Previous in Forum: wind generator   Next in Forum: Power factor correction capacitor for Single Phase and FHP motors
Close
Close
Close
15 comments
Rate Comments: Nested
Active Contributor

Join Date: Dec 2007
Location: USA
Posts: 18

6 types of 3 phase motor starters

12/15/2007 8:58 PM

Hello all--

Any of you guys out there know what the 6 types of 3 phase motor starters are?

Any help much appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: 6 types of 3 phase motor starters

12/15/2007 10:58 PM

Motor Starters are often used in conjunction with speed control of motors.

  1. Resistance- also includes liquid electrolyte resistance type
  2. Autotransformer
  3. Star-Delta
  4. Direct-on-Line
  5. Electronic Soft start
  6. Magnetic Amplifier

Those are the more common types - there are variations of the above, plus other types.....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Good Answer (Score 4)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2006
Location: Rochester, NY
Posts: 867
Good Answers: 11
#10
In reply to #1

Re: 6 types of 3 phase motor starters

12/17/2007 7:53 AM

OK, so here is the follow up question. Why would you choose one type over the other? One poster indicates that magnetic amplifiers are pretty much obsolete, why?

Now that my curiousity is peaked I'm going to have to look for a reference...

__________________
Eric
Register to Reply
2
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#12
In reply to #10

Re: 6 types of 3 phase motor starters

12/17/2007 10:18 AM

Ca1ic0cat,

For a detailed answer you need to go to the reference books. I'll attempt a short answer here. In the USA, contact any EASA motor shop.

The simplest of all is DOL (Direct On Line or "across the line" as it is usually called in the USA). It has the least number of parts and is easy to build and install. It switches the entire line (mains) voltage to the motor. Therefore it also has the highest inrush current before the motor gets up to speed and its back EMF cuts the current down to the nameplate rating.

All other types address this inrush problem with various ways of reducing the apparent voltage the motor sees (thus reducing the current the motor draws while getting up to speed).

Part-winding divides the winding into (typically) two parts with a 50-50 or 1/3-2/3 split and energizes only one at first for a timed interval before energizing the rest of the winding. This makes the motor act like it is a smaller motor for a brief time.

Wye-delta (or star-delta) types connect the windings in star form so they see a lower voltage while starting and then reconnect them into the delta form to apply full voltage after a timed interval. They are more complex than part-winding and come in two subtypes (open transition and closed transition).

Primary resistor put a resistor in series with each line lead during the initial starting period to drop voltage there and thus reduce starting current. These resistors can get very hot.

Autotransformer types use the impedance of the autotransformer instead of the resistance of a primary resistor to reduce the motor voltage.

I don't know how the magnetic amplifier types work.

With wound-rotor motors you can use a resistor on its windings to increase the impedance of the motor windings and thus reduce the starting current. In some designs this will allow variable speed. Slip rings and brushes are required to bring the rotor windings out.

When selecting the starting method (including others such as soft-start and VFD), you have to weigh factors such as motor horsepower (kW), motor type (high efficiency motors have larger inrush currents for the same output), available current, utility rules, inertia of load, starting time (with a high inertia load such as a chipper this can be as much as 2 minutes), and others.

--JMM

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Dec 2007
Location: USA
Posts: 18
#2

Re: 6 types of 3 phase motor starters

12/15/2007 11:11 PM

Sparkstation---

My hat is off to you

Thank you so much for that elusive bit of knowledge!

You know the net is a great place in general for info but when it comes right down to getting the right answer for a specific question---well you just can't beat the power of the people in these forums.

Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#3
In reply to #2

Re: 6 types of 3 phase motor starters

12/15/2007 11:16 PM

Hello quest, thank you for fast feedback response.

You're very welcome.

Learn much, help others = a good motto.....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
2
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#5
In reply to #2

Re: 6 types of 3 phase motor starters

12/16/2007 2:46 PM

Quest ,

Nothing more to add . I am very Very happy to see that you responded to the answer and thanked " Sparkstation" instantly. Very good manners which lacks in this site with most of the thread initiators. Good example. Hope others also will try to follow you.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#4

Re: 6 types of 3 phase motor starters

12/16/2007 10:38 AM

There are two main types of induction motors a) Cage b)Wound rotor also known as slip ring motor.

For cage Starters available are Direct on Line (DOL), Star delta, Auto Transformer, resistance starter, Electronic Soft starter.

For slip ring type we have stator rotor starters wher the stator is DOL and rotor through a resistance which is 100% at stand still and gradually cut down to enable motor to accelerate.Rotor resistance can be liquid type or resistance in steps made of CI, Punched steel plates etc.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Active Contributor

Join Date: Dec 2007
Location: USA
Posts: 18
#6
In reply to #4

Re: 6 types of 3 phase motor starters

12/16/2007 2:59 PM

Thanks nesubra for that extra clarification--- that will go down in my notes

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: 6 types of 3 phase motor starters

12/17/2007 12:29 AM

I wouldn't put Magnetic Amplifiers in the "most common" category. I haven't seen one used in 25 years and as far as I know there is only one company left in the world who is making them (for motor starting).

I would say that Part Winding motor starters are much much more common, at least in the US.

One could also argue that VFDs could fall into that category; they are used to start 3 phase motors after all, albeit also to change speed.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Dec 2007
Location: USA
Posts: 18
#8
In reply to #7

Re: 6 types of 3 phase motor starters

12/17/2007 12:54 AM

Point well taken JRaef,,,,

Thanks for the update

Register to Reply
Active Contributor

Join Date: Sep 2007
Posts: 22
Good Answers: 1
#9

Re: 6 types of 3 phase motor starters

12/17/2007 4:05 AM

Three phase motors do not need starters. That's what's so neat about three-phase power! Single phase motors need starters because they don't know which way to go when the power is applied. Oh, you were just trying to catch us with this trick question, weren't you -- you devil! --jer

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11
In reply to #9

Re: 6 types of 3 phase motor starters

12/17/2007 9:06 AM

???

ALL motors need starters. How else would you turn them on or off and protect them?

You are maybe referring to Starting Capacitors? They are a completely different thing (and by the way, not ALL 1 phase motor designs need them).

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#13
In reply to #9

Re: 6 types of 3 phase motor starters

12/17/2007 2:54 PM

The Motor Starters discussed here are used as " Power Switching device " which switches on Power to the motor. It is not the rotating magnetic force that provide the starting torque. They are devices that simply switches on Power to the motor.

1. Manually operated Motor Starters are used for starting fractional HP squirrel cage induction motors.

2.Direct on Line (DOL) starters are used for switching on( Starting) small capacity motors where starting current is not large. In few cases Large motors are also started with DOL starters where high starting current is not detrimental to the system.

3.In case of larger size Squirrel cage Induction motors auto transformer were used for starting where reduced voltage is supplied initially for starting and later full voltage is applied.These have become more or less redundant.

4. The later version is manual or Automatic star delta starters used for larger motors for starting where both ends of the windings are brought out and externally star connected while starting and later switched over to delta connection to limit starting current.

5.Resistance Starters are used for slip ring Induction motors for starting.In this case Resistance is connected to the rotor winding at initial starting and when the speed pick up they are manually or automatically reduced and finally rotor windings are short circuited when the motor picks up rated speed.

6.The Soft starters are the latest introduction with electronic voltage regulation for starting.They are energy saving starters

7. Magnetic Amplifiers are used for switching of SMPS ( Switch mode Power systems) They are not known to be used for motor starting purpose.

Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#14
In reply to #13

Re: 6 types of 3 phase motor starters

12/17/2007 4:10 PM

"7. Magnetic Amplifiers are used for switching of SMPS ( Switch mode Power systems) They are not known to be used for motor starting purpose."

Hello V.I.Abraham, and others,

Magnetic Amplifiers are sometimes still used for starting motors of 40MVA and above - the application of the motor was generally to be used, (with varied excitation), as a Synchronous Power Faction Correction Capacitor, used at a substation where supply lines exceeded 100 miles in length.

Very efficient in their day, many are still in use, and I saw my first one in 1962, helping to complete the installation of one, back in the days when the thyratron, (Who remembers the thyratron), was still around.

These days because more efficient methods are used, it would be rare to see one, except in the above specific type of installation.

To save me typing it all out here is some information for those interested:

[quote]

http://www.lmpforum.com/inforum/index.php?showtopic=257&view=findpost&p=693

Hereinafter is further information received from the manufacturer regarding the flux compensated magnetic amplifier (FCMA) soft starter. FCMA works on the principle of unsaturated core in the working zone, accordingly it does not generate harmonics, which is an advantage compared to the SCR soft starters.

FCMA is connected in series with the motor to provide stepless reduced voltage starter to ensure a constant low starting current with incremental voltage and torque to the motor to achieve smooth acceleration of the drive.

FCMA consists of main winding and compensating winding connected in phase opposition, so that the net flux in the core is difference between the main winding flux and the compensating winding flux.

The line current is limited and the motor voltage is reduced due to the impedance of FCMA.

As the motor speed increases, the compensating flux increases due to the counter emf feedback keeping the motor current constant, thus reducing the net flux and hence the impedance of the FCMA.

Due to the smooth decrease in FCMA impedance, the voltage across the motor increases in a gradual speed dependant ramp from the starting value (50-60%) to run value (94-98%). The increasing in motor voltage increases the motor torque to meet the load demand.

Then a bypass contactor closes to ensure full voltage running of the motor.[/quote]

So there is the distinct advantage of using the Magnetic Amplifier type of Motor Starter, refer to the absence of harmonic generation.

If you have ever seen a rotatable mass of some 40+ tons, go from standstill to around 1,000RPM in a few seconds, without "dipping the lights" you would agree that it was an interesting experience.

Kind Regards.....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#15
In reply to #14

Re: 6 types of 3 phase motor starters

12/19/2007 2:41 AM

Spark Station : Thank you for the information provided regarding "Flux Compensated Magnetic Amplifier " I wiithdraw my coments annd modify as "They are also used for Motor starting ".

Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ca1ic0cat (1); jerrymack (1); jmueller (1); JRaef (2); nesubra (1); quest (3); Sparkstation (3); V.I.Abraham (3)

Previous in Forum: wind generator   Next in Forum: Power factor correction capacitor for Single Phase and FHP motors