High Generator bearing temperature with increase in terminal voltage

05/26/2023 4:59 AM

One of our 24MW,13.8KV STG was tripped due to the stator earth fault causing the blackout of the plant and resulting in the damage of the stator windings(U,W).

Our grid is and island grid with 3 STGs connected to the grid (2 of 24MW and one of 10MW)

The stator winding were repaired and one turn of each phase (U,V,W) was bypassed and new rotor was installed.

Rotor healthiness was tested through RSO test. However, stator windings was checked by megger test and Hi-Pot test at 17KV for 1 minute and was found ok.

At startup, we decided to check the generator through open and short circuit test. While performing open circuit test , the AVR voltages were increased manually with some steps. When the terminal voltage (Vt ) of the generator reached 11KV , the NDE (non-Driven End) Bearing Temperature increases to 425 C resulting in the tripping of turbine.

While, same test was repeated, and the same result was obtained but this time we decreased the excitation voltages which decreases the temperature of the NDE bearing protecting the turbine from tripping.

Kindly suggest what can be the real causes on the issues on the generator and what checks need to be taken before attempting another start-up??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: High Generator bearing temperature with increase in terminal voltage

05/26/2023 6:08 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2
In reply to #1

Re: High Generator bearing temperature with increase in terminal voltage

05/26/2023 7:20 AM

http://www.sumatron.com/dl/Utilization%20of%20Repetitive%20Surge%20Oscillograph%20(RSO).pdf

How do shorted-turns make themselves noticeable?

 Mostly by increased vibrations

 Vibrations sensitive to field current (VAR) changes

 Sometimes by reduced excitation capability

 Often they DON’T cause any obvious performance changes and are only found by monitoring (e.g.: flux probe and shaft voltages) and/or by testing (RSO, Open Circuit voltage, impedance, poledrop, etceteras)

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#15
In reply to #2

Re: High Generator bearing temperature with increase in terminal voltage

05/28/2023 10:36 AM

The Sumatron article is using RSO to test a rotor, they have exchanged the rotor so probably not the best diagnostic for this situation, certainly enlightening though.

Register to Reply
Associate

Join Date: Mar 2018
Posts: 31
#3

Re: High Generator bearing temperature with increase in terminal voltage

05/26/2023 8:13 PM

Dear seniors

Thank you for support

I ld like to highlight that rated machine rpm is 1800 rom and we are doing open ckt test after winding repair...

Now when voltage is 10kv then nde bearing temp remains 60 degree c while at voltage 11kv the temp rise upto 425 degree c and even a rtd on bearing is burnt out

Wat relates bearing high temp with increasing terminal voltage

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #3

Re: High Generator bearing temperature with increase in terminal voltage

05/26/2023 9:59 PM

It sounds like your rotor has too many shorted turns...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Associate

Join Date: Mar 2018
Posts: 31
#7
In reply to #5

Re: High Generator bearing temperature with increase in terminal voltage

05/27/2023 2:33 AM

We installed new spare rotor

Rso is also ok so inter turn are not there

Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#4

Re: High Generator bearing temperature with increase in terminal voltage

05/26/2023 8:21 PM

I work in instrumentation and the highest voltage I've ever handled is 440V so anything I say here might not be correct.

I suspect that at high voltages, you are getting insulation breakdown and current is flowing through the bearings. You might be getting sparks between the balls and the races, which can cause the high temperatures.

If that is the case, I would say, your bearings are already damaged and you need to replace them.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#6

Re: High Generator bearing temperature with increase in terminal voltage

05/27/2023 12:29 AM

Maybe check that your excitation current is not returning through the shaft, rather than the sliprings. A ground fault could find a nice easy return path through the huge shaft & bearings rather than the brush rigging. You should be able to verify this with a clamp on dc ammeter, like a Fluke 469.

Register to Reply
Associate

Join Date: Mar 2018
Posts: 31
#8
In reply to #6

Re: High Generator bearing temperature with increase in terminal voltage

05/27/2023 2:37 AM

Sir we have brush less excitor...the generator nde bearing is insulated....

The shaft connected to coupling generator is inly ground for complete train

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#9
In reply to #8

Re: High Generator bearing temperature with increase in terminal voltage

05/27/2023 9:53 AM

Then the only other explanation I can think of is that the repairs changed the location of the magnetic center of the rotor, so you need to move your thrust bearing. That is the only way I can think that rated air gap flux could cause a shift in rotor position.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10
In reply to #8

Re: High Generator bearing temperature with increase in terminal voltage

05/27/2023 12:11 PM

It seems like at this point the force on the thrust bearing is increasing suddenly...do you have any way to measure this thrust force?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Associate

Join Date: Mar 2018
Posts: 31
#11

Re: High Generator bearing temperature with increase in terminal voltage

05/27/2023 1:10 PM

I m thinking from another view

Due to winding repair we bypassed coio from all 3 phases and it has caused asymmetry in magnetic field distribution that cause spike in voltage and ultimately breaking down nde bearing insulation

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#12
In reply to #11

Re: High Generator bearing temperature with increase in terminal voltage

05/27/2023 1:19 PM

I think highly unlikely, especially since only reduced excitation has been applied, but easy enough to check.

