Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member

Join Date: Mar 2006
Location: Chennai, India
Posts: 312
Good Answers: 3

SF6 or Vacuum Circuit Breaker?

04/20/2006 4:10 PM

HT Switchgears in our factory presently use MOCBs (Minimum Oil Circuit breakers).
While retrofitting these breakers, to go in for modern technology, we have the option to select either 'SF6' or 'Vacuum' interrupters.
Which is more economical?
Is it possible to get remote annunciation (visual/audio), in a control room, when the vacuum bottle gets damaged? Please advise, sharing experience of users.

__________________
nvmani
Register to Reply
Pathfinder Tags: circuit breaker technology Vacuum
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Sep 2005
Posts: 39
#1

HT Switchgears

04/21/2006 1:09 AM

You can select either SF6 or Vacuum breakers but both have advantages and disadvantage.

For SF6 Breakers there is one Red, Yellow and green lamp to indicate the SF6 pressure inside the breaker. You need to check the SF6 gas pressure inside the Breaker every month to ensure that the SF6 gas is still O.K. For Vacuum Breaker you don't need to do it because the Vacuum breaker is completed seal.

If SF6 breaker gas pressure is less, you can fill it back. But for Vacuum Breaker, if the vacuum inside the breaker leaks you can't vacuum it.

For maintenance cost you need to stand by a cylinder of SF6 gas inside your substation for filling. But for Vacuum Breaker you don't need it.

In over all, in the maintenance cost, I believe that SF6 Breaker is still cheaper than the Vacuum Circuit Breaker because Vacuum Circuit Breaker does have any limited operation life. For Vacuum Circuit Breaker, there is limited operation life. You need to change all the Vacuum breaker poles if the operation life is up.

I don't know what is your intake voltage in this case, for us, we use SF6 Circuit breakers for all the 11KV system and Vacuum Circuit Breaker for 33KV system.

Hope this information can help you.

Register to Reply
Anonymous Poster
#3
In reply to #1

Re: HT Switchgears

02/08/2009 7:44 AM

Hi . please send me your products tecnical catalogs . tnkyou

email : mohammad_3437@yahoo.com

Register to Reply
Participant

Join Date: Mar 2011
Posts: 3
#6
In reply to #1

Re: HT Switchgears

03/12/2011 3:43 AM

thanks

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#2

Re: SF6 or Vacuum Circuit Breaker?

07/09/2007 12:06 PM

The maintenance of OCB and MOCB is very cumbersome job and need regular attention and are prone to fire hazard . We had major accidents in our substations due to OCB which prompted us to change over to SF6 and VCB in all our modernisation programs and new substations. We have provided SF6 breakers for our 33 KV substations and VCB for 11 KV substations. These Breakers are in operation for the past 15 years. My experience with these breakers are very high rating due to minimal maintenance cost.

The SF6 circuit-breaker, interrupters which have reached the limiting number of operations can be overhauled and restored to 'as new' condition. In practical experience under normal service conditions the SF6 interrupter never requires servicing throughout its lifetime.Vacuum-circuit breaker have a 'sealed for life' design. If your requirement is for 11v KV substation I strongly recommend for VCB . They are cheaper in that voltage range.You can have a comparative study of SF6 and VCB in the following link

http://www.panickker.net/article6.htm

If you are working in India there are good number of reputed electrical manufacturers supplying VCB like Siemens , Jyoti, Cromton, Southern Switcher ,and many more.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#4

Re: SF6 or Vacuum Circuit Breaker?

02/16/2009 8:08 AM

The question is not which one, VCB has a limitation in the maximum voltage/ current that it can handle. You know thet the Vacuum works only on the capacity of the vacuum to quench the arc, But at the moment of break/make, ionisation/ plasma is created by the metals of the contactor, which will self feed the arc.

The Blast of SF6 breaks this plasma by cooling it/ removing the ions and allowing them to re-combine.

Assuming that you are working at alow enugh load and voltage (original being MOCBs) I think VCB is a good enough choice for you.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Anonymous Poster
#5
In reply to #4

Re: SF6 or Vacuum Circuit Breaker?

11/30/2009 2:02 AM

Can I have a list of the SF6 Circuit Breaker manufacturers in India?