Could anybody briefly describe "Tertiary Piping" and why it is such an important concept if running chilled water through a high rise sky scraper or campus???
__________________
WARNING! All suggestions are informative only. It is the prerogative of the user to implement under his sole responsibility. This commentator will not be liable for any damages or injuries incurred.
Tertiary pumping has three "levels" of pumping. The first level, or primary, is constant volume pumping through the chiller's evaporator bundles. These pumps run when ever a chiller is on. Each chiller has a dedicated primary pump. The secondary pumping system is typically a variable volume scheme that is controlled with a variable speed drive based on "building" differential pressure. This is a pressure differential sensor located between the chilled water supply and return. The VFD is controlled to maintain a differential pressure setpoint. As chilled water valve(s) in various AHUs modulate to maitnain SAT setpoint, a variance in flow is required through out the building. The VFD allows the secondary pumps to respond to building load and operate in a more energy efficient manner. The secondary and primary loops are separated from each other through a "common" pipe. A tertiary system has a third level of pumping. In a building, that third level or tertiary pumping will be at the air handling units. It will be used to provide additional head to move flow through the air handler's cooling (or heating) coils. In a campus design, the tertiary pumping may be a "booster pump" located at a campus building with the primary-secondary located at a central plant that distributes water to all of the building throughout the campus through a massive system of piping located underground.
Further to what other contributors have added, one important use of a tertiary system in High Rise buildings is to reduce the effects of head pressure by incorporating heat exchangers and pumps to work at a lower pressure on the lower floors. The head pressure works out at approximately 1 bar (15psi) for each 10m (30ft) of height. This could mean something like 20 -30 bar or more at ground level for a 40 story building, increasing the cost of valves and fittings to withstand and operate at these pressures. So basically you have a tertiary circuit serving floors 1 to 20 at 10-15 bar with heat exchangers interfacing the secondary circuit and the secondary circuit serving floors 21 to 40 operating at a similar pressure.
apologies if i have rambled a bit, this is my first contribution.
Good Answers:
"Almost" Good Answers: