Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member

Join Date: Mar 2006
Location: Chennai, India
Posts: 312
Good Answers: 3

Electric Insulated Floor Mats in Substations

04/28/2006 9:17 AM

Electric insulated mats are used in front of high voltage switchboards at substations, for safety. Both rubber and PVC insulating mats are used. Since rubber mats are not weather/ moisture proof, is it safer to use PVC?
Request for more information,relevant IEC specifications, on this, if any.

__________________
nvmani
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#1

insulating floor mats

04/29/2006 4:55 PM

If your substation is not weather resistant, neither mat will be safe. I'm not sure if there are IEC or other standards, but there are some users of DC substations that use these. I will try to find a spec.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member

Join Date: Mar 2006
Location: Chennai, India
Posts: 312
Good Answers: 3
#2
In reply to #1

Re:insulating floor mats

04/30/2006 3:15 AM

Further to your comment,I wish to add thatIndoor substation is protected against rains and also provision of positive pressure ventilation and space heaters in switchboards prevent humidity. However,PVC has superior dielectric strength and insulating property,which can provide better safety to operators as compared with Rubber.This needs to be however established through some technical literature,standards. Please help.

__________________
nvmani
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#3
In reply to #2

Re:insulating floor mats

05/11/2006 8:31 PM

Not a lot of detail, but this is the spec text I found for a DC sub: "Provide the switchboard, rubber matting ribbed type with dielectric rating of 40,000 volts, DC and certified as tested and passed, under requirements of ASTM regulations to ensure personnel safety against 8000 volts to ground. Mat shall be continuous length, black color, minimum 1/4-inch thick, minimum three foot (3') wide and extend the full length of entire switchboard. Mat shall be installed full depth of working space." Best I can find, sorry no technical reference.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Anonymous Poster
#12
In reply to #2

Re:insulating floor mats

07/24/2010 7:59 AM

I would to like to throw some light on the fact that if you go through the BIS specifications for Insulating Mats you will not that BIS has not mentioned PVC word in its specifications. Only RUBBER Mats are being used since years all around the world as insulating mat and are still being used. BIS has mentioned "ELASTOMER" which includes "RUBBER" but not "PVC".

Please go through the links below and it will be justified that only rubber mats serves as better insulating Mats than "PVC"

http://www.balmoraleng.com.au/rubber-products/hv-rubber-mats.html

http://www.cablejoints.co.uk/sub-product-details/switchboard-switchgear-matting-electrical-safety-matting-bs921

Hope that the information provided is helpful.

Register to Reply Score 1 for Good Answer
Participant

Join Date: May 2008
Posts: 1
#4

Re: Electric Insulated Floor Mats in Substations

05/29/2008 2:56 AM

PVC mats are the recent introduction for elctrical insulating application for floorings--

they are avalaible as per latest IS 15652 -2006 specifications in India which has referred to IEC 61111-2002-2006 in its FOREWORD. These ELECTROMAT mats are suitable upto 33 KV .Thickness is only 3mm plus they are fire retardant and acid/alkali/oil proof.They are washable and easy to inastall .we offer the same and have installed electromat in sevaral pertrochemical/engineering/pharmaceutical units.they are easy replacement of traditional rubber mats .

Register to Reply
Associate

Join Date: Jun 2008
Location: Chennai
Posts: 31
#5
In reply to #4

Re: Electric Insulated Floor Mats in Substations

06/16/2008 5:17 AM

Hi,

Rubber mat shall be provided for 132kV Control & realy panel aslo with a standard thickness of 8 or 10 mm and 1000 mm wide.

As, indiacted it shall be continous for all the coupled panels.

N.Suresh

__________________
N.Suresh
Register to Reply
Anonymous Poster
#6
In reply to #5

Re: Electric Insulated Floor Mats in Substations

11/25/2008 6:21 AM

Thanking you

Register to Reply Off Topic (Score 5)
Anonymous Poster
#7
In reply to #5

Re: Electric Insulated Floor Mats in Substations

05/28/2009 11:45 PM

There is no IS for rubber mat IS5424 is withdrawn and replaced with IS:15652. There are no rubber mats with IS15652 specification and proper cpri test report.

