Time delay for power contactor

07/05/2023 10:49 AM

The concern here is that if a fault occurs at the motor terminals, the bus voltage may drop, causing the power contactors in motor feeders to fail because the holding power to the contactor comes from the same bus. Is there a ready-made product for applying a temporal delay to these contactors?

Register to Reply
Pathfinder Tags: contactor Time Delay
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Time delay for power contactor

07/05/2023 4:16 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Time delay for power contactor

07/06/2023 5:12 AM

In a well-designed system, a <...fault at the motor...> should operate either its overload protection device, or the circuit protection device, and disconnect it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2012
Posts: 1071
Good Answers: 92
#3

Re: Time delay for power contactor

07/06/2023 7:46 AM

If the bus is appropriately sized and the feeds to the motors are appropriately fused, that shouldn't be an issue as the breaker should trip out before the fault draws enough power to drop the voltage to a point where the contactor coils drop out.

I don't see how a time delay will add any additional latching time for the coils in the event this does happen, as that scenario is supply dependent not signal dependent.

If your concern is that the power fluctuations caused by such a fault could create this problem before the breaker trips out, then you need to isolate the power supply to the contactors so that can't happen. For a real band-aid fix, maybe a zener diode then capacitor before the contactor signal switching??

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Time delay for power contactor

07/06/2023 11:05 AM

...or trickle-charge a battery off the <...110VDC bus...> and use that to power the circuits feeding the <...power contactors...>, thereby making an uninterruptible power supply for them.

If, that is, a suitable piece of equipment is not available off-the-shelf.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#5

Re: Time delay for power contactor

07/06/2023 11:06 AM

For large motors that you don’t want to disconnect during a transient event, it has been longstanding industry standard to use dc coils on the contactors, and adding time delay undervoltage release protection to the contactor control. The motor doesn’t separate from the supply during transient events.

If you have an ac coil for your contactor, you can count on it dropping out at 63% of its rated voltage in one cycle. If you use a time delay relay to hold the run signal on, the contactor can open and then reclose, likely out of synchronism, which may not be desirable. VFDs now will commonly resynchronize before connecting to a spinning motor, if you select it in the operation parameters.

For the same starter, a dc coil will drop out at about 20% of its rated voltage. For big dc coils, holding resistors are often added to reduce power dissipation after the contactor has closed, taking advantage of the increased mechanical holding capacity.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Time delay for power contactor

07/06/2023 11:08 AM

So there's any number of ways of solving the problem, as usual.

Things are a bit easier in the DC domain, too.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7

Re: Time delay for power contactor

07/06/2023 12:16 PM

A fault involving only one of the poles (to ground) should not cause a problem to voltage profile as the fault current is low.

If the fault is between +ve and -ve poles, the current will be large and the MCB sizing is such that the MCB (upstream of the Contactor) opens the circuit faster than the Contactor.

Coordination between MCB and the Contactor is part of the design and ensures that for any current beyond the safe magnitude level for the contactor, the MCB interrupts even before the contactor opens.

If there is a limitation in terms of MCB operating speed, it is better to consider HRC fuse.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#8

Re: Time delay for power contactor

07/06/2023 2:57 PM

You can use a Time delay relay the contact of which can control the supply voltages to coils of the main contactors...

The time delay relays that are commercially available, depending on the models can have adjustable time delay as well...

A sample of similar time delay relay that I've used back in the 70's as shown...

__________________
vsar
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: Time delay for power contactor

07/07/2023 6:09 AM

That presupposes that the upstream supply is already resilient to the impact of a <...fault occurs at the motor terminals, the bus voltage may drop...>. Otherwise, there is nothing to gain by using them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JNB (1); PWSlack (4); raghun (1); rwilliams (1); SolarEagle (1); vsar (1)

Previous in Forum: Exciter Vibration   Next in Forum: Bizarre Behavior From Incandescent Neon Lamp

Advertisement