Anonymous Poster

An HVAC question

01/29/2008 5:20 PM

A local supermarket had an extensive refit last spring and when it reopened I noticed that in all the refrigerated sections it seemed extremely warm, much warmer than areas of the store that don't have refrigeration to cool the merchandise. The heat is coming into the aisles from the ceiling and it seems that the heat being extracted by the refrigeraters and freezers is being vented back into the same aisles where the refrigeraters and freezers are located. In the summertime this is very uncomfortable because they have air conditioning that is trying to cool the store but the heat from the refrigeraters and freezers are heating it back up in those refrigerater and freezer sections. I would like to ask HVAC engineers if this is a normal way of doing things because it seems to be a contradictory solution to the problem of disposing of the heat. Perhaps they are legally required to vent it back in to the store instead of venting it to the outside atmosphere? The store is in the UK.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: An HVAC question

01/30/2008 5:50 AM

The efficient way is to reject the heat to outside, but that normally requires cheap and noisy roof-mounted units, which neighbours would have the right to object to.

For a silent method of getting rid of surplus heat, it could be used to heat water, which could be offered to the neighbours to heat their homes.

While that would be fine in the cold UK winter, the summertime is the present problem.

Perhaps outside water-cooled tower system, (watch out for Legionnaires disease though), which can be kept fairly quiet, and reject the heated water to a storm-water pipe or channel with permission from the local Council Authority.

I would be asking other HVAC firms in the area if they could improve the situation, and if so at what cost.

Get any offers in writing, of course, and ensure you watch carefully for the "hidden extras" which like to creep into any construction project..

You say <"The store is in the UK">, and I realise that the weather in different parts of the UK is quite variable, so the proper calculations need to be done before alterations are commenced.

The cost of electricity is a major running cost for a supermarket, and any means of minimising those electricity costs would be greatly appreciated by the owners.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Power-User

Join Date: Aug 2007
Location: Knoxville Tenn, Lake Helen, FL
Posts: 191
#2

Re: An HVAC question

01/30/2008 10:54 PM

They probably bought off on someones less efficient design.. now they are stuck with it. I 'think' traditionally (due to the historical evolution of in store refrigeration units.. ) that they would exhaust the heat back to outside or at least an area behind the refrig units where the customers can go, thus making it more comfortable for the shoppers and less comforatable for the workers. SO maybe the kickpanels are missing or not installed correctly, or their inefficienct redesign of their store did not incorporate a back area sealed off from the cooler shopping areas? Maybe they didn't use exhaust ducts to outside to save money, maybe they are not installed correctly.

Mom n pop stores in 1940's did not envision the massive refrigeration we have now.

IE The cold drink cooler just sat there right in the store with no plan for exhaust heat on hot summer days, much like the home refrigerators.

In their case they might be stuck with it now that they have spent their money already on whatever they got.. if not they can install more ac and try to seal off the venting from the heat exhaust from the units to outside or at least to a back area , maybe rearrange how they cold units are setup so that they could all exhaust to same duct to a outside (or at least back area). Sometimes in one story stores its simply a duct UPwards to the roof outside. Zoundz like poor planning !

__________________
Peace begets Synergy which begets Progress!
Reply
Associate

Join Date: Nov 2007
Posts: 53
Good Answers: 1
#4
In reply to #2

Re: An HVAC question

01/30/2008 11:08 PM

I seems to me that the condenser should be installed in a duct that could be selectively vented to the indoors or outdoors...Clint

__________________
Clintb3252
Reply
Anonymous Poster
#3

Re: An HVAC question

01/30/2008 10:55 PM

In the US larger parallel refrigeration systems (typical of supermarket operation) use heat reclaim where the compressor discharge gas passes through a coil in the conditioned air stream for the initial stage of heating. Thermostatically controlled to by-pass the heating coil and go directly to the roof mounted condenser or a water pre-heater to the gas or electric fired water heater. Whatever the store you entered has it appears the controls need some adjustment.

Note: To accommodate a good neighbor policy air-cooled condensers can be esthetically hidden and noise abatement techniques used.

Reply Score 1 for Good Answer
Anonymous Poster
#8
In reply to #3

Re: An HVAC question

01/31/2008 8:18 PM

Here in Florida we use the heat reclaim system to control the humidity in the store. As you said the hot gas is run through a coil in the conditioned air ductwork after the evaporator coil. This puts heat back into the air to allow it to absorb humidity in order to reduce condensation on cool surfaces in the store especially in areas where there are refrigerated cases. This seems counterintuitive to saving energy but it allows the medium and low temperature refrigeration systems to to do less work removing latent heat from the air they are working with and also reduces the amount of ice that forms on those evaporator coils. Balancing the heat reclaim system is difficult to get right at first. Your maintenance contractor should beable to make adjustments to the system and get the air there feeling right. But be patient it takes time.

Reply
Active Contributor

Join Date: Nov 2007
Posts: 18
Good Answers: 1
#5

Re: An HVAC question

01/31/2008 8:00 AM

...at the very least, move the condensing units to the roof to get that heat load out of the building.

Reply
Associate

Join Date: Aug 2007
Location: Cincinnati, Ohio
Posts: 36
Good Answers: 1
#6

Re: An HVAC question

01/31/2008 8:23 AM

I did an extensive remodel of a large chain supermarket in 2006, and we moved a lot of the freezer and medium temp cases around. These units do not have the typical compressor / evaporator coil on the units themselves, as you might see in your home. The cases are freon piped to a compressor room where the, hence the name compressors are located and the coils are located on the roof. The units have fans on them, but do not discharge heat directly from them.

This is for your typical large type supermarket. Now if you are speaking small mom and pop type store then it is possible that the units are self contained and if that is the case then disregard what I said.

May be a HVAC imbalance situation where the zone where the equipment is now located is not sized to handle the load of these freezers/ medium temp cases.

Where is this located, what state? If this is a large chain store I am sure they are aware of the problem and are working on it.

Dave

Reply
Anonymous Poster
#10
In reply to #6

Re: An HVAC question

02/02/2008 10:58 AM

The store is located in SE England and it's a very large store belonging to one of the largest chains in the country. I phoned their HO and asked them why they did their refit this way and they more or less told me to Foxtrot Oscar so I left them to their dumbness. I was just curious is all. Thanks everyone for your input.

Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#7

Re: An HVAC question

01/31/2008 4:17 PM

The reason is that these stores have large areas of refrigerated equipment. The heat removed from the building would have to be replace. Summer time that would be fine but in the winter. That means a bigger HVAC unit to cover the heat loss. The freezers and refrigerated displays are continuously being open and closed. Heat from the isle goes into the freezer say then we take it out and dump it back into the isle. The only adjustment to the HVAC is to make up for the heat of the equipment. The other way the area would become too cold.

You may find a little psychology coming into play here. Hot isle with lots of different ice creams and cold beverages? A lot of which are bought on impulse.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Anonymous Poster
#9

Re: An HVAC question

02/01/2008 10:35 PM

may I suggest a sub cooler and a complete re routing to combine the neareswt coolers ,what the hell the compressors are old anyway

Reply
Reply to Forum Thread 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); Clintb32 (1); Dlingo (1); ozzb (1); Sparkstation (1); TRIPLEBATTERYLIFE (1); Twangmaster (1)