Previous in Forum: Short Circuit Calculation For Circuit Breakers   Next in Forum: Creepage Distance for 500kv Post Insulators
12 comments
Cable Specifications For The Power Cable
12/12/2007 7:54 AM
Dear Sir,
I want to know the optimum cross section of the cable that I should connect from 240 KW generator to the synchronizing panel and from synchronizing panel to 440V/11KV transformer. Kindly also indicate the number of runs that is required and the general specifications of the cable.
In one of my present sites I have two runs of 120 Sqmm cable from a 200 KW generator to the panel and from panel to the similar transformer. At full load the cable is getting heated up. Please suggest me a solution to this also.
Thanxs in anticipation
Pathfinder Tags: Cable cross section
Re: Cable specifications for the power cable
12/12/2007 7:59 AM
<At full load the cable is getting heated up. Please suggest me a solution to this also.>
  1. Power factor correction at the load end of the cable.
  2. Double-up the cable, i.e. add more conductors to each phase.
  3. Renew the cable with one with a larger cross-section area.
Re: Cable Specifications For The Power Cable
12/12/2007 11:01 PM
its depend which cable you are using alluminium or copper,please write in detail
12/12/2007 11:38 PM
could you please provide some more detail like length of cable from Gen to panel, panel to Trx, UG or in Air, temperature limit, Cu/Al, %VD allowed in your local regulation etc.
manirul
12/13/2007 12:48 AM
one another thing please you check that there is no loose connection then also cable be heated,and alluminium cable 1sqmm is for 1 ampere only and 1amps copper cable is 4 amps and more.
Good Answers: 42
12/13/2007 4:15 AM
Hope you are an Electrical Engineer .The answer is based on that expectation . The cable manufacturers normally provide their rating depend on cable laying conditions. That is UG or OH ,Ambient temperature ,Depth of cable trench ,Thermal resistivity of soil ,ground temperature and other parameters. After considering the rating factor and specified rating of the cable manufacturer you can decide the size of the cable yourself. Only important factor is you should use only cable confirming to standard Specification and as far as possible of reputed make so that you get the correct rating as they specify.
12/13/2007 4:48 AM
yes sir all things is write but question is that he want cable cross section area on 240 kw load only
Good Answers: 42
12/16/2007 1:53 PM
Dear Sir,
What I replied earlier is that the size of the cable depend on the cable laying conditions to know the de rating factor.So please specify that then only you can select the correct size of cable .Hope you understand.If you want a proper answer your question must be complete and clear.
12/18/2007 7:19 AM
Dear Sir,
First clarification is that I am a mechanical engineer. What I am looking for is the thumb rule for deciding the cable size. Like one of the respondent has written that 1 Sqmm of Al cable can be used for 1 amps current carrying capacity and 1 Sqmm of Cu cable for 4 amps. Can we use this as a thumb rule.
I intend using Al cable to connect up the 240 KW generator with the panel and to the sychronising panel and finally to the transformer to hook up with the 11 KV grid. The total length of the cable will be about 30 meters. Major portion of the cable will be OH with very little UG.
Can you also give me the relation between the Wattage/HP to the current rating.
Hope i have framed my question correctly for a full reply.
CDRGAR
04/12/2008 12:23 AM
Dear sir, please please please at lest don't apply thumb rule for cable sizing.
manirul
03/10/2009 10:25 AM
Please visit for information http://www.relemaccables.com
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member
04/12/2011 11:03 AM
Pls check the tightness of the cable termination. Pls lay more parallel cables per phase to increase the current carrying rate.
12/04/2013 4:20 AM
Dear Mr.cdrgar,
Pl. refer to the links below and I am sure, you will find more details, and your doubt will be cleared.
http://electrical-engineering-portal.com/general-considerations-when-choosing-power-cable
http://electrical-engineering-portal.com/cable-substation-power-plant
DHAYANANDHAN.S
Register to Reply 12 comments
cdrgar (1); dhayanandhan (1); joginder pal singh (3); manirul (2); PWSlack (1); relemacsales (1); sidhu16 (1); V.I.Abraham (2)
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays