4 Pole MCB to a single phase load

12/29/2022 4:56 AM

I only have a 4P MCB (Miniature Circuit Breaker). What would be the best method if I wanted to connect single phase load to it? 1 or 2,

Register to Reply
Pathfinder Tags: mcb
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: 4 Pole MCB to a single phase load

12/29/2022 6:06 AM

You always start with 1 for L1 live wire in, and the second is L2 and so on....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #1

Re: 4 Pole MCB to a single phase load

12/29/2022 2:13 PM

Just remove the handle tie bar...

...or you could check the load on each leg and use that circuit to balance the load if needed...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#6
In reply to #3

Re: 4 Pole MCB to a single phase load

12/30/2022 8:39 AM

??? Why would you want to allow N to turn off and leave Lx on? If it is going to trip N it seems that it must trip Lx at the same time. I would do as someone said, check the phase loads and put it on the lowest load.

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #6

Re: 4 Pole MCB to a single phase load

12/30/2022 4:23 PM

How is N going to trip, it's just a switch...it can be bypassed anyway....I don't know why you would want a neutral switched in a 120v circuit, but the application is unknown...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #7

Re: 4 Pole MCB to a single phase load

01/03/2023 4:20 AM

The neutral is switched when there is a need to carry out isolation for safety. Because the neutral is a current-carrying conductor, it is considered live, and under some circumstances (loose or missing neutral ink upstream is one example) it will carry a voltage. And voltages hurt.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#12
In reply to #9

Re: 4 Pole MCB to a single phase load

01/04/2023 12:09 PM

There is also a need in transfer switching between sources like line and generator. Which is an isolation function as well.

__________________
Most people are mostly good most of the time.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#13
In reply to #9

Re: 4 Pole MCB to a single phase load

01/04/2023 3:31 PM

In a single phase application I don't think it is necessary....Yes the original application may call for the neutral to be switched, but that would be a 3Ø circuit with floating ground...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9912
Good Answers: 1141
#2

Re: 4 Pole MCB to a single phase load

12/29/2022 1:23 PM

IMHO, I believe #2 is better. A 4P breaker is designed for a 3-phase load. In #2, the breaker sees the same current in all three phases. If only one phase carries current as in #1, the tripping circuitry may not work reliably.

Check your local Electrical Standards

https://www.quora.com/How-do-I-use-3-pole-MCCB-as-a-single-phase

https://lselectricamerica.zohodesk.com/portal/en/kb/articles/can-i-use-a-3-pole-mccb-on-a-single-phase-system

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4
In reply to #2

Re: 4 Pole MCB to a single phase load

12/29/2022 3:49 PM

I guess it depends on if you have a common trip breaker or not....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #4

Re: 4 Pole MCB to a single phase load

12/29/2022 4:36 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: 4 Pole MCB to a single phase load

12/30/2022 5:08 PM

Just follow the wiring regulations applicable to the country of installation; in the UK it is British Standard 7671, where switching the neutral has special considerations depending on application.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#10

Re: 4 Pole MCB to a single phase load

01/03/2023 11:58 PM

Most people would be less confused if you just used 2 of the 4 poles. It might appear to some that you are increasing the interrupting rating of the breaker by series connecting the contacts, and send someone off on a wild goose chase when they come across this in the future. Leaving the unused poles empty confirms that you are perhaps a Yankee, for future service. It is unlikely that on this sort of unsophisticated circuit breaker that any 3 phase balance sensing would affect the thermo-magnetic trip characteristic for a single pole load.

Register to Reply
Associate

Join Date: Jun 2011
Posts: 41
Good Answers: 1
#11

Re: 4 Pole MCB to a single phase load

01/04/2023 2:12 AM

Depends:

Four pole usually used for three phase, the fourth contact is used to 'hold' coil in 'on' position.

If contactor has also thermal overload, to use for single phase load L1 is looped back into L2; L3 is neutral; L4 not required unless used for 'breaker hold'. Thermal setting is adjusted for the load.

No thermal involved, then L1 is 'live', L2 is neutral; other two contacts are then spare. Always have full isolation of load on switch-off.

Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#14

Re: 4 Pole MCB to a single phase load

01/05/2023 6:11 AM

You can have either one or the third would be to have, similar to example 2, on phase and neutral two series contacts each. These protect from overcurrent and overload so most likely it will have similar current values on L and N. Moreover, it increases the arc breaking capacity on both wires.

__________________
The time is ......now
Register to Reply