Register to Reply Off Topic (Score 5)
Anonymous Poster
#8

Re: Electric Insulated Floor Mats in Substations

03/09/2010 1:44 PM

WE offer PVC Insualtion Mat, confirming IS:15652/2006

Contact:09891417740

COMPARISON OF ELECTROMAT WITH RUBBER MAT

COMPARISON

Prevailing Standards

Traditional Rubber Mats

Electromat High Voltage Insulating Mats

New Standard

BIS DOC. 5440 Above 6 mm 3 mm & below 3 mm IS-15652 : 2006
Dislocates / Bottleneck for Trolley Movement, maintenance activities are disturbed Pastable type, Permanently fixed, smooth Trolley movement IS-15652 : 2006
Decays / Poor life Long Life Long Life
BIS DOC. 5440 Highly fire prone and Fire encouraging Fire Retardant IS-15652 : 2006
Absorb Moisture Safe / Moisture Proof Safe / Moisture Proof
Poor Electrical Insulation High Electrical Insulation Properties High Electrical Insulation Properties
IS : 8437 Part I & IEC – 479 clause3.2.33&4.2 Unsafe in case of earth Leakage Current 100% Shockproof Below 10 mA at 66 KV IS-15652 : 2006
Ugly Elegant / Aesthetic Look IS-15652 : 2006
Cleanliness not possible Washable / easy to clean Long Life
BIS DOC. 5440 Clause 3.5.3 Adversely effected by Chemicals associated with electrical industry like Alkalis, Acids, Diesel, Transformer oil etc. No effect of these chemicals Washable / easy to clean

NOTE: IS =

Indian Standards
BIS = Bureau of Indian Standards
Register to Reply Score 1 for Off Topic
Anonymous Poster
#13
In reply to #8

Re: Electric Insulated Floor Mats in Substations

07/24/2010 8:12 AM
Register to Reply Off Topic (Score 4)
Anonymous Poster
#9

Re: Electric Insulated Floor Mats in Substations

05/01/2010 7:09 AM
Dear sir we are in req of Electrical insulated mats as under and as per IS 15652:2006 the attached speck 1.33KV-96 sq mts 2.6.6KV-260 sq mts 3.440V-250Sq mts Please send your offer at the earliest Regards

S.Ravi Shanker Dayanand
M/s S.VENKATA RAO
Electrical Contractors
# 4-54-2,Pl.No.104
Lawsons Bay Colony,
Visakhapatnam-530017
Andhra Pradesh
09246622600
Register to Reply Off Topic (Score 5)
Anonymous Poster
#10

Re: Electric Insulated Floor Mats in Substations

07/16/2010 7:25 AM

Insulating Mat - confirming to IS: 15652:2006

FEATURES AND SPECIFICATIONS:

  1. All Products are ISI marked.
  2. High Die Electric Strength Up to 65 KV.
  3. Insulation Resistance Up to 1494000 Mega Ohm.
  4. Fire Retardant.
  5. Good Mechanical Properties To With Stand Load and Movement of Breaker Trolleys and Associated Electrical Equipment including heavy foot traffic.
  6. No Adverse Effect of Acids, Alkalis and Transformer Oil.
  7. Manufactured Without Any Metallic Derivatives
  8. Suitable For Both A.C & D.C Electrical Installations
  9. Easy To Install, Can Be Pasted.
  10. Water And Moisture Proof, Does Not Decay.

High Tensile Strength and Elongation Properties

PROOF VOLTAGE

Class

Voltage Systems

Thickness

A

Up to 3.3 KV

2.0 mm thick

B

Above 3.3 to 11 kV

2.5 mm thick

C

11 kV to 65 kV

3.0 mm thick

Contact:

PH:9810110578, 0120-2833692

http://www.santoshrubber.com

Register to Reply Score 1 for Good Answer
Member

Join Date: Aug 2011
Location: Gurgaon, Haryana
Posts: 6
#23
In reply to #10

Re: Electric Insulated Floor Mats in Substations

08/29/2011 5:15 AM

Vardhman specializes in manufacturing of various types of rubber sheet. The wide ranges of the sheets are designed in lieu of providing ready solution to every unique demand emerging in the world market.

Vardhman Sheets offers following features-

High temperature Resistance
Abrasion Resistance
High Tear Strength
Acid & Alkali Resistance
Low temperature Resistance
Suitable for water proofing
Electrical shock Proof
With or Without Insertion
Different Patterns

Features :

  • Tests and specifcations also meet BS 921, IEC 61111, ASTM
  • For both A.C. and D.C. applications
  • Di-electric Strength 110KV (110000 volts)
  • AC proof Voltage up to 70 KV
  • Low and Extreme low temprature resistant
  • Acid, Alkalis and transformer oil proof
  • Flame retardant
  • Good Aging properties
  • High Insulation resistant exceeding 1100000 M Ohms.
  • High tensile strength and elogation properties
  • Leakage Current less then 5Ma


Dimensions
Thickness- 0.5mm (1/2") to 50mm (2").
Length-Continuous lengths up to 30000mm (30Mtrs.) or in desired length.
Width-Up to 1200mm (4Feet).

