Moisture measurement in instrument air

01/03/2008 1:03 PM

Can anyone tell me what is reliable methods of measuring water/moisture in instrument air systems at power plants.

We use reactivated alumina dual cylinder air dryers which has worked fine but we have been having some problems with water in the instrument air supply and would like to install an on-line monitor with a 4-20ma output so i can monitor the quality of the instrument air.

__________________
Learn more, Do more , Be more
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Jul 2007
Location: 30°30'N, 97°45'W, Elv: 597 ft.
Posts: 2410
Good Answers: 10
#1

Re: Moisture measurement in instrument air

01/03/2008 5:49 PM

What levels are you talking about?

__________________
I never apologize. I'm sorry that's just the way I am.
Register to Reply
Commentator

Join Date: Oct 2007
Location: Caribbean
Posts: 79
Good Answers: 2
#2
In reply to #1

Re: Moisture measurement in instrument air

01/03/2008 5:56 PM

Well we have had instances where an operator would open a drain valve at the bottom of the Fisher pressuregulators which regulates the pressure from 100 psi down to 40 psi and get maybe a 1/4 of a small coke cup.

After that the air has water droplets in the air spray.

We have had valve positioners malfunction as a rsult of the excess water.

It is my intention to keep all the instrument air dryers well maintained, change the reactivated alumina dessicant on a regular basis, but just in case we do get abnormal amounts of water, a 4-20 ma generated alrm on the DCs would alert the operator.

__________________
Learn more, Do more , Be more
Register to Reply
Guru

Join Date: Jul 2007
Location: 30°30'N, 97°45'W, Elv: 597 ft.
Posts: 2410
Good Answers: 10
#3
In reply to #2

Re: Moisture measurement in instrument air

01/03/2008 6:05 PM

That's what I thought. I am only familiar with equip that test in the ppm range.

Although, Meeco or Ametek might make something for you. I'll do a little looking too.

Have you checked with GlobalSpec - CR4's parent?

__________________
I never apologize. I'm sorry that's just the way I am.
Register to Reply
2
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#4

Re: Moisture measurement in instrument air

01/03/2008 11:04 PM

Several chronic problems occur with desiccant dryers. The reactivation cycle may not be working, the desiccant may be plugged, but the most common reason for downstream moisture is caused by gas flow rate that is too high for the dryer. It takes time to remove the moisture, and if the flow rate is too high, not enough of the moisture is removed. There are many types of moisture measuring devices. Each type has advantages and disadvantages. For your application, I recommend a chilled mirror type. You can find all the manufacturers with a Google search under "chilled mirror hygrometer".

Register to Reply Good Answer (Score 2)
Anonymous Poster
#5

Re: Moisture measurement in instrument air

01/04/2008 12:12 AM

AMETEK has some good equipment for this.


Panametrics has aluminum oxide based sensors that are down and dirty but work well enough in this application.

Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#8
In reply to #5

Re: Moisture measurement in instrument air

01/04/2008 8:49 AM

One reason I recommend the chilled mirror type of hygrometer is that this measuring technology is a standard based on first principles. This means that it requires no calibration. Sensor based instruments such as Panametrics require periodic calibration to insure accuracy, and they do drift. Advantages the Panametrics sensor has over a chilled mirror system include faster response time and the fact that they are water specific. In this application response time is usually not an important consideration and as long as water is the highest condensable gas in your sample it will be the only gas to condense on the mirror. We have evaluated and used all types of hygrometers and make our recommendation based on many years of experience.

Register to Reply
Commentator

Join Date: Oct 2007
Location: Caribbean
Posts: 79
Good Answers: 2
#9
In reply to #8

Re: Moisture measurement in instrument air

01/04/2008 9:35 AM

Many thanks to all you folks for your assistance and guidance.

It is really refreshing to know that technical folks in the field all over the world have this cooperative spirit.

I probably should have given a bit more information on my problem:

I am the I&C engineer on a large power plant in the Caribbean.Tropical weather ( or to tease a bit , golf weather all year round) so no chance of freezing anything.

We have dual chamber Pall Trinity ( I think they may have been bought out by someone else) reactivated alumina dessicant dryers.

We do have problems with the spool valves which do the absorbing/reactivating cycles on the dryer, as a result we can have water or a heavy concentration of moisture in the instrument air system before the operator can realize he has a problem.

We even had situations where machines tripped off-line as a result of water in the air system causing pneumatic fuel valve problems.

I observed that many folks are using the refregerated-dryers now .

Has anyone out there switched from dessicant to refregerated drying and if so what has been your experience.

I know I need to fix the dryer problem but installing hygrometers will al least hel me to manage the problem until final solution

I am still looking forward to your comments and assistance.

Thanks again.

CR4 is a great help.

__________________
Learn more, Do more , Be more
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#11
In reply to #9

Re: Moisture measurement in instrument air

01/04/2008 10:26 AM

Refrigeration dryers work very well however, they have similar limitations as desiccant dryers. If you put too much air through them (exceed their capicity) the air will come out wet. You should probably start by knowing approximately how dry your air needs to be. Room air at 50% RH is about 16,000 parts per million of water by volume (ppmv) at atmospheric pressure. Air dried to -40 degrees has about 130 ppmv. Air used for critical applications can be dried to about 5.0 ppmv. As you can see, there is a substantial range.

Register to Reply
Guru

Join Date: Jul 2007
Location: 30°30'N, 97°45'W, Elv: 597 ft.
Posts: 2410
Good Answers: 10
#12
In reply to #8

Re: Moisture measurement in instrument air

01/04/2008 11:41 AM

He's talking about significant amounts of H2o. I agree with the dessicant statement. However it seems his app should allow for inexpensive monitoring of the dryer performance downstream where the negligible drift factor is easily overcome.

__________________
I never apologize. I'm sorry that's just the way I am.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Moisture measurement in instrument air

01/04/2008 3:57 AM

A factory in north-west London uses instrument air that is dried to -40degC dewpoint. If there is water at any point downstream of the dryer then there is something seriously amiss with it, and it is overdue for attention.

Fitting an additional measuring device will simply illustrate the problem, not solve it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Brecksville, OH
Posts: 1621
Good Answers: 18
#14
In reply to #6

Re: Moisture measurement in instrument air

01/04/2008 6:22 PM

Fitting an additional measuring device will simply illustrate the problem, not solve it


Definitely the case. Putting in a different measuring instrument wont repair the problem. Did the problem have a known start date; if so what happened about that time? Otherwise, I would call the manufacturer of the driers (or a competitor thereof).

__________________
"Consensus Science got us into this mess, then why can't it get us out?" : Rephrase of Will Rogers Comment
Register to Reply
Associate

Join Date: Aug 2007
Location: Va Beach
Posts: 25
#7

Re: Moisture measurement in instrument air

01/04/2008 8:43 AM

PWSlack is correct. You need to look at your system, and then install a monitor. I was researching some of the same products and have some downloaded product files that may be of intrest to you. Here's a link to Bosch Rexroth product website http://www.boschrexroth.com/pneumatics-catalog/Vornavigation/Vornavi.cfm?Language=EN&PageID=p55166 . I'll send you a couple of the files I downloaded during my research on dryer and hygrometer products.

__________________
"Twenty years from now you will be more disappointed by the things that you didn't do than by the ones you did do." - Mark Twain
Register to Reply
Commentator

Join Date: Oct 2007
Location: Caribbean
Posts: 79
Good Answers: 2
#10
In reply to #7

Re: Moisture measurement in instrument air

01/04/2008 9:36 AM

many thanks

__________________
Learn more, Do more , Be more
Register to Reply
Power-User

Join Date: Dec 2005
Posts: 125
#13
In reply to #10

Re: Moisture measurement in instrument air

01/04/2008 6:17 PM

Normally, instrument air is de-hydradrated using a compressed air refrigeration machine which dries the air to 35 dF dew point. The accumalated condensate is drained through an automatic dump valve. I would think the -40 dC would be too low, the moisture would freeze in the moisture storage tank. The air dryer refrigeration system, these are packaged units, is sized according to the capacity of the air compressor.

Hope this helps.

g scott

_______________________________________________________________________

When I ponder, Isits and thinke, sometimes I just sits.

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

agua_doc (1); Anonymous Poster (1); djacob (3); OLD F**T (1); PWSlack (1); ramorrison1 (1); TexasCharley (3); welderman (3)

Previous in Forum: Pressure Gauge   Next in Forum: Is it OK if Cat6 cable connected to RJ45 sockets?

Advertisement