Why 3-Phase Motors Instead Of 2-Phase?

12/20/2007 8:25 AM

Hello; I am learning about electric motors theory and there is a question that puzzles me. Probably it has a very simple answer, but I can not see it.

I think I see the advantage of AC motors (no brushes, cheaper to produce, easy regenerative braking), and I see the problem of AC 1-phase motors (starting the spin). However I can not understand why 3-phase systems are preferred over 2-phase ones.

If I understood correctly, a 2-phase motor will start to spin by itself without problems. Cost should be similar, it just have a diferent wiring in the stator. I guess that regenerative braking can also be implemented like in 3-phase motors, reducing the frequency of the wave to produce a negative slip, right?
So, if 2-phase systems are simpler, require less cables, use simpler controls, and have the similar properties to 3-phase ones...why are 3-phase ones preferred? Efficiency maybe?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/20/2007 8:38 AM

The various encyclopaediae that offer explanations point out that 3-phase transmission transfers power smoothly 'twixt generator and load. 3-phases are the minimum needed to confer direction of rotation, and use the minimum of copper to do it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#2

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/20/2007 9:32 AM

A single or dual phase motor will work however requires a separate field coil to ensure the motor goes in the correct direction.

The most efficient is the three phase motor which does not need a separate coil to ensure proper direction.

Also, If you add all three phases, The average voltage is zero

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Power-User

Join Date: Jan 2007
Location: UK S.Northants
Posts: 485
Good Answers: 19
#3

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/20/2007 11:44 AM

the three-phase system needs the minimum amount of conductors for the maximum transmission of power for a balanced load. If you drive a lathe with a three-phase motor the torque is even over 360 degrees rotation and a better turned product will result, a two-phase motor (that's single plus capacitor or genuine two-phase) will have uneven (lumpy) torque resulting in a discernible difference in turned product, all other elements being equal. The permutations arising from three wires - ok and a neutral are incredibly useful, allowing two voltages and capable of supplying a combination of loads. You need already 3 (or 4) wires for two phases, so this is three phases for the price of two! If it was soap powder you would buy it!

Register to Reply
Guru

Join Date: Jul 2006
Location: Silicon Valley
Posts: 5356
Good Answers: 50
#9
In reply to #3

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/22/2007 2:11 AM

OK. So riddle me this... A girlfriend of mine is into pottery. Recently, we purchased a wheel. Our decision was based on the fact that one particular wheel (controlled by a foot pedal) could turn very slowly without losing any torque! This was a single-phase 110V setup. So why no loss in torque at low revs?

__________________
"Perplexity is the beginning of dementia" - Professor Coriolus
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10
In reply to #9

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/22/2007 2:19 AM

I suspect modern electronics.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jul 2006
Location: Silicon Valley
Posts: 5356
Good Answers: 50
#11
In reply to #10

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/22/2007 2:24 AM

Now Andy. Don't make me send you to the Principle again!

__________________
"Perplexity is the beginning of dementia" - Professor Coriolus
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12
In reply to #11

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/22/2007 2:33 AM

What else could be the reason, I am willing to learn!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jul 2006
Location: Silicon Valley
Posts: 5356
Good Answers: 50
#13
In reply to #12

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/22/2007 2:51 AM

Do you remember last week's phonics lesson? OK, Andy... And the word "how" means what?

__________________
"Perplexity is the beginning of dementia" - Professor Coriolus
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14
In reply to #13

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/22/2007 7:47 AM

Is this a Christmas Quiz ? or don't you now either ?

G'on, show us how clever you are, pretty please?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jul 2006
Location: Silicon Valley
Posts: 5356
Good Answers: 50
#15
In reply to #14

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/23/2007 3:08 AM

Yes it is a Christmas quiz. How do you keep the torque going when the revs drop on an electric motor. If I knew how, I wouldn't have axed the question!

__________________
"Perplexity is the beginning of dementia" - Professor Coriolus
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#16
In reply to #15

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/23/2007 4:17 AM

My apologies for thinking you were making a quiz.....

If it is a DC motor (of almost any type) or a Universal motor, then Pulse Width Modulation is a method favoured by many that allows good torque at low speed, but as to whether this has been done on this potter's Wheel, I could not say.....the AC mains would need to be rectified first......

With PWM, the motor is supplied with 100% full voltage pulses, but the width (timing) is variable from say 5% on to 95% off, to 100% on to 0% off......

I am of the opinion that there are further electronic methods for AC motors that I have never come across in detail.....maybe someone else can let us know more.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Jan 2007
Location: UK S.Northants
Posts: 485
Good Answers: 19
#21
In reply to #9

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/27/2007 11:46 AM

Vermin, I don't subscribe to any threads, but check back occasionally, so I don't know if you will read this. There is the element of gearing. Your girlfriend's wheel even when flat out will still rotate slowly compared to the motor rpm, and when rotating slowly the motor will be rotating much more quickly. I had a go at pottery once, even with the bit at the start (throwing?) which I imagine is the highest load likely to be imposed on the motor, she would not notice the lack of torque. Compare this with putting >1mm cut on steel at 1800 rpm. Regarding lack of torque, once playing with a 1ph to 3ph inverter on the bench driving a fairly chunky motor (no size given but it was a heavy lift) it was really easy to stop the motor with my hand on the very lowest ranges (speed control selected via a pot); no torque to speak of. As another point of reference I once had a treadle metalworking lathe and used it on treadle power. To do big cuts I used the backgear which gave me about 10X the torque.

Register to Reply
Guru

Join Date: Jul 2006
Location: Silicon Valley
Posts: 5356
Good Answers: 50
#22
In reply to #21

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/28/2007 3:33 AM

HUX,

Thanks for the answer. As far as I could tell the foot-pedal contained only a potentiometer. They were doing something much trickier with the torque. For example, if you grabbed the wheel and tried to stop it at low RPMs it would practically throw you across the room. It was quite impressive, because potters like to do things to their creation at very low revs.

__________________
"Perplexity is the beginning of dementia" - Professor Coriolus
Register to Reply
Participant

Join Date: Dec 2007
Posts: 2
#4

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/20/2007 6:17 PM

Thanks all for the answers, please let me know if I am getting all my facts correctly:

- A real 2-phase motor starts by itself, and you change rotation direction just exchanging phases. A +90 degree phase diference would set one direction, and -90 the other one. Is that right?

- The number of cables to deliver 3 phase is the same needed to deliver 2 phases ,because 3 phases which are 120 degrees out of phase add to 0 volts, but that's not the case for two waves 90o out of phase.

- In a 3-phase motor, torque is even along the whole rotation. In a 2-phase one, torque changes as the adition of the voltages change.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#23
In reply to #4

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/28/2007 11:32 AM

I don't really think you understand it fully, maybe I am wrong, but here goes.

Two phase motors run on single phase, a better name is split phase. They usually use a capacitor to try and get the second field to be at a max at a different time to the first field which is attached directly between phase and neutral. The turning moment is not very good and they have problems with starting loaded.....Sometimes the so called starting field is taken out of circuit once the motor is running using a centrifugal switch. Sometimes, for more shaft power, the starting cap and field are left in circuit, but need to be rated for that.....

3 phase motors have the 3 ( or multiples of 3) fields connected one per phase, the voltage maximums are 120° to each other, so that basically each field is "on" at a different time, so that the strongest field point basically rotates. This drags the so called "Squirrel (Skwirrel Kris?) cage rotor around at almost the same speed as the field rotates. The difference being the so called "slip" which varies from motor type and with load.....

Basically 3 phase have a clearly defined rotating field and single phase do not have it quite so well defined and suffer from lower starting torque because of that....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jul 2006
Location: Silicon Valley
Posts: 5356
Good Answers: 50
#25
In reply to #23

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/29/2007 2:55 AM

Ya know, if someone was to draw a graph of the fields (sine waves and their phases?), it might make it clearer.

__________________
"Perplexity is the beginning of dementia" - Professor Coriolus
Register to Reply
Power-User

Join Date: Dec 2007
Location: Sandy Eggo, Khalifornia US of A
Posts: 468
Good Answers: 1
#5

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/20/2007 10:59 PM

Efficiency is the main reason I would think. Picture an X/Y axis (positive/negative, time elapse) and put three sine waves 120 degrees apart and you will see a smaller drop off of the peak voltage than if you had only one phase. With a single phase motor you have 180 degrees of "positive" on the sine wave, this is the only time that you will enduce a voltage if I am correct. On the negative side of the sine wave nothing is going on. I guess you could almost look at it as on (positive) off (negative). 3 phase motors are always up in the positive side and most of the time right up around RMS (it has been a few years since I went over this in my apprenticeship, I hope it is not too confusing...Good luck)

__________________
Madness takes its toll, please have exact change...
Register to Reply
Anonymous Poster
#6

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/21/2007 3:51 AM

Think about disponibility. Electricity is supplied as three phase. There is not two has network, afaik. 1-phase is directly obtained from a 3-phase network with a neutral wire. But 2-phase is not.

Register to Reply
Associate

Join Date: Dec 2007
Posts: 54
Good Answers: 2
#7

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/21/2007 11:31 AM

I have always thought that three phase would always be better because the effective value of voltage would be increased sinusoidally,i.e.,for a current that varies sinusoidally with time, the effective value of amperage is the product of a common factor of 0.707(effective electromotive force).So, the efficiency of each phase would be a product of 0.707,i.e.,-first phase=0.707 total effective electromotive force,etc.+ second phase (0.707)(0.293)emf,etc

I would like to hear what you electricrical engineering people have to say......

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/21/2007 10:34 PM

Technically seen, there is no 2 phase motors, they use a single phase supply to power two separate fields, shifting the vector of one field relative to the other with a starting capacitor to simulate 2 phases....otherwise they old not self-start as there would be no rotating field....They tend to be used where not to much motor power is needed.....

3 phase motors are obtainable in much larger and more varied sizes and will self-start without capacitors and other tricks...as the 3 phases "rotate" so to say, dragging the squirrel cage rotor along with it.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#18
In reply to #8

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/23/2007 3:13 PM

Philadelphia Pennsylvania is another place that still has a number of true 2 phase systems installed from bygone days.

In a nutshell, the answer was given earlier. Many many people confuse 2-phase with 1-phase power that uses 2 hot legs. They are NOT the same thing. 1-phase motors must have something to make them spin in the first place. Polyphase motors do not. 2-phase is a true polyphase system, but true 2-phase requires 4 wires (maybe 3 if you know what you are doing). 3 phase requires 3 wires. So the benefits of smoother power and self-starting motors are compounded with the least number of wires to accomplish it.

http://www.3phasepower.org/2phasesystems.htm

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#17

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/23/2007 11:17 AM

In #4 it should read the direction of a three-phase electric motor is reversed by changing any two of its phases.

The direction of a two phase motor is determined by ? Maybe the relationship ( phase and or placement ) of the added coil ?

There are maybe three 1500kW or thereabouts two (2) phase generators driven by hydro wheels near Dubuque, IA operating today. They go thru three phase switchgear and into transformers for connection to the grid. I sold a turbine repair job there about 10 years ago.

There are many motor winding designs, look up EASA (Electric Apparatus Service Assn) www.easa.org and there links to there member sites should provide tons of info about every concievable electric motor. Another is www.Barks.com I think for Barks Publications which prints the monthly magazine "Electric Apparatus" which is the newsletter of the electric motor and switchgear industry.

You may see my ad in there also! Happy Holidays

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Register to Reply
Anonymous Poster
#19

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/24/2007 3:17 AM

Hi my friend , In general without going in depth , you should know that :

1. normally the generated power by a generatoe or transformer is 3 phase , then later it will be singlr phase when it reaches your home , so if you have already a 3 phase power , why you will chande it to single phase?? , just buy a 3 phase motor.

2. you have to know that single pase motors are used for low loads but for high loads you have to use 3 phase ones , ( for example you will not find a single phase motor 40 kw as an example ).

Register to Reply
Guru

Join Date: Jul 2006
Location: Silicon Valley
Posts: 5356
Good Answers: 50
#20
In reply to #19

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/24/2007 11:05 PM

I am looking at my toe, but no electricity is coming out of it. Am I looking at the wrong toe?

By the way - Merry Christmas!

__________________
"Perplexity is the beginning of dementia" - Professor Coriolus
Register to Reply
Power-User

Join Date: Dec 2007
Location: Sandy Eggo, Khalifornia US of A
Posts: 468
Good Answers: 1
#24
In reply to #20

Re: Why 3-Phase Motors Instead Of 2-Phase?

12/29/2007 12:03 AM

Hmmmmmmmmmm, is that why they call them kiltoewatts? OOOps, I am sorry it was kilowatts damn and to think I was trying to come up with a reason for the brown under my toenails . Happy New Years... 2008? Already?

__________________
Madness takes its toll, please have exact change...
Register to Reply
Register to Reply 25 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (6); Anonymous Poster (2); CoronaCameraMan (1); Ferris (2); HUX (2); inventorman (1); JRaef (1); lpons (1); PWSlack (1); techno (1); vermin (7)

Previous in Forum: Low Pass Filter Design   Next in Forum: Design Software
You might be interested in: DC Motor Drives, Regenerative Blowers, DC Motors

Advertisement