Dear all good day
please the signal (Bias control signal out of service low) appear on the CFD Common Functional Display, when we try to operation the BSDG the bsdg only cracking but there are no combustion could help us to know the source of this signal to fix it.
thanks
Pathfinder Tags: Black Star Desal Generator
Re: Black Star Desal Generator
03/22/2026 11:38 AM
Generator set manufacturer and model number of this diesel genset would be helpful.
What advice does the operations manual offer?
03/22/2026 12:07 PM
Genset model: MBH6350MD
Engine type: GE16V250
Re: Black Star Diesel Generator
03/22/2026 10:58 PM
It is highly unlikely that the bias signal out of range is the cause of the engine cranking but not firing. Fuel in the correct amount and timing and compression are the two things needed to make a diesel engine work.
The bias signal is likely linked to droop operation, but without further information, it is a useless troubleshooting tip.
Location: 1942 Broadway St STE 314C, Boulder, CO 80302, United States
10/14/2026 5:29 AM
Cranking with no combustion on a diesel comes down to fuel quantity, fuel timing or compression – the bias signal is almost certainly a red herring, since it sits in the speed/voltage droop loop and cannot stop the engine firing.
On a set that has been standing, work the fuel path first:
  • Confirm the fuel shut-off solenoid / rack actually pulls in during cranking.
  • Check the low-pressure side for a clogged or air-leaking element. A blocked or water-loaded fuel filter water separator is the most common cause of crank-no-fire after storage, and a weeping filter-head gasket or drain lets air in so the transfer pump never builds pressure.
  • Bleed the system properly, then read transfer-pump pressure at the injection pump inlet.
  • Only then check rack travel and injection timing.
As a quick confirmation: if it cranks at normal speed and you get no exhaust smoke at all, that points to zero fuel being delivered rather than a timing fault. If you do replace the element, fit a genuine coalescing type (fuel water separator filter) rather than a plain screen strainer, and re-bleed to the injectors afterwards.