02/01/2008 9:49 AM

What is the max. voltage that is allowed in electric fence as per IEC

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Aug 2007
Posts: 86
Good Answers: 2
#1

Re: Maximum Voltage for Electric Fences

02/01/2008 5:26 PM

Hi nambiathiri,

The max voltage covered by IEC EN61011 1993 is 250V,so I guess this is the max allowed. The energy per belt is limited to 5 or 6 joules dependent on country of use.

Ouch!

The standard covers fences intended for livestock containment,and you would probably need to purchase on line to see the full standard.

I think the criteria are based on a maximum shock to that from from a RCD protected 230v AC supply.

If you trawl a search engine for electric fence manufacturers you may find them quoting bits of the standard and the criteria complied with.

When RCD first appeared I tried to get the manufacturers reps to demonstrate how safe they were,but had no takers.I dont think I've ever had a belt from a RCD protected supply,certainly my body has never tripped one.

Has anyone had a belt which tripped an RCD ? Could you share your experience with us? Im too old an eng to try it and thats my excuse.

Del the cat if youre rubbernecking this how about it,you must have some lives left.

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2
In reply to #1

Re: Maximum Voltage for Electric Fences

02/01/2008 5:58 PM

I had a few belts from them on my grandmother farm but never trip any thing that I know of. They sure ain't fun to walk into in the dark. The system they had pulsed the current. I wish they would have put lights on it though. Real pain to see in the dark. After a while I learn to take one of the farm dogs. They new real well where the line was and would stoop to go under drawing their tail down between their legs.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #1

Re: Maximum Voltage for Electric Fences

02/02/2008 10:21 AM

Yes I have, I tripped out our training lab by touching a mains input pin while teaching a class of our engineers on switched mode power supply repair.....

It did hurt for a split second, but absolutely no damage of any sort except to my pride.

The biggest problem was finding it to reset!! Took 15 minutes.....it took all the mains sockets off and the lighting too!!!

I recently had three installed for the three phases coming into my house.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Aug 2007
Location: Toronto
Posts: 239
Good Answers: 9
#3

Re: Maximum Voltage for Electric Fences

02/02/2008 3:42 AM

Better be careful about the numbers here folks. While the IEC may cover 230 volt units, that refers to input volts. (Sorry, I don't have a copy of that standard). The actual voltage on the fence will be a lot less. For shock hazard, a number of standards limit leakage current to 0.5 mA, but up to 5 mA in some cases. I don't know the fatal current, but Google can help with that. Considering a human body is just a large resistor, we should be able to calculate the max tolerable voltage. Consider that a 12 volt car battery is no shock hazard, but grabbing 120 volts is definitely painful. A telephone ringing circuit is 50 volts I believe and gives a painful jolt. So, I would venture to say that fences would be in that range.

Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#4
In reply to #3

Re: Maximum Voltage for Electric Fences

02/02/2008 7:30 AM

The farm had a back up battery for power failure it was only 6 volts.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
2
Associate

Join Date: Jan 2008
Location: Bath, UK
Posts: 53
Good Answers: 2
#5
In reply to #4

Re: Maximum Voltage for Electric Fences

02/02/2008 8:14 AM

Again the 6V is only a supply voltage. In the UK often the farm electric fences are run off a 12V car battery (or replaced by a 230V~ battery charger giving 12V dc) this is then switched through an auto transformer [no jokes about a DC Transformer] it is the switching off & on of the power that caused the collapse of the field in the transformer so generating the HV output. A slow frequency 'square wave' pulse voltage (not an ac as there is no -ve) This is similar to the Ignition system on a petrol car.

The High Voltage is needed (may be 1,000V dc but it is very low current & therefor power) to get around the long field fence - a long piece of wire has a voltage drop / power loss due to the resistance. This is why our Power Distribution Grids are 11,000, 30,000 & upwards as a high voltage ac is more efficient (although now they are developing very high volts DC distribution systems)

DO NOT put 230~ mains to a cattle fence direct, with or without an RCD, this is only for supply to the system, the output is of low power, low amps but high Volts.

The shock from an RCD will be limited to 30mA for <30mSec. It is quite a shock! Similar to getting a shock from a car ignition but more than a cattle fence.

It is most dangerous is to get a shock across your chest as surgeons can use small amounts of power to stop & start hearts during open heart surgery, a refibulator however looks like a bigger shock - last resort!

I have just Googled IEC EN 61011 1993nd it seems moder fences use mains ac 50/60Hz transformed to around 20,000V (20kV) 50/60HZ.

Register to Reply Good Answer (Score 2)
Commentator

Join Date: Aug 2007
Posts: 86
Good Answers: 2
#6
In reply to #3

Re: Maximum Voltage for Electric Fences

02/02/2008 8:48 AM

Youre right,again, it probably refers to input volts.

I had a sudden flashback remembering repairing a fence pulser which had a test unit with a scale in kV. and the pulser having an automotive ignition coil as its pulse output device.

Googling I found this DEFRA pdf which specifies that voltages above 10,000 should not be used ! This spec also gives the joule requirements for various animals.

www.defra.gov.uk/wildlife-countryside/vertrebrates/reports/Electric-fencing-manual.pdf

Right then,back to your and others inrush/magnetising explanations.

Register to Reply
Associate

Join Date: Jan 2008
Location: Bath, UK
Posts: 53
Good Answers: 2
#10
In reply to #6

Re: Maximum Voltage for Electric Fences

02/02/2008 2:31 PM

I guess things have changed, when I was a kid you could hear the fence pulser clicking, maybe about twice a second. Often a transformer was replaced with a car coil as farmers made do rather than order the replacement part, but that power certainly would not cover the distances mentioned above, things are on a different scale in the US or AUS. etc.! The older units depended on raw high volts to cover the distances, with an old battery as the source is unlikely to kill. It makes sense to use the mains frequency & supply (220/230V~ or 110V~ depending where one is in the world) but then it would be current limited and it seem from previous contributor with practical knowledge up to 10kV.

I know from working with the Electricity Suppliers on earth leaks I was surprised to learn & a farmer will probably have knowledge of this, one has to be careful with four legged animals as a power shock that a human would survive will kill them, it is depending on the voltage gradient from back legs to front [or v/v] If a cow rubs up against a electricity pole with a small earth leak and her rear legs in a muddy puddle >50 or 60 V differential with enough energy will be its last pleasure.

Register to Reply
Active Contributor

Join Date: Jan 2008
Posts: 14
#7

Re: Maximum Voltage for Electric Fences

02/02/2008 10:10 AM

Thje fence charger I use is the largest one that TSC sells.

It has an imput voltage of 120 V and a maximum output voltage of 10,000 V - - - the tester I have rarely goes over about 8,500 V on clear dry days and if it goes below 2,000 V I have an alert that will let me know so I can check and clear it. It is also rated to charge 150 miles of fence ( I only have about 5 miles of fence) and it is rated at 12 Joules - -- In the literature it will not harm even small animals but it will really get your attention if you get into it.

This fence charger is strong enough that I've had cars go thru the fence and the cattle stay in as they will not go near where it was.

Register to Reply
Guru

Join Date: Feb 2008
Location: Milky Way galaxy, Sol solar system, Earth (not Giaha), USA, WA, N.E.
Posts: 691
Good Answers: 13
#9

Re: Maximum Voltage for Electric Fences

02/02/2008 2:26 PM

As a youngster I used to cut asparagrass in the mornings before school. The farmer I worked for had a bull in a small pasture next to the field I worked. I came one morning to find the bull astraddle of the electric fence. Every time the jolt went through he let out a bellow. I shut off the fence and led this once fierce animal quite calmly back into the coral. I have often wondered if he was any good as a bull after that.

__________________
They that do not learn from history and apply those lessons to the present are bound to repeat its failures.
Register to Reply
Associate

Join Date: Dec 2007
Location: Tampa Florida
Posts: 42
Good Answers: 2
#11

Re: Maximum Voltage for Electric Fences

02/02/2008 11:09 PM

I just installed the smallest fence charger i could buy at tractor supply for a boxer dog that used to climb the chain link fence. to go roam the hood

after the first time he put his paws on the wire he never gets close to that fence

that scared me so i called manufacture and they assured me that my Little fencer put out 1000 v pulsed and that it was harmless even there largest fencer putting out over 20k was safe for animals no amps just volt to carry the distance of a few miles or so

__________________
Say what you do,And do what you say
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - Member Engineering Fields - Manufacturing Engineering - Member

Join Date: Jan 2008
Location: Honeydew, South Africa, 26° 04' 50" Lat, 27° 54' 59" Long
Posts: 136
Good Answers: 3
#12

Re: Maximum Voltage for Electric Fences

02/04/2008 12:55 AM

Hi

In SA voltage is 220V input, and 10 000 out/on fence. Battery backup is 12V 7Ah. Delivers a hell of a shock.

__________________
Make The Most Of It.
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Conrads (1); George W. (1); Graebeard (1); JohnBob (2); oldeng (2); ozzb (2); RAYSLENN (1); Shadetree (1)

Previous in Forum: Magnetizing Current, Inductance, Inrush, etc.   Next in Forum: Grounding Pedestal

Advertisement