or overloaded motor and stop the entire operation in the proper sequence to prevent backlash,which can still happen in a catastrophic situation such as a sudden bearing lock up,but acoustic monitoring of the bearings make this very unlikely.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: