Ammeter Location for Star-Delta Starter Circuit

05/04/2026 11:16 AM

Is the red rectangled area correct location for the installation of Ammeter?

This is the Electrical Star-Delta starter circuit

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#1

Re: Ammeter Location for Star-Delta Starter Circuit

05/04/2026 11:02 PM

I will answer you with a few unanswered Socratic questions. Hopefully, my questions will be better than a direct answer to your question.

What will the existing ammeter location inform an operator as they cycle through the normal operations of starting and running operations?

Will the existing ammeter location provide any useful information during an anticipated fault condition for either starting or running operation?

Will moving the ammeter to the proposed location improve or obfuscate operational and fault conditions for an operator?

Will adding a second ammeter to the proposed location, with potentially differing levels, clarify or confuse an operator during running, starting, and/or fault conditions?

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#2
In reply to #1

Re: Ammeter Location for Star-Delta Starter Circuit

05/04/2026 11:10 PM

I'm following up on my earlier questions, with the caveat that frugal, commercial conditions differ from academic or forensic conditions. In other words, adding metrology when one is unsure what will or should happen is vastly different from doing so when one knows how a system should work.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Anonymous Poster #1
#5
In reply to #1

Re: Ammeter Location for Star-Delta Starter Circuit

05/05/2026 4:15 AM

What will the existing ammeter location inform an operator as they cycle through the normal operations of starting and running operations?

I understand with the present location , can see only the current through the windings (both in Star and delta) and not the line current.

Will the existing ammeter location provide any useful information during an anticipated fault condition for either starting or running operation?

Yes, it can as the ammeter can see the current through the windings during starting (star) and running (delta)

Will moving the ammeter to the proposed location improve or obfuscate operational and fault conditions for an operator?

May be no, as the operator can see the line current (current consumption) but not the actual current when running (delta)

Will adding a second ammeter to the proposed location, with potentially differing levels, clarify or confuse an operator during running, starting, and/or fault conditions?

Yes, it can

Reply
2
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#3

Re: Ammeter Location for Star-Delta Starter Circuit

05/05/2026 12:25 AM

What is wrong with the standard location shown on your diagram? Your indicator shows the current that passes through the overload protection, giving you direct insight as to what the protection is experiencing.

Reply Good Answer (Score 2)
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 808
Good Answers: 65
#4

Re: Ammeter Location for Star-Delta Starter Circuit

05/05/2026 3:36 AM

The area marked in red would be the best position for the 3 phase ammeters using CTs. The present position of the ammeter and CT on one phase only does not give a full indication of the motor current per phase.

__________________
Hare today, goon tomorrow!
Reply
Anonymous Poster #1
#6
In reply to #4

Re: Ammeter Location for Star-Delta Starter Circuit

05/05/2026 4:19 AM

When single ammeter on one phase and three phase ammeter on all three phases would be deemed appropriate? (apart from commercial reasons)

Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#7
In reply to #6

Re: Ammeter Location for Star-Delta Starter Circuit

05/05/2026 3:32 PM

It is of little practical use. A 3 phase motor protection relay would be your best investment for a large expensive motor, so you might analyze unbalance currents and possible rotor heating. A display instrument will not have the precision needed to do a thorough analysis.

A star delta starter is rarely needed, and in itself provides usually unnecessary stress on motor windings. Much better to model your power system and find out if the reduced voltage starter is needed at all. The starter itself reduces the reliability of the process by usually unnecessarily introducing more points of failure in your manufacturing system.

Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#8

Re: Ammeter Location for Star-Delta Starter Circuit

05/19/2026 8:53 AM

I'm not an electrical guy (I'm instrumentation-mostly electronics) but I have worked on motor controls out of necessity.

In all of the motor controls I've worked on, the ammeter was connected in the location of your red box, between the contactor and the breaker. When I asked one of my electrician friends, he answered, "The ammeter is supposed to monitor the current load on the supply. Also, the meter will show you if the current is close to or exceeding the breaker setting. If the motor is operating close to or occasionally exceeding the breaker setting, you can bet that the breaker will soon trip off."

I bow to the knowledge of people who actually trained on these things. (",)

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Reply
Reply to Forum Thread 8 comments