08/09/2024 3:57 AM
I want to select a suitable threaded rod for cable tray of 600mm width and 75mm height, length 1.5 m and weight is 19.6kgs.
Weight of 1.5 meters length of 17 cables laid on cable tray is 25.7kgs.
weight of 2 numbers of 40x40x5mm size, horizontal GI angle of length 700mm is 5.8kgs.
Total weight including cable tray, cable and GI Angle is 51.1kgs.
(We consider, 4 no's of 2 meters length threaded rod where weight on each threaded rod is 51.1kg/4 no's, is equal to 12.775kgs on each threaded rod).
As per threaded rod manufacturer's technical data sheet, the yield strength of 8mm threaded rod is 475.63 N/mm2.
I have to justify to my client that the selected 8mm threaded is suitable for my application.
Please help me with a suitable calculation.
( I am stuck with the units measured where we have calculated the total weight in KG and according to Technical data sheet the unit is in N/mm2.)
Pathfinder Tags: Cable Tray Threaded Rod
Re: Cable Tray Threaded rod calculation
08/09/2024 4:46 AM
8 mm diameter is π x 4x4 square mm
Just divide number of Newtons by 9.81 to get kilograms.
So approximately 50 x 50 = 2500 Kg
You're well in.
Good Answers: 137
08/09/2024 6:21 AM
Just a couple of comments
π x 4x4 = 50mm^2 is quite a bit more than the actual stress area 36.6mm^2
and you wouldn't design on the yield strength
But still well in for the actual load
Good Answers: 27
08/10/2024 8:26 AM
Although the chosen tray specification is well beyond the application safety requirement, the customer may have have some cost constraints and limitations that need to be factored in and considered..
vsar
Good Answers: 137
08/10/2024 9:15 AM
I wouldn't think you'd go below M8 rod for practical reasons, but without knowing the details of the job, it seems a bit odd to hang the trays on 2m of threaded rod.
Good Answers: 27
08/10/2024 9:44 AM
I concur as you noted without knowing the details of the job, it seems a bit odd to hang the trays on 2m of threaded rod.
vsar
Re: Cable Tray Threaded Rod Calculation
08/10/2024 10:50 AM
Universally in the US trays are hung with 1/2” threaded rod. Anything smaller is tough to work with, tools, handling, storage. My sympathy for you working with a client who wants you to justify threaded rod cost hanging cable tray. 2 meters of hanging is not that unusual, I would be concerned that 1/4” rod would give you very poor lateral stability. When the guys start pulling wire in the tray, that’s when those spindly M8 rods are going to be a problem.
Good Answers: 137
08/10/2024 11:04 AM
Agree, I thought lateral stability could be a problem, but without more detail...........
Good Answers: 42
08/13/2024 1:14 PM
See attached B-LINE recommended threaded rod for cable trays
Julius
Good Answers: 42
08/13/2024 1:17 PM
See:
https://www.eaton.com/us/en-us/products/support-systems/cable-tray-and-ladder-systems.html
Julius
Good Answers: 116
08/22/2024 8:54 AM
Consulting the Eaton data as suggested in post#8 is good engineering!
It has to last 30 years despite corrosion [plating quality??]. Experience matters.
In practice, it is more likely a nut will fail [stripped thread] than a rod break- calculations on area of rod given by one post are misleading - shear strength is lower than tensile. How strong is the fastening to the ceiling/wall?? - they are less predictable than a rod/washer nut etc. which are testable.
10/18/2024 11:30 AM
Here’s the rough breakdown I followed: the load per rod is about 12.775 kg, so if you convert that to Newtons (just multiply by 9.81), you get around 125N per rod. The 8mm rod I used had a yield strength of 475.63 N/mm², which was more than enough when you factor in its cross-sectional area, around 36.6mm² for M8.
10/22/2024 1:01 PM
As long as your load per rod doesn’t push that limit, you should be safe. If you’re looking for more specs or want some options, I found tecnotools.com.au to be a pretty handy source for cable tray supports.