In ABB relays,
What is the meaning of 1 out of 3?
What is the meaning of start value multiplier?
Re: ABB Relay Parameters
08/06/2024 5:33 AM
A1) It looks as though only one phase is being used, though a phone call to <...ABB...> would confirm it (invitation declined), or perhaps a look at the wiring diagram for the equipment, which has been withheld from the forum.
A2) -
08/06/2024 7:35 AM
Only one of the 3 phases is used to energize the relay.
08/06/2024 10:49 PM
Yes. And the energy it takes to do that is printed on the label of the device...Watts, Amps and/or Volts.
08/06/2024 11:51 AM
..."According to the standards, the relay should start once the energizing current exceeds 1.3 times the set start current when the normal, very or extremely inverse time characteristic is used. When the long-time inverse characteristic is used the relay should start when the energizing current exceeds 1.1 times the set start current."...
https://library.e.abb.com/public/eccfd9ab4d23ca1dc125795f0042c8db/DAHandbook_Section_08p02_Relay_Coordination_757285_ENa.pdf
08/06/2024 1:33 PM
Some good info there,Thanks for the link.
08/06/2024 12:33 PM
RTFM!
08/06/2024 1:35 PM
Only as a last resort.
08/06/2024 1:36 PM
Last words of a Rednek:"Hold my beer and watch this."
08/07/2024 1:26 AM
Those are not ABB proprietary terms, they are very normal English words that can only be interpreted within the context of the subject relay equipment. So without the model number of the relay, any response is totally guesswork. You will need to read the manual after all.