You can roll the generator set at low speed allowing the shaft to float on the bearing film, and monitor the shaft axial position with a displacement laser as you apply excitation. Since it is a brushless exciter, you may have trouble getting enough field current at low speed, but it might be enough.

Register to Reply
Associate

Join Date: Mar 2018
Posts: 31
#13

Re: High Generator bearing temperature with increase in terminal voltage

05/28/2023 5:15 AM

We have started machine by degausing turbine side shaft and replacing pmg

Now no bearing temp abnormal observed

But since to handle emergency we bypassed stator coils so we ve to increase excitation to reached rated terminal voltage...now machine tripped on stator neutral over voltage as excitation voltage increased beyond 20 percent

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#14
In reply to #13

Re: High Generator bearing temperature with increase in terminal voltage

05/28/2023 10:17 AM

Please confirm if the hot NDE bearing is a thrust bearing? If not, then axial shaft position should not cause heat, I jumped to conclusion. This is the bearing on the exciter end of the generator shaft, also insulated?

A ground fault somewhere within 20% of the bottom of the stator windings could easily give you that neutral voltage. Machines that small I usually see medium resistance grounded, but you have high resistance or reactance grounded? You definitely have a ground fault, since the machine is not even connected to anything, I assume?

Before, your excitation was over 20% before observing high bearing temperature, so not sure how you think degaussing the shaft fixed anything, plus changing exciter should not have created a ground fault.

It is also difficult to believe that the pilot exciter magnetic center would develop enough force to shift the main generator shaft enough to be noticeable.

You may be forced to disable the neutral voltage relay to allow further measurements as your excitation is increased. My question is why didn’t it trip before? It makes no sense.

Register to Reply
Associate

Join Date: Mar 2018
Posts: 31
#16
In reply to #14

Re: High Generator bearing temperature with increase in terminal voltage

05/28/2023 11:10 PM

Sir NDE is journal bearing not thurst bearing

The neutral us grounded through transformer...i.e high impedance grounding

The stator of machine is repaired near slot exit area by bypassing coils...probably ground fault occured due to poor repair ..may be lack of stress grading layer overlap etc

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#17
In reply to #16

Re: High Generator bearing temperature with increase in terminal voltage

05/29/2023 12:12 AM

So your theory about high neutral voltage (because of your high reactance grounding) breaking down the bearing insulation seems like the root cause, good work!

Not enough voltage behind the ground fault to cause a problem until excitation was built up, and perhaps the voltage relay wouldn’t actuate because you in essence were solidly grounded through the bearing insulation?

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#18
In reply to #16

Re: High Generator bearing temperature with increase in terminal voltage

05/29/2023 7:41 AM

Points:-

  1. You have phase to earth voltages from a potential transformer PT. The star point voltage to ground is available from the star point [SP] ground transfo or a PT across SP grounding resistor, which appear at stator ground fault relay [SGF]. The effective star point resistance to ground [please state] & voltage will give Stator-ground current. Stator phase with lowest voltage will have ground fault - position % from star from SGF relay voltage. High Resistance ground should permit current less than will cause stator damage.
  2. You have rotor ground at drive end. What do AC and DC voltages from DE ground to insulated NDE pedestal tell you about rotor end-end?
  3. You have replaced rotor. Rotor currents should not get into bearings. Did you test rotor winding insulation to rotor before installing?
  4. Seems an old machine. Pedestal insulation is suspect. Have you measured that?
  5. Bypassing a coil does not ensure its own short-circuit does not heat.

67model

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19

Re: High Generator bearing temperature with increase in terminal voltage

06/01/2023 5:24 AM

Please confirm the original equipment manufacturer is involved with, at least, advising on this repair.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Mar 2018
Posts: 31
#20
In reply to #19

Re: High Generator bearing temperature with increase in terminal voltage

06/01/2023 5:47 AM

We confirm that OEM was invloved in repair process...repair was done by OEM recommended serving company

Register to Reply Off Topic (Score 3)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#21
In reply to #20

Re: High Generator bearing temperature with increase in terminal voltage

06/01/2023 7:35 AM

CR4 members cannot know anything about gen except your advice.

I think, from your post #13, that present situation is a stator earth fault at 20% excitation, which would be about 20% rated stator volts.

What is setting of Hi-R stator earth fault relay causing trip? [It seems you have star earth by single phase power transfo with secondary resistor, not resistor & parallel PT?] It will not be less than 5% of 13.8 kV- it suggests you have stator earth fault 20% or more from star point at much less than rated volts. This suggests a serious stator problem.

With brushless excitation there should be no interaction between rotor and stator circuits - why was PMG changed?

Bearing temperature 425 'C seems odd - NDE journal temp indicator range would usually be 150 -200 'C max. Also 425 'C is above melting point of white metal, but you give no report of bearing replacement or any inspection of NDE journal, if only to check NDE journal to ground insulation and/or shaft/bearing shell condition.

Effect of AC on NDE temperature amplifier is unknown. Maybe DC pulse from spark-over stator to rotor at one instant in rotation?

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22
In reply to #20

Re: High Generator bearing temperature with increase in terminal voltage

06/13/2023 7:09 AM

Then there will be a commercial warranty as part of that process. If it isn't right, get the OEM back in to sort it out.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856