Color-Standard Black, Blue, Red or in desired color.
Packing-Roll Type in Laminated H.D.P.E. Fabric.

ClassMax. Use Voltage (KV)AC Proof Voltage (KV)Di-electric Strength (KV)Thickness
A3.310302.0mm
B1122452.5mm
C3336653.0mm

You can also visit our website : www.rubberindia.in, www.insulatingmat.com
Moreover You can reach us at +91 9971244314/ sales@rubberindia.in

__________________
You can Reach me at +91 9971244314
Register to Reply Score 1 for Off Topic
Member

Join Date: Aug 2011
Location: Gurgaon, Haryana
Posts: 6
#26
In reply to #10

Re: Electric Insulated Floor Mats in Substations

09/02/2011 3:33 AM

Vardhman insulating switchboard matting is considered as personal protection equipment (PPE), it is specially designed for use in front of open switch boards or high voltage equipment. Used in many industrial plants and factories to protect against electrical shocks. Mats conforming to this standard are highly recommended in all kinds of electric sub-stations, transformer rooms, lift machine rooms, switch rooms, electrical panels, ac plant rooms, x-ray plant rooms, lt/ht labs, around bus bars, generator rooms, etc. as a safeguard to the life of human being due to any possible leakage.

For details please visit our website: www.rubberindia.in

CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.


Features :

  • Tests and specifcations also meet BS 921, IEC 61111, ASTM
  • For both A.C. and D.C. applications
  • Di-electric Strength 110KV (110000 volts)
  • AC proof Voltage up to 70 KV
  • and ExLowtreme low temprature resistant
  • Acid, Alkalis and transformer oil proof
  • Flame retardant
  • Good Aging properties
  • High Insulation resistant exceeding 1100000 M Ohms.
  • High tensile strength and elogation properties
  • Leakage Current less then 5Ma
  • On Request We Provide
    • Inspection facilities
    • In house and government laboratory test certificates of the product
    • Pasting and fixing as per requirement

    ClassMax. Use Voltage (KV)AC Proof Voltage (KV)Di-electric Strength (KV)Thickness
    A3.310302.0mm
    B1122452.5mm
    C3336653.0mm


    Dimensions

    FormRolls or Mat
    Length2M / 5M / 10M / 20M
    Width3 Ft.(900 mm)/1M/1.2M"
    Color
    Other Colors as per request
    Red / Black / Blue
    Thickness
    For special outdoor applications, the mats
    can be supplied with higher thickness with confirmation to IS15652-2006
    2mm, 2.5mm, 3mm
__________________
You can Reach me at +91 9971244314
Register to Reply
Anonymous Poster
#11

Re: Electric Insulated Floor Mats in Substations

07/20/2010 5:07 AM

Yes correct and it has been proved, BIS changed the old standard IS:5424 ( insulating Rubber Mats for Electrical Insulation Purposes ) to IS:15652/2006 ( Insulating PVC Mats for Electrical Insulation Purposes).

Register to Reply
Anonymous Poster
#14
In reply to #11

Re: Electric Insulated Floor Mats in Substations

10/29/2010 3:27 PM

Sir, I would like to inform you that the BIS has not mentioned PVC anywhere in the Standard and the name for IS:15652-2006 is "INSULATING MATS FOR ELECTRICAL PURPOSES" and NOT "Insulating PVC Mats for Electrical Insulation Purposes".One can obtain the standard booklet from BIS Office or logon to and download the IS:15652 standard on very nominal charges which will give you clarifications on Insulating Mats for Electrical Purposes. And I request not misguide the readers as this forum is meant for educating the readers and not for misguiding them. PLEASE PLEASE DON'T MISGUIDE THE READERS!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!

Register to Reply Off Topic (Score 4)
Anonymous Poster
#15
In reply to #14

Re: Electric Insulated Floor Mats in Substations

11/28/2010 3:59 PM

Does PVC is safe for Electrical Insulation?

Register to Reply Off Topic (Score 5)
Anonymous Poster
#16
In reply to #15

Re: Electric Insulated Floor Mats in Substations

11/28/2010 10:58 PM

sir, PVC is new for electrical insulating mats. Whereas rubber mats are in use since many decades and are accepted all around the world including US, UK, AUSTRALIA, AND MANY MORE.

