Hi all,

I would like to ask two questions.

1) Why do the motor draws very high current during starting?

2) Ideally V = IR so if R is constant and V decreases so I also decreases but for motors its reverse i.e. V decrease I increases hence undervoltage protection is provided. Why is it so here?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Motor

01/18/2008 6:51 AM

V=IR yes for simple resistance.
At the instant the motor tries to start there is predominantly the resistance of the wire stopping the current the resistance is low ... the current is high. As the motor starts it generates a 'back emf' which opposes the the current flow and thus reduces it.

To demonstrate the back emf take a small dc motor spin the shaft and you will see it acts as a generator producing a voltage.

This is a simplifed explanation avoiding concepts like inductance. For a fuller explanation wait for the other guys to join in or do some searching on the web.

In simple terms anything with a big coil of wire will give a switch on surge e.g. a transformer... until the magnetic field exists the high current will flow.

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#4
In reply to #1

Re: Motor

01/23/2008 5:35 AM

I think we should also demonstrate the inertia of motor as a reason for high starting current. Say for Boiler feed pump, normally motor is started with discharge valve closed to reduce starting, keeping a little discharge through orifice.

__________________
BNDas
Register to Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#2

Re: Motor

01/18/2008 7:45 AM

Think of a motor as a generator. When you spin a generator, the faster it goes, the more Voltage you get. So, the motor generates a "back emf" Voltage which opposes the current going through the motor. When the motor gets up to speed, the back emf is almost as high as the applied voltage and the net voltage is fairly low. If you measure the resistance of a motor winding, it is fairly low so you can't use R to limit current.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: Motor

01/21/2008 7:08 AM

The induction motor may be viewed as a Transformer with a shorted secondary ie the stator the primary and rotor the shorted secondary.When a voltage is applied the circuit which predominantly inductive there is no back emf and there is a large inrush current.As the emf builds up the starting current dies down.Similar phenomenon takes place in Transformers too.If u go back to your text books it will clearly explain why and how a back emf develops in a circuit.As regards second question why current increases when voltage decreases is answered by the very equation u have stated.V=IR .Now when V decreases I has to increase to deliver the same out put.Similarly if V increases I redcses to Maintain the same power out put.The other effects of Decrease or increase in V and I in a motor is very detailed subject.The motor draws increased current till about 80% rated voltage and then it stalls unless the load is reduced correspondingly.Hope this answers your question.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

biswanath.das (1); nesubra (1); TVP45 (1); user-deleted-1105 (1)

Previous in Forum: Distribution Line Tie In   Next in Forum: Starting current and breaker and cable choice

Advertisement