Circuit Breaker Selection using IEC 60909

02/08/2024 8:55 AM

How can the short circuit results be utilized for choosing the appropriate circuit breaker? Consider parameters such as I"k, Ik, and Ip

For MV Circuit breakers,

Im of breaker > Ip (from short circuit results)

Ib of breaker > Ik or Ib calculated (from short circuit results)

For LV Circuit breakers,

Ics > Ik"

Im > Ip

Icw > Ik

Is my understanding right?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Circuit Breaker Selection using IEC 60909

02/08/2024 10:27 AM

A1) Use the appropriate national electrical standard. In the UK, for example, it is BS7671.

A2) If in doubt, consult a qualified local Electrician, who will be able to calculate, install, test and certify when complete.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Circuit Breaker Selection using IEC 60909

02/08/2024 3:30 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#3

Re: Circuit Breaker Selection using IEC 60909

02/09/2024 1:02 AM

Older Yanks use ANSI values, as those were the ones the equipment was tested to, using terms as shown by SE in his reply.

In broad terms, ANSI C37, I believe,

The medium and higher voltage equipment was tested for momentary withstand, which includes the asymmetrical component, and the interrupting rating had to exceed the value the system could deliver at the time of interruption, for instance 2Hz or 5Hz from sensing of 3 phase bolted fault with all generation on line. The X/R ratio is calculated from local generation values, using the subtransient reactance of the connected machines.

For low voltage, <600V, the interruption value is taken to be the symmetrical value only, braced for the asymmetrical forces.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Circuit Breaker Selection using IEC 60909

02/16/2024 6:35 AM

One could always discuss <...the short circuit results...> with the <...circuit breaker...> supplier. Telephone, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PWSlack (2); rwilliams (1); SolarEagle (1)

Previous in Forum: HT Motor with GRR Control Tripping on Over Current   Next in Forum: Ground Grid Rods

Advertisement