Associate

Join Date: Jul 2007
Location: São Mamede Coronado - Portugal
Posts: 27
Good Answers: 3

Two motors in the same electrical shaft.

01/30/2008 6:01 AM

Can I rewind one motor - just one of the two which work in the same electrical shaft - by using a different copper profile from the original one but assuring the same cross section?

Can I change the existing rectangular wire 3,55x1,25 mm by 6 round wires of diameter 0,95 mm?

I want to change the copper profile, because with these round wires the rewinding is too much easier to execute.

Can this solution be applied? Or, is not advisable because can change a lot the electrical data? Which special attention do I should have?

The two existing motors are exactly identical, of the same manufacturer, and work in the same electrical shaft to assure the same speed at the two motor shafts. Just one of them have the rotor burned and have to be rewounded.

__________________
Best regards, SMCTR
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Two motors in the same electrical shaft.

01/30/2008 7:07 AM

Hello SMCTR

  1. What voltage supply into the motor?
  2. What rotational speed?
  3. Is it the stator, or the rotor which needs rewinding?

There may well be a mechanical reason for the using of rectangular winding, because it is more robust, and resists vibration cracking better than small fine wires.

Advise further with

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Associate

Join Date: Jul 2007
Location: São Mamede Coronado - Portugal
Posts: 27
Good Answers: 3
#2
In reply to #1

Re: Two motors in the same electrical shaft.

01/30/2008 7:48 AM

Hello Sparkstation,

The motors have the following main data: 11 kW, PF 0,80, Stator 380 V - 25 A, Rotor 255 V - 28 A, 50 Hz, 1440 rpm

Just one of them have the rotor burned and have to be rewounded.

In such application the both stators are fed from the same power supply as well as the rotors, which are fed also from the same power supply (but not the same of the stator). The two rotors are synchronized, assuring the same speed at both shafts.

A typical application can be found on the dams, to close and open the "canal lock" (up and down motion). Or, on the coupled cranes, where the two motors have to assure the same motion speeds.

Best regards

__________________
Best regards, SMCTR
Register to Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#3
In reply to #2

Re: Two motors in the same electrical shaft.

01/30/2008 7:42 PM

Well, I never rewind motors. I just burn 'em out and send 'em to the rewind shop in Irwin. But, I have wound transformers with round and rectangular/square wire. Because of the packing factor, you just can't get as much copper in a given space when you use round and the result is heat. Sounds like you might be running these boys a little hot already. I'd vote for the rectangular.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#4

Re: Two motors in the same electrical shaft.

01/30/2008 11:39 PM

Sorry to be that imprecise. But, If those motors share the load, and the setup does not mind, that the motor with the round instead square wire does not pick up more than 80 - 90% of its load, no problem. But, why do you bother with it, instead sending it to a professional rewinder?!? If you are too cheap, I can guarantee, it will cost you.

Register to Reply
Power-User
Hobbies - Musician - New Member

Join Date: Apr 2006
Location: Brigham City, Utah
Posts: 163
Good Answers: 5
#5

Re: Two motors in the same electrical shaft.

01/31/2008 12:41 AM

"Can I rewind one motor"

CAN - Yes

SHOULD - No

__________________
Kindness knows no boundaries.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Two motors in the same electrical shaft.

01/31/2008 1:10 AM

Were they standard Squirrel cage Induction Motors, you might have a problem. Even a slight difference in slip from one to the other will make one of them drag the other as an additional load instead of sharing the load. Rewinding, even using the exact same method and materials, will not likely end up with them being identical any longer, and using different materials / methods almost assures that.

But you apparently have Wound Rotor Induction Motors (otherwise you could not have burned out the rotor windings and would not have rotor nameplate data). WRIMs have the inherent ability to have their output torque tweaked by adjusting the rotor resistance. So all you will need to do is monitor the stator currents of both motors and adjust the rotor resistance of one of them to make them share the load. Do it under full working load however, it may be different than unloaded.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: Jul 2007
Location: São Mamede Coronado - Portugal
Posts: 27
Good Answers: 3
#7

Re: Two motors in the same electrical shaft.

01/31/2008 8:01 AM

Thanks to all of you for your comments.

For such applications – electrical shafts to guarantee the same speed at the two motors – the both motors have to be electrically exactly identical.

So, the copper profile can not be changed, have to be exactly equal to the original. Moreover, during the winding the same mean length have to be maintained to assure the same resistance as the original.

If the copper profile changed from rectangular wire to 6 round wires, the resistance will not be the same, which will cause the motor-set malfunction and the rotor synchronism loss with the corresponding overheating.

The rotor resistance will be different, mainly due to "skin effect" which is proportional to the current and frequency values. Moreover, the torque characteristic will be different, which will cause bigger problems during the motors star-up and stop-down.

An alternative solution for such motors, in case of difficulty to reproduce the original winding design, will be to rewind the both rotors which will assure the same electrical data at both rotors.

__________________
Best regards, SMCTR
Register to Reply
Commentator
Fans of Old Computers - Commodore 64 - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Control Engineering - Process Control Engineer

Join Date: Dec 2007
Location: Idaho, USA
Posts: 79
Good Answers: 2
#8
In reply to #7

Re: Two motors in the same electrical shaft.

01/31/2008 6:04 PM

You could put a limited slip differential in to account for different torques. Otherwise you may have problems with overcurrent when one motor starts acting like a generator.

__________________
It is impossible to defeat a fool in an argument, he wil bring you down to his level and beat you with experience.
Register to Reply