Register to Reply Off Topic (Score 5)
Member

Join Date: Jul 2010
Posts: 5
#17
In reply to #15

Re: Electric Insulated Floor Mats in Substations

11/29/2010 5:54 AM

Insulating mats for Electrical Purpose CONFIRMING TO IS: 15652: 2006: CM/L 8385793 (SUPERSEDING IS 5424: 1969) Application: Mats confirming to this standard are highly recommended in all kind of electric sub-stations, transformers rooms, lift machine rooms, switch rooms, electrical panels, AC plant rooms, X-ray plant rooms, LT/HT labs, around bus bars, generator rooms, etc. as a safeguard to the life of humen being due to any possible leakage. Construction-Lining: Manufactured by appropriate vulcanized rubber compound free from any imuling leading to deterioration of insulating properties Surface: Upper surface shall have small aberration to avoid kippry effets. Lower surface shall be plain or could be finished strip resistant. Dimensions: Thickness : 2.00/2.50 mm. : 3.00/3.50 mm Length & Width : 1.00 Mtr. X 2.00 Mtr. : 1.20 Mtr. X 2.40 Mtr. *Continues length on request. *Colors: - As per requirement. Classes & maximum use of Voltage Class Thickness (mm) Tolerance on Thickness (%) A.C. (R.M.S.) (KV) A 2.00 ±10 3.3 B 2.50 ±10 11 C 3.00 ±10 33 For further information, please visit rubberindia.in

Register to Reply Score 1 for Off Topic
Anonymous Poster
#18
In reply to #17

Re: Electric Insulated Floor Mats in Substations

02/14/2011 1:24 PM

Insulating Mat - confirming to IS: 15652:2006

FEATURES AND SPECIFICATIONS:

  1. All Products are ISI marked.
  2. High Die Electric Strength Up to 65 KV.
  3. Insulation Resistance Up to 1494000 Mega Ohm.
  4. Fire Retardant.
  5. Good Mechanical Properties To With Stand Load and Movement of Breaker Trolleys and Associated Electrical Equipment including heavy foot traffic.
  6. No Adverse Effect of Acids, Alkalis and Transformer Oil.
  7. Manufactured Without Any Metallic Derivatives
  8. Suitable For Both A.C & D.C Electrical Installations
  9. Easy To Install, Can Be Pasted.
  10. Water And Moisture Proof, Does Not Decay.

High Tensile Strength and Elongation Properties

PROOF VOLTAGE

Class

Voltage Systems

Thickness

A

Up to 3.3 KV

2.0 mm thick

B

Above 3.3 to 11 kV

2.5 mm thick

C

11 kV to 65 kV

3.0 mm thick

Contact:

PH:9810110578, 0120-2833692

e-mail: s_rubber123@yahoo.com

http://www.santoshrubber.com

Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#19

Re: Electric Insulated Floor Mats in Substations

04/03/2011 10:03 AM

Is it safe to use PVC Insulating Mats, in place of Rubber Insulating Mats for High Voltage Electric Panels?

Register to Reply
Member

Join Date: Jul 2010
Posts: 5
#20
In reply to #19

Re: Electric Insulated Floor Mats in Substations

04/03/2011 11:34 AM

I would to like to throw some light on the fact that if you go through the BIS specifications for Insulating Mats you will not that BIS has not mentioned PVC word in its specifications. Only RUBBER Mats are being used since years all around the world as insulating mat and are still being used. BIS has mentioned "ELASTOMER" which includes "RUBBER" and NOT "PVC".

Please go through the links below and it will be justified that only rubber mats serves as better insulating Mats than "PVC" all around the world.

http://www.balmoraleng.com.au/rubber-products/hv-rubber-mats.html

http://www.cablejoints.co.uk/sub-product-details/switchboard-switchgear-matting-electrical-safety-matting-bs921

Hope that the information provided is helpful.

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: India
Posts: 12
#21

Re: Electric Insulated Floor Mats in Substations

04/12/2011 1:41 PM

Why BIS changed the specification from 6mm to 25mm Rubber Mats for Electrical Purposes to 2mm, 2.5mm, 3mm Elastomer Mats, if both are supposed to be composed of RUBBER.

Register to Reply
Member

Join Date: Jul 2010
Posts: 5
#22
In reply to #21

Re: Electric Insulated Floor Mats in Substations

08/24/2011 1:42 AM

I would like to ask you that you have written "elastomer mats" and BIS has clearly mentioned "it includes rubbers, latex and elastomeric compounds that may be naturalor synthetic or mixture or a combination of both". And PVC is NOT AN ELASTOMERIC MATERIAL it is a THERMOPLASTIC MATERIAL.

