Anonymous Poster #1

Neutral Connection For Balanced Load

05/20/2023 11:47 AM

Could you please guide me that I have LV transformer Star connected. Only 3-phase are going to panel. Star point(Neutral bus) of TR is solidly grounded. Panel has neutral bus. Also empty (No cables), No Ground cable. Reason being balanced load (Motors DOL and through VFD only). My Question: Can I make connection (Cabling) between TR neutral and Main panel Neutral, as I need 230V for ACB motor. That turning it to TNS system. Doing so any adverse effects? Any recommendation?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#1

Re: Neutral Connection For Balanced Load

05/20/2023 1:31 PM

According to BS 7671 means shall be provided for the main earthing terminal of the installation to be connected to the earthing point of the source of energy.

That means you need a conductor between Y secondary transformer point [earthed] to connect these two points. In a fault phase-to-ground case the short-circuit through earth is not sufficient to start the protection

__________________
Julius
Reply
Associate

Join Date: Feb 2017
Posts: 42
#2
In reply to #1

Re: Neutral Connection For Balanced Load

05/20/2023 3:06 PM

7anoter4 Thanks for your reply;

So what I understood, I need to bond the main panel earth bus with the Transformer neutral bus with earting/bonding conductor.

So in this case I should not use neutral conductor. That is cabling between TR Neutral and Main Panel Neutral? Actually i wanted to have 230Vac Auxilary supply in the main panel for spring charging motor of ACB. Thats why thinking to bring Neutral in the main panel. And converting Open Neutral to TNS.

Reply Off Topic (Score 5)
Anonymous Poster #1
#3
In reply to #1

Re: Neutral Connection For Balanced Load

05/20/2023 4:33 PM

Okay our actual problem is we do not have 230Vac in main panel to charge spring charging motor of ACB.
From Transformer no Neutral is coming to main panel. So what are doing manually charging the spring. And we have faced some problem doing so. So I decided to bring Neutral from transformer to Main Panel and get 230Vac just to charge the spring charging motor. Rest system will stay same. Neutral will not be distributed as all load connected is balanced. Motors 4-DOL and 8-VFD driven 90Kw each.
please assist if my understanding is not violating any code or standard practice.

Reply Off Topic (Score 5)
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#6
In reply to #3

Re: Neutral Connection For Balanced Load

05/20/2023 11:01 PM

You need to add an insulated conductor between the transformer neutral connection and the panel neutral. That is how all three phase 4 wire systems are designed and operated. It was omitted in your case because it was not necessary at the time. Use the same gauge wire as used for the phase conductors, for compatibility, or use a reduced size protected by the breaker rating for the spring charging motor. Or purchase a transformer and derive the voltage you need to run the spring charging motor.

You should have a ground conductor that is separate from the neutral conductor. That is used to carry the earth connections from your motors and equipment to the ground connection that your transformer is earthed to.

Reply
Associate

Join Date: Feb 2017
Posts: 42
#7
In reply to #6

Re: Neutral Connection For Balanced Load

05/21/2023 1:56 AM

Yes thank you I can install one Control/Auxiliary Transformer 400/230Vac on the incoming of the ACB/Trafo. This is more economical then installing a bunch of cables from Tr. Neutral to panel Neutral. Output side. Instead of bring.

Your suggestion about keeping ground conductor separate from the neutral conductor is complying to IEC Standard. Surely will take into consideration.

Thanks for your valuable input.

Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #7

Re: Neutral Connection For Balanced Load

05/25/2023 7:44 AM

Of course, doing such a thing will unbalance the phases.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Neutral Connection For Balanced Load

05/20/2023 7:03 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #4

Re: Neutral Connection For Balanced Load

05/20/2023 7:25 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Associate

Join Date: Feb 2017
Posts: 42
#8
In reply to #5

Re: Neutral Connection For Balanced Load

05/21/2023 2:02 AM

No Sir it hasn't tertiary winding, it is simply two winding Transformer 1250Kva 6.6/0.451kv dyn11.

I agree with the solution to install one Control/Auxiliary Transformer 400/230Vac on the incoming of the ACB/Trafo. This is more economical then installing a bunch of cables from Tr. Neutral to panel Neutral. Output side. Instead of bring.

Suggestion about keeping ground conductor separate from the neutral conductor is complying to IEC Standard. Surely will take into consideration.

