Where to connect the PE core?

12/27/2022 6:29 AM

Our panel is supplied by a Solidly earthed transformer. The question is where to connect the PE core at the panel side for all the cables as the power system is TN-S and all incoming and outgoing cables are 5 core (3Ph + N + PE). As there are no terminals designated for the PE core of any of the cables, the panel instead has an earth bar that spans its whole length.

Register to Reply
Pathfinder Tags: PE Core Solidly earthed
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Where to connect the PE core?

12/27/2022 2:44 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
2
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#2

Re: Where to connect the PE core?

12/27/2022 11:33 PM

The Protective Earth for any power system is earthed, no matter the transformer connection or line to neutral or line to line loads. The bar is where the PE connections are made. The bar is designed to provide a convenient place that can accommodate just about any connector & bolt you may have, drill and tap or through bolt your terminal lug, and you have a nice low impedance link to work with, for any or all conductors. The conductors are all sized to conduct the available ground fault current to the power system neutral, to assure prompt tripping of the protective devices, to prevent or reduce the probability of a fire.

There is no need to segregate the PEs, as is required for neutrals for line to neutral loads. One big bar works fine.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Where to connect the PE core?

12/30/2022 5:09 PM

A qualified Electrician in the UK follows BS7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

PWSlack (1); rwilliams (1); SolarEagle (1)

Previous in Forum: Best place to locate a power factor correction capacitor   Next in Forum: 4 Pole MCB to a single phase load

Advertisement