HT Motor with GRR Control Tripping on Over Current

01/31/2024 1:56 PM

We have a 750 kW, 3-phase AC induction motor for the preheater fan in our cement plant. It has a grid rotor resistance panel for speed control. It is observed sometimes whenever the speed is changed using GRR (from one step to the other step), the motor trips on over current. It is observed all 3 phase currents are high and almost equal. The speed of the motor is changed in 27 steps from 600 RPM to 990 RPM. The GRR is controlled by the Siemens-7 200 microcontroller. Many times it tripped on over current during changing of speed from one step to another step. sometimes it tripped when it is run constant speed also. What is the problem?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: ht MOTOR WITH GRR CONTROL TRIPPING ON OVER CURRENT

01/31/2024 3:28 PM

How long has this system been in service, and what are your planned maintenance procedures...? ....because it sounds like you need a rebuild...and if it's a recent install, it sounds like something is undersized, or poorly installed...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2
In reply to #1

Re: ht MOTOR WITH GRR CONTROL TRIPPING ON OVER CURRENT

01/31/2024 4:28 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#3

Re: ht Motor with GRR Control Tripping on Over Current

01/31/2024 11:26 PM

Has this ever worked correctly & reliably?

When the rotor is short circuited, full speed, how does the actual current compare to the rated current?

Was your controller designed to operate at part speeds, such as continuous energization of the resistance elements? As they heat up, the resistance can change, shifting the breakdown torque of the motor.

Are the grids covered in cement dust, preventing the cooling designed into the original installation?

Can you verify that all of your steps are closed transition? Open circuit reduces your pullout torque significantly.

If the slip rings open circuit, the slip becomes very high, causing large stator currents.

Have you checked the resistance of each step? Are the resistances balanced for each phase?

Your fan air temperature has a very large effect on the load shown to the motor at any given speed. If the air cools off during the run, the rotor could start slipping in the air gap, drawing huge currents for apparently no reason.

What is the condition of your inlet vanes/damper, if you have leaves that are loose, unlinked, or plated over with caked in dust, these could shift position on your speed run-up, causing load upsets.

Keep in mind that the torque capability of your motor is directly linked to the secondary resistance. If the fan torque, changing at the square of the speed, exceeds the torque available from the motor, then you will get overcurrent.

Register to Reply Score 1 for Good Answer
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#4

Re: ht Motor with GRR Control Tripping on Over Current

02/01/2024 7:50 PM
__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#5
In reply to #4

Re: ht Motor with GRR Control Tripping on Over Current

02/01/2024 8:16 PM

After I posted my message, I realized that the Step 7 was probably being used as a PI or PID controller for the air fan, so wanted to add one more question, did someone recently adjust the Integral on the controller?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: HT Motor with GRR Control Tripping on Over Current

02/06/2024 5:16 AM

The power drawn by any <...fan...> is proportional to something like the cube of the tip speed. So changing from <...600 RPM...> to <...990 RPM...> will involve a factor of (tap, tap tap, press equals) about 4.5 in the current, assuming constant supply voltage.

The electrical installation needs to be assessed as to whether or not it is up to the task, which includes the motor rating, the cables feeding it, the motor protection arrangements, and the upstream feeder as well as the <...GRR...> panel.

If in doubt, consult a qualified local Electrician.

The <...problem...> would seem to be a reluctance to do this, for reason(s) unknown.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 6 comments