Thanks for responding to my enquiry.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9
In reply to #8

Re: Neutral Connection For Balanced Load

05/21/2023 1:35 PM

Seems like a delta wound transformer would trap the harmonics....

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Associate

Join Date: Feb 2017
Posts: 42
#10
In reply to #9

Re: Neutral Connection For Balanced Load

05/21/2023 4:48 PM

Yes that's right, Harmonic current keep circulating in delta winding and does not reflect to utility. Its overheating effect is obvious. But our TR is already very much over sized.

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#11

Re: Neutral Connection For Balanced Load

05/22/2023 2:05 AM

NEC [NFPA 70] in USA recommends a grounding conductor between the source [of the power] grounding and the consumer grounding in any case [grounded system and ungrounded system]. The earth shall not be considered as an effective ground-fault current path. See NEC art.250.4 A and B.

IEC 60364-1 , BS 7671 or BS 7430 permits [IT system] only local grounding if the source system is ungrounded or grounded through an impedence.

__________________
Julius
Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#12

Re: Neutral Connection For Balanced Load

05/22/2023 8:29 AM

Simpler solution could be using a small 400/230V single phase transformer connected between two phases on primary side, with secondary feeding the ACB motor.

We had 3-phase (and no neutral) LV switchboards in one of the power plants.

All the single phase loads like lighting and small power are supplied using 3-phase, Dyn connected, 415/433V ratio transformers through 3-phase, 4-wire Distribution boards.

__________________
Raghunath
Reply
Associate

Join Date: Feb 2017
Posts: 42
#13
In reply to #12

Re: Neutral Connection For Balanced Load

05/22/2023 10:19 AM

Simpler solution could be using a small 400/230V single phase transformer connected between two phases on primary side, with secondary feeding the ACB motor.

Yes this is the most economical solution and time saving keeping the rest system integrity as it is. Neutral and Ground bus will remain isolated. We will surely go for this option.

Later I dig more and found in this system for single phase loads one 20KVA single phase 400/230Vac is used. But I must use another aux. TR. around 500/600VA 400/230Vac only for ACB spring charging motor. Whose primary must come from TR output.

Thanks for valuable input.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #13

Re: Neutral Connection For Balanced Load

05/25/2023 7:47 AM

Of course, doing such a thing will unbalance the phases.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Associate

Join Date: Feb 2017
Posts: 42
#16

Re: Neutral Connection For Balanced Load

05/26/2023 1:34 AM

Can anybody help me how to upload doc/pdf file to this forum. Asking to insert link??

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #16

Re: Neutral Connection For Balanced Load

05/26/2023 4:05 AM

The best way is to upload it to the cloud and put the link in a reply to the original poster, which is Anonymous Poster #1.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#20
In reply to #16

Re: Neutral Connection For Balanced Load

05/26/2023 11:28 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Associate

Join Date: Feb 2017
Posts: 42
#18

Re: Neutral Connection For Balanced Load

05/26/2023 4:56 AM

Thanks all for your technical expertise shared. Please see attached report I have finally submitted. Client intension to go with Inverter option. Kindly advice how much watt inverter would be enough for spring charging motor of ACB. I have proposed 1000W I believe it very much oversized.

Reply
Associate

Join Date: Feb 2017
Posts: 42
#19
In reply to #18

Re: Neutral Connection For Balanced Load

05/26/2023 4:57 AM
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#21
In reply to #18

Re: Neutral Connection For Balanced Load

05/30/2023 7:23 AM

<...how much watt inverter would be enough for spring charging motor of ACB...>

The forum cannot see either the label on it or the manufacturer's instructions for it, which are where the answer can be read.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Associate

Join Date: Feb 2017
Posts: 42
#22
In reply to #21

Re: Neutral Connection For Balanced Load

05/30/2023 8:17 AM

Yes you are right, I am waiting issue of WO to take spring charging motor name plate data. But so far I have seen in common range of 200W to 600W.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#23
In reply to #22

Re: Neutral Connection For Balanced Load

06/01/2023 3:18 AM

If <...in common range of 200W to 600W...> is true then <...believe it very much oversized...> would be false.

The absence of as-built documentation and maintenance manuals and procedures for this piece of kit would raise a very loud alarm here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply