Measuring High Voltage AC

06/01/2024 4:25 PM

I have an analogue 30kV ac panel meter. I want to measure up to 12kV AC voltage with it. Do I need to use a voltage divider as the same for DC? If so what would the resistance be?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Measuring High Voltage AC

06/01/2024 6:32 PM

Assuming one can safely use a 30kV rated panel meter, one can safely measure 12kV AC with a 30kV AC panel meter. Your analog panel meters will only be at about 1/3 deflection. The resolution and uncertainty won't be ideal but a measurement can be made. As the name implies, adding any voltage divider network will reduce the voltage to less than 12kV and thus farther away from the 30kV full deflection.

Unless these voltages are significantly current-limited, these are lethal voltage levels and should not touched by a novice. Significantly current-limited voltage sources must be measured by nearly ideal instrumentation to obtain an accurate result.

Please stop now before you get hurt or hurt somebody else.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Oct 2010
Posts: 76
#7
In reply to #1

Re: Measuring High Voltage AC

06/05/2024 2:11 PM

Thanks for the response to my question. It is stated 30kV. 100V. Does that mean full deflection is actually 100 volts?

I am a physicist and have been designing and building Tesla Coils for over 30 years, so I am very familiar with both high voltage and high current. But this is the first time that I actually need to measure the ac output of a HV transformer and have never used a hv ac meter before.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#10
In reply to #7

Re: Measuring High Voltage AC

06/05/2024 3:40 PM

Yes, the scale is 50kV = 100 volts. A potential transformer (PT) would be normally used, at that voltage, a capacitively coupled PT would be less, but less accuracy. You may find a 30kV rated probe for a meter, ie Fluke, for lab work, will be easier. If you know the internal resistance of the meter, you can use a voltage divider, ratio 30kV to 100V with high accuracy. Those resistors are mounted on ceramic insulators, 30kV creep distance is something you will want to look up.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#12
In reply to #10

Re: Measuring High Voltage AC

06/05/2024 9:05 PM

I forgot you just need 12kV, lots easier & cheaper to buy a standard 14400V to 150V transformer and replace the meter with a standard 150 volt scale meter, 0-150Vac. You will be far ahead of where you are now. These transformers come with HV current limiting fuses mounted on the top, so all you need is clearance.

Register to Reply
Commentator

Join Date: Oct 2010
Posts: 76
#16
In reply to #10

Re: Measuring High Voltage AC

06/06/2024 9:40 AM

Hi,

The ac voltage I want to measure is from a distribution transformer that I have rebuilt.

The actual meter is 30kV and not 50kV as in the image I uploaded. I think that the information you have supplied me will suffice. Thanks!

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#17
In reply to #16

Re: Measuring High Voltage AC

06/06/2024 11:31 AM

Here is a video of a real high voltage termination:

https://youtu.be/sQrHTU8Mtow

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#18
In reply to #17

Re: Measuring High Voltage AC

06/06/2024 11:57 AM

A simple line diagram of voltage distribution.

https://youtu.be/gpbBhZcLrWs

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#13
In reply to #7

Re: Measuring High Voltage AC

06/05/2024 10:52 PM

As others have said, the panel meter you show requires some form of a calibrated (resistive and/or transformer) network to accurately reduce the voltage at the panel meter. Redesigning another network for a different voltage ratio requires additional knowledge of the panel meter, voltage source and all leakage paths to provide accuracy. I suspect you need accuracy in your measurement. You probably should instead use a HV probe like this.

You can even get a calibration certificate if you need it.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Feb 2020
Posts: 482
Good Answers: 7
#2

Re: Measuring High Voltage AC

06/01/2024 9:38 PM

Would they feed 30KV to a panel meter?

__________________
Light is only half of what you think it is.
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3

Re: Measuring High Voltage AC

06/01/2024 11:32 PM

You normally would use a transformer. It is likely the meter is a 120Vac full scale, so your potential transformer would be 12kV to 120Vac. The transformer is designed for high turns ratio accuracy.

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#4

Re: Measuring High Voltage AC

06/01/2024 11:35 PM

Perhaps you have the meter movement for a 30KV instrument without the rest of the parts. Please show us a picture so that we can determine it. Is it in a wood box? Are there input terminals? If so what DC resistance is measured on them?

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 76
#8
In reply to #4

Re: Measuring High Voltage AC

06/05/2024 2:19 PM

Thanks for the response to my question. It is stated 30kV. 100V. Does that mean full deflection is actually 100 volts?

I am a physicist and have been designing and building Tesla Coils for over 30 years, so I am very familiar with both high voltage and high current. But this is the first time that I actually need to measure the ac output of a HV transformer and have never used a hv ac meter before.

