Anonymous Poster

Motors

12/14/2007 10:40 AM

Distinguished fellow Engineers, I am an Electronic engioneer by profession. Can you please assist me understand electrical engineering. Can I stop a motor and start it again immediately.Is there a rule which specify waiting period before you can start a motor again.If i can not start the motor immediately after stopping it why doesn't the manufactutres build in this feature in the motors from the factory. The reason i am asking this question is that I was working with electrical engineers on commissioning a project, we had a 19.2A rated motor. Once we stopped it we were told to wait for an unspecified amount of time before we can restart the motor again. Help me to understand Electrical engineering.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#1

Re: Motors

12/14/2007 12:27 PM

When you start a motor the inrush current is much higher than the normal running current. This inrush current is only there for a brief period, but as you can imagine that builds up a lot of heat very quickly. Most larger motors do have motor protection equipment that will prevent a motor from being started too soon. It should show you how long until it can be restarted, as well as being able to say how many starts per hour are allowed. Searching the internet will get you a lot of info. For example here is a link to a primer on the subject:

http://baen.tamu.edu/users/stark/AGSM325_files/Lecture/6D%20Motor%20Protection%20Handout.325.pdf

Good Luck!

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Motors

12/14/2007 7:19 PM

If you have a need to start and stop a motor quite frequently, may I suggest that, depending upon the HP, torque and the RPM you need, a servo from any of the major manufacturers might be a suitable choice. I'm a Pacific Scientific fan. PacSci is now owned by Danaher. Here is a URL for you to look at.

http://www.danahermotion.com/

Rick...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Power-User
Technical Fields - Technical Writing - Validation Specialist-Medical Devices United States - Member - From the Big Apple! Hobbies - Model Rocketry - Rockets should go nuclear! Fans of Old Computers - PDP 11 - Studied computers at W.H.Taft H.S., Bronx, NY. Popular Science - Cosmology - Radio Science Observing

Join Date: Dec 2007
Location: Miami, FL.
Posts: 303
#3

Re: Motors

12/14/2007 9:08 PM

Is it OK to use a soft-start ckt.? These are availble thru Emerson...

__________________
WARNING! All suggestions are informative only. It is the prerogative of the user to implement under his sole responsibility. This commentator will not be liable for any damages or injuries incurred.
Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#4

Re: Motors

12/15/2007 7:26 AM

Motors are rated for duty cycles. As per Indian Standards I.S:325 there are various duty cycles such as S1 to S4 which means Light duty, Medium Duty, Heavy duty.......... Contineous duty.Some motors used for Hoists and Cranes are suitable for reversing operations too. Frequent On and Off heats up motors so you have to select motor according to your application. For Pumps you have to normaly select contineous duty motor.There are also FEM European Standards for motors.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#5

Re: Motors

12/15/2007 8:00 AM

Your question is a bit surprising considering that you are an electronics engineer...

The answer to your question has nothing to do with electronics. Haven't you heard the word Inertia? what about acceleration? The electric part deals with in-rush currents and is not exclusive to motors. It will be the same for any inductor. or did you skip this class?

However, serious manufacturers will specify, or supply upon request the maximum recommended number of starts per time units, and this usually be from full stop to full RPM. You can take it from there. Obviously, the bigger the motor the less start-stops you are going to have. (remember?-bigger mass bigger inertia.) Stopping the motor will be easier than starting it again. You can assist stopping with mechanical breaks, or electrically, (DC motors), In both cases heat build up is your main enemy. You did not specify if you have to reverse the motors, (CW to CCW) But if you do there's a whole lot of different rules now. It is an interesting and not so complicated subject. you will enjoy studying it.

__________________
Never trade luck for skill.
Reply Score 1 for Good Answer
Anonymous Poster
#6

Re: Motors

12/15/2007 3:59 PM

The issues are two:

*The high start current heats the motor more than the running current.

Frequent starts might result in overheating.


*The motor will experience high stress if not allowed to stop before restarting it.

Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#7

Re: Motors

12/15/2007 5:32 PM

if it is possible you can use a clutch for the mechanical transmission of power

__________________
The time is ......now
Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#8

Re: Motors

12/15/2007 5:40 PM

AT 19.2 amps and ??? volts?

Lets assume 19.2 Amps and 230V.

Although there is a duty cycle for starting and stopping, the cost of the small motor (19.2 Amps at assumed voltage of 230V) is so small, you can probably beat it up and not worry if you have adequate overload protection (and spare motors) in place.

At one extreme, a high HP AC motor (1000 + HP) may be rated for 3 "across the line" starts per hour and then a 3 hour cool down period must follow. Inrush current for starting high inertia loads can be brutal.

Now, going to another extreme, motors and drives for press feeders and veneer lathes can have extreme starting and stopping requirements in the range of 10 to 100 start/ stop cycles per minute! However, the controls involved and the design of the system is not trivial. Literally weeks of design will go into a system with a 500Hp lathe motor doing 10 start stop cycles per minute running 24/7 production. The RMS of both drive and motor has to be carefully modelled and guarantees made on production rates.

Reply
Anonymous Poster
#9

Re: Motors

12/15/2007 9:25 PM

Pump motors can be spinning backward, starting them in this state will draw even more amps and possibly trip overloads, so the control system needs a backspin delay timer to keep them from restarting too soon.

Motor application determines starting procedures, so this should be done with control systems.

Reply
Anonymous Poster
#10

Re: Motors

12/16/2007 2:23 AM

Distinguished guest #1, exactly how is it you got to be an electronic engineer without understanding electrical engineering?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Motors

12/17/2007 4:15 AM

<Can I stop a motor and start it again immediately.Is there a rule which specify waiting period before you can start a motor again.>

Yes, though there are limits for larger motors.

A motor coming up to speed consumes more current than when it is running at full speed. That means more heat is dissipated in the motor at this time, and so it will run hotter. The higher current causes the starting equipment and the cables feeding it to run hotter too. Some manufacturers of starters and motors impose constraints so that one errs on the side of caution. "Maximum 5 starts per hour" might be a typical declaration, for the simple reasoning above. Ignore it, and one is in warranty-free, uncharted waters. As to whether ignoring it is worth the risk is a judgement only able to be taken locally.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); GW (1); Kilowatt0 (1); nikolay (1); North of 60 (1); PWSlack (1); ronald (1); suresh sharma (1); wangito (1)

Previous in Forum: Non-Standard Transformer   Next in Forum: electric motors

Advertisement