Cable Specifications For The Power Cable

12/12/2007 7:54 AM

Dear Sir,

I want to know the optimum cross section of the cable that I should connect from 240 KW generator to the synchronizing panel and from synchronizing panel to 440V/11KV transformer. Kindly also indicate the number of runs that is required and the general specifications of the cable.

In one of my present sites I have two runs of 120 Sqmm cable from a 200 KW generator to the panel and from panel to the similar transformer. At full load the cable is getting heated up. Please suggest me a solution to this also.

Thanxs in anticipation

Register to Reply
Pathfinder Tags: Cable cross section
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cable specifications for the power cable

12/12/2007 7:59 AM

<At full load the cable is getting heated up. Please suggest me a solution to this also.>

  1. Power factor correction at the load end of the cable.
  2. Double-up the cable, i.e. add more conductors to each phase.
  3. Renew the cable with one with a larger cross-section area.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Dec 2007
Posts: 27
#2

Re: Cable Specifications For The Power Cable

12/12/2007 11:01 PM

its depend which cable you are using alluminium or copper,please write in detail

Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#3

Re: Cable Specifications For The Power Cable

12/12/2007 11:38 PM

could you please provide some more detail like length of cable from Gen to panel, panel to Trx, UG or in Air, temperature limit, Cu/Al, %VD allowed in your local regulation etc.

__________________
manirul
Register to Reply
Associate

Join Date: Dec 2007
Posts: 27
#4

Re: Cable Specifications For The Power Cable

12/13/2007 12:48 AM

one another thing please you check that there is no loose connection then also cable be heated,and alluminium cable 1sqmm is for 1 ampere only and 1amps copper cable is 4 amps and more.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#5

Re: Cable Specifications For The Power Cable

12/13/2007 4:15 AM

Hope you are an Electrical Engineer .The answer is based on that expectation . The cable manufacturers normally provide their rating depend on cable laying conditions. That is UG or OH ,Ambient temperature ,Depth of cable trench ,Thermal resistivity of soil ,ground temperature and other parameters. After considering the rating factor and specified rating of the cable manufacturer you can decide the size of the cable yourself. Only important factor is you should use only cable confirming to standard Specification and as far as possible of reputed make so that you get the correct rating as they specify.

Register to Reply
Associate

Join Date: Dec 2007
Posts: 27
#6
In reply to #5

Re: Cable Specifications For The Power Cable

12/13/2007 4:48 AM

yes sir all things is write but question is that he want cable cross section area on 240 kw load only

Register to Reply Score 1 for Off Topic
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#7
In reply to #6

Re: Cable Specifications For The Power Cable

12/16/2007 1:53 PM

Dear Sir,

What I replied earlier is that the size of the cable depend on the cable laying conditions to know the de rating factor.So please specify that then only you can select the correct size of cable .Hope you understand.If you want a proper answer your question must be complete and clear.

Register to Reply
Active Contributor

Join Date: Mar 2007
Posts: 16
#8
In reply to #7

Re: Cable Specifications For The Power Cable

12/18/2007 7:19 AM

Dear Sir,

First clarification is that I am a mechanical engineer. What I am looking for is the thumb rule for deciding the cable size. Like one of the respondent has written that 1 Sqmm of Al cable can be used for 1 amps current carrying capacity and 1 Sqmm of Cu cable for 4 amps. Can we use this as a thumb rule.

I intend using Al cable to connect up the 240 KW generator with the panel and to the sychronising panel and finally to the transformer to hook up with the 11 KV grid. The total length of the cable will be about 30 meters. Major portion of the cable will be OH with very little UG.

Can you also give me the relation between the Wattage/HP to the current rating.

Hope i have framed my question correctly for a full reply.

CDRGAR

Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#9
In reply to #8

Re: Cable Specifications For The Power Cable

04/12/2008 12:23 AM

Dear sir, please please please at lest don't apply thumb rule for cable sizing.

__________________
manirul
Register to Reply Off Topic (Score 5)
Member

Join Date: Mar 2009
Location: India
Posts: 6
#10
In reply to #8

Re: Cable Specifications For The Power Cable

03/10/2009 10:25 AM

Please visit for information http://www.relemaccables.com

Register to Reply Off Topic (Score 5)
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#11

Re: Cable Specifications For The Power Cable

04/12/2011 11:03 AM

Pls check the tightness of the cable termination. Pls lay more parallel cables per phase to increase the current carrying rate.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12

Re: Cable Specifications For The Power Cable

12/04/2013 4:20 AM

Dear Mr.cdrgar,

Pl. refer to the links below and I am sure, you will find more details, and your doubt will be cleared.

http://electrical-engineering-portal.com/general-considerations-when-choosing-power-cable

http://electrical-engineering-portal.com/cable-substation-power-plant

DHAYANANDHAN.S

Register to Reply
Register to Reply 12 comments
Copy to Clipboard

Users who posted comments:

cdrgar (1); dhayanandhan (1); joginder pal singh (3); manirul (2); PWSlack (1); relemacsales (1); sidhu16 (1); V.I.Abraham (2)

Previous in Forum: Short Circuit Calculation For Circuit Breakers   Next in Forum: Creepage Distance for 500kv Post Insulators
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement