Starting current and breaker and cable choice

01/18/2008 7:19 AM

By which multiplicator should the starting current should be calculated for chosing the cabling, and which breaker or fuse value should be set for a DOL 30KW smoke evacuation vent, directly connected to a generator line, for In 57Amps. In*6 seems too much an not an economical choice. I am asking this for a 380V 50Hz millimetric region.

Thanks

Register to Reply
Pathfinder Tags: breaker cable DOL electrical selection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Starting current and breaker and cable choice

01/19/2008 3:54 AM

starting current going to last for few cycles,hence no need

to size the cable for the same.i would choose cable of size

considering In*1.2.

Register to Reply
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#2

Re: Starting current and breaker and cable choice

01/19/2008 11:41 AM

I would probably fuse it for 100 amp... possibly slow-blow... but I AM NOT A POWER PERSON!! I am curious how you high power types would do it?

Bill

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Starting current and breaker and cable choice

01/19/2008 2:50 PM

Each jurisdiction, at least those with any sort of regulatory structure, will have a code in place that details what minimum and maximum ampacity those components must have.

For example... in general in Canada, motor feed conductors must be sized so that their ampacity is equal to or greater then 125% of the full load current of the motor.

You need to check with the Authority Having Jurisdiction where you live to get the requirements for minimum and maximum ampacity ratings for your location.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Active Contributor

Join Date: Jan 2008
Posts: 16
#4
In reply to #3

Re: Starting current and breaker and cable choice

01/19/2008 3:05 PM

Hi, North of!

Tell me please, do you have different ampacity regulations concerning DOL starting smoke evacuation fans from generators, versus normal, delta-star starts for non emergency equipment?

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #4

Re: Starting current and breaker and cable choice

01/21/2008 9:00 AM

Yes we do have separate regulations covering DOL vs part winding started motors.

What the regulations are in my area is not what you should be focused on. You should be focused on, IMHO, the regulations in your region.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Anonymous Poster
#6

Re: Starting current and breaker and cable choice

01/21/2008 1:10 PM

For a given nominal current In = 57A, select as wire size (#4 awg)( 21 mm2) and for a circuit breaker 100A. Thus the multiplicator would be ~ 1.8. Normally 1.5 - 1.6. This is valid for normal motors under normal starting conditions. If the starting process extends over a longer period of time, the circuit breaker size shall be increased to avoid nuisance tripping during start. It would also be a good idea to verify the manufacturer's technical specifications.

Tomad

Register to Reply Score 1 for Good Answer
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); North of 60 (2); Sciesis2 (1); Skipper_A (1)