Grid Connected System Still Importing Power from the Grid

04/28/2024 7:43 AM

Hello

I'm curious about why a solar inverter continues to draw a small amount of energy from the grid even when the solar panels are producing sufficient energy for both immediate use and storage.

is it normal ? or do I need to change some settings ?

Best regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#1

Re: Grid Connected System Still Importing Power from the Grid

04/28/2024 11:01 AM

I think the reason is that any solar inverter that operates in parallel with the Grid could continue to operate if the Grid was disconnected and so cause problems.

If a Grid employee disconnects to do work, a part which should be dead is not and could be dangerous & there would be no way to turn off except by stopping power in many homes with solar power & inverter.

Consequently, it is part of the spec. for solar inverters that they go off-frequency when disconnected from Grid & consequently shut themselves down on "Off frequency protection".

If they continued operation there is the question of how they would behave if out of frequency or phase when Grid came back - they could blow fuses or fail & short the Grid supply - there is no mechanism to synchronise across a breaker that recloses to the Grid.

To keep inverter synchronous with Grid, a small power must be drawn, in effect the inverters are always trying to push off-frequency.

Register to Reply Good Answer (Score 3)
Associate

Join Date: Feb 2019
Posts: 40
#5
In reply to #1

Re: Grid Connected System Still Importing Power from the Grid

04/29/2024 10:13 AM

Thanks for your answer

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #5

Re: Grid Connected System Still Importing Power from the Grid

04/29/2024 5:59 PM

Hello Amineln,

Unusual to get a thanks [or often, a reply] from the original poster. It makes the day!

Raghun adds a very important point - the reactive power still has to come from the Grid, with an associated current. This is because the solar inverters are required to deliver AC at unity power factor.

Even if your load power factor is 0.95, the reactance side of the right angle triangle is √[12 - 0.952] = 0.31. The lagging or leading part of the total current is over 30 %. That is not negligible when the Vars are measured.

You are most likely on a domestic type supply of 400/230V from a 3 phase transformer. Keeping your supply close to 230V, [+/- 6% ideally] depends mostly on the regulation of the transformer. Regulation is very good [0 to - 2% at rated current unity to 0.95 lead or lag] if power factor is close to unity but swings to +/- 4% for zero power factor.

So requiring solar inverters to work at unity power factor has minimum effect on voltage regulation & transfo supplying your reactive load is what it would do without any local generation.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9
In reply to #6

Re: Grid Connected System Still Importing Power from the Grid

04/30/2024 9:08 AM

The local requirements [UK] G98 applying to Inverters up to 16 amps/phase [400/230 volts 50 Hz] connecting to LV network is :-

<<9.5.1 The power factor capability of the Micro-generator shall conform to EN 50438. When operating at Registered Capacity the Micro-generator shall operate at a power factor within the range 0.95 lagging to 0.95 leading relative to the voltage waveform unless otherwise agreed with the DNO eg for power factor improvement.>>

DNO is the LV network operator. EN50438 is a European standard.

Consequently, the calculation of lead/lag current at 0.95 power factor compared to total generated current.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#2

Re: Grid Connected System Still Importing Power from the Grid

04/29/2024 3:20 AM

Load consumes reactive power, in addition to active power.

In your case, while the active power is coming from solar panels, grid is supplying the reactive power that is required by load as well as the inverter itself.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Jul 2016
Posts: 1375
Good Answers: 105
#7
In reply to #2

Re: Grid Connected System Still Importing Power from the Grid

04/29/2024 7:58 PM

Off grid inverters run reactive loads all the time, so maybe draws just enough current to keep track of the grid health, though realistically, that would be less than milliamperes, perhaps not enough to complain about?

Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9914
Good Answers: 1141
#3

Re: Grid Connected System Still Importing Power from the Grid

04/29/2024 8:20 AM

I'm thinking that it might need to draw a small amount of power from the grid in order to keep it's output synchronised with the grid voltage and phase.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2016
Posts: 1375
Good Answers: 105
#4

Re: Grid Connected System Still Importing Power from the Grid

04/29/2024 9:51 AM

How much is a little power, and how are you measuring it?

What happens if you disconnect from the grid?

What is the make and model of your equipment?

Register to Reply
Active Contributor

Join Date: Apr 2020
Posts: 13
#8

Re: Grid Connected System Still Importing Power from the Grid

04/30/2024 8:56 AM

I can't say why but I would say it's normal. My monitoring system shows power flow both to and from grid in the same hour (see screenshot). I don't thing you need to change anything.

https://photos.app.goo.gl/AZyCnHc8fwkd8Fps9

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Grid Connected System Still Importing Power from the Grid

05/01/2024 8:00 AM

Ask the question "How does this thing know how to synchronise with the local power grid?"

Ask the question "How does this thing know how to disconnect from the grid so as to protect repair workers while the grid is down?"

Answers on a postcard, please.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (3); Amineln (1); Joacchim (1); PWSlack (1); raghun (1); Rixter (1); rwilliams (2)

Previous in Forum: Been Away a Long Time   Next in Forum: Vector Group of Transformer

Advertisement