Register to Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#11
In reply to #8

Re: Measuring High Voltage AC

06/05/2024 5:14 PM

All I see is a meter movement, you didn't answer any questions. You probably need a transformer as stated in post 3 but with 100V output @ 30KV input. Full scale on the meter shown is 50KV, not 30KV. Does it have any resistors or capacitors on the back?

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#5

Re: Measuring High Voltage AC

06/02/2024 5:18 AM

Be certain you know what you are doing,otherwise,you will be a copper splattered shadow on the enclosure wall.

30Kv does not play,and rarely gives second chances.I know one person that survived a 13,200 volt short,because it blew him backwards away from the bus bars,but it flash blinded him for several weeks and peppered his body with molten copper.

Asking your question makes me question your qualifications.Have you ever seen a high voltage fault?Imagine a stick of dynamite exploding and it will be close to the result.

I have seen a complete substation tower fed by 13,200v melt down to the ground,with large I beams turned into molten metal puddles.A chain link fence surrounding the substation had a bulge of a worker running away.

You could really see the outline in the fence wire.

There are plenty of old electricians,and plenty of bold electricians,but there are no old,bold electricians.Be very careful.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Oct 2010
Posts: 76
#9
In reply to #5

Re: Measuring High Voltage AC

06/05/2024 2:21 PM

Thanks for the response to my question. It is stated 30kV. 100V. Does that mean full deflection is actually 100 volts?

I am a physicist and have been designing and building Tesla Coils for over 30 years, so I am very familiar with both high voltage and high current. But this is the first time that I actually need to measure the ac output of a HV transformer and have never used a hv ac meter before.

Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#6

Re: Measuring High Voltage AC

06/02/2024 8:41 PM

I've never seen or heard of a 30kV panel meter. It is probably a panel meter that accepts a much smaller voltage (say 100V or even 10V)and the panel face is just scaled to read 30kV maximum.

I suggest you test the meter with smaller voltages first to find its maximum deflection voltage. Then choose a step down transformer for 30kV to 100V (or whatever the max deflection volt) and connect it to the meter. A 30kV stepdown transformer, however, isn't small and wouldn't be installed in the monitoring panel.

30kV is much too high for someone who is inexperienced (as I assume you are). Better to give the job to someone who knows what he's doing.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#14

Re: Measuring High Voltage AC

06/06/2024 9:17 AM

I am presuming you are measuring a low power high voltage source, such as the 25kv on old analog televisions, not a high current source like on the electrical grid.

If so this changes the recommended measurement methods.

The Fluke probe above is a good method for such voltage, If the voltage source is a low amp capacity short circuit type, like a spark plug ,etc.

These voltages will hurt, but not vaporize you upon contact like a utility type HV transformer. You did not specify the source of high voltage, so I took the safe presumption for safety.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 76
#15
In reply to #14

Re: Measuring High Voltage AC

06/06/2024 9:34 AM

The ac source is from a distribution transformer that I have rebuilt.

Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#19

Re: Measuring High Voltage AC

06/09/2024 5:32 AM

Hello all, I'm wincing at this thread. Asking an anon forum about 30kV metering, providing a picture of an obviously LV panel meter and then comment about having rebuilt a transmission network transformer.

I'm wondering about the insulation tests on the transformer, the connection quality (not the resistance, but the actual shape of the joint), and a heap of other concerns.

To the OP, PLEASE (yes in caps) engage a suitably qualified professional in this field and even pay them some extra to involve you as they do the necessary verification of the work. Having them independently verify your work and provide feedback will assist you to move forward in this field.

I support your enthusiasm and with time, you may become one of those suitably qualified professionals.

I worked on HV for use in underground, gassy coal mines.

__________________
Just an Engineer from the land down under.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#20

Re: Measuring High Voltage AC

06/09/2024 7:56 AM

Here is a high voltage explosion and a mere 480v explosion arc.

https://www.youtube.com/watch?v=k41zThvzqc0

https://www.youtube.com/watch?v=2Xoyb9M5-EA

I repeat,BE VERY CAREFUL.

All analog meters work on milliamps,internally,so internal resistance of meter must be known to calculate proper v/a applied to meter.Applying 30kv to a meter is very silly and dangerous.

Is your life insurance paid up?

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Haymaker (1); HiTekRedNek (5); Just an Engineer (1); Manfred2 (5); redfred (2); rwilliams (3); StandardsGuy (2); Vulcan (1)

Previous in Forum: Transformer Coordination   Next in Forum: MV/LV Transformer Winding Configuration

Advertisement