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: India
Posts: 12
#24

Re: Electric Insulated Floor Mats in Substations

08/29/2011 12:18 PM

Thermoplastic is also an elastomer, although Plastic may or may not be thermoplast.

TPE - Thermoplastic Elastomer is a class to Plastic which exibit properties of both Plastic & Rubber.

For Reference check- http://en.wikipedia.org/wiki/Thermoplastic_elastomer

Register to Reply
Member

Join Date: Aug 2011
Location: Gurgaon, Haryana
Posts: 6
#25

Re: Electric Insulated Floor Mats in Substations

08/30/2011 4:27 AM
PointsVardhman® Insulating MatsPoly / PVC Mats
Eco FriendlyYes - BiodegrableNon - Non Biodegrable
Physical Properties

Tensile
Elogation

Excellent
High
High
Comparativery Poorer
Poor
Poor
Abrasion RessitaneExcellentPoor
ThicknessAny Thickness - 2mm to 50mmOnly below 3mm
Acceptability
Reliability
Standards
Worldwide - Germany, UK, America
Since 1969 in India
IS - 15652, IS - 5424, BS - 921, ASTM, IEC - 61111
PVC No where
Recentely tries
No
Maintenance
Fixing
Storage
Replacement
Not Required
Not Required
In Any atmospheric Condition
Easy to remove and istall
High
Necessary
Rigidity increases or decrease if not stored at ambient temperatiure
Very typical, involves high time and cost
PricingLessMultiples
Flame RetardanceGoodPoor Being petroleum based product
Fire RiskNo - asc no pastingPasting adhesive material is highly flammable and thus very risky in possible areas of electric spark
Electric InsulationExcellentCompartively Poorer
Ground TreatmentNot RequiredRequired
__________________
You can Reach me at +91 9971244314
Register to Reply
Active Contributor

Join Date: Jul 2010
Location: India
Posts: 12
#27

Re: Electric Insulated Floor Mats in Substations

09/06/2011 7:23 PM

Does any one know the reason why IS:5424-69 standard has been replaced by IS:15652???

Register to Reply
Member

Join Date: Jul 2010
Posts: 5
#28
In reply to #27

Re: Electric Insulated Floor Mats in Substations

09/06/2011 11:41 PM

If BIS wanted to replace Rubber Mats by PVC Mats then why would they mention "Rubber" in the composition clause and not "PVC"???

Guess some people dont have time to go through IS specifications and were busy on google looking for illogical support to their statements totally ignoring BIS specifications. I request them to kindly go through them again and dont put up any comments without having any documentary proofs such as BIS specifications as web links are not acceptable to BIS.

Insuulating Mats are to be manufactured as per BIS specifications not "WIKIPEDIA"

You may put up any govt. lab's PVC Mat Type Test Report and prove the fact that PVC is the right material for Insulating Mats.

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: India
Posts: 12
#29

Re: Electric Insulated Floor Mats in Substations

09/07/2011 7:48 AM

First of all I suggest you to clam down & don't make sarcastic comments!!!

We are here to discuss about Technical issues related to PPE not to make any personal comments. You are taking things personally.

Now, coming back to the topic there is a huge difference between TPE & PVC. You will here be surprised to know even Rubbers come under a class of Plastics but off course they are not PVC because that is a separate class of Plastics.

The reason I have chosen Reference of Wikipedia because it is the most renowned encyclopedia, whose facts & figures are accepted World-Wide needn't to mention over any Local/National standards.

Again please refer to this link to get fair Idea about what I just explained- http://en.wikipedia.org/wiki/Plastic#Fossil-based_plastics

Remember, PLASTIC not always mean PVC, it mean "everything capable of being shaped or molded".

Further clarification/suggestion with Proven facts are welcomed, Your work in terms of BIS standards know-how is appreciated!

Thanks for your time.

Register to Reply Off Topic (Score 5)
Active Contributor
Malaysia - Member - Master

Join Date: Mar 2008
Location: Malaysia
Posts: 21
#30

Re: Electric Insulated Floor Mats in Substations

04/24/2013 11:51 PM

Sirs,

If my substation & switchboard is 33kV, what class & type of mat should I use.

Need to consider phase-phase as working/rated voltage(33kv) or phase to ground (19kV) only.

Appreciate any advice.

__________________
Elect & Instr
Register to Reply
Active Contributor

Join Date: Apr 2011
Location: INDIA
Posts: 10
#31

Re: Electric Insulated Floor Mats in Substations

01/02/2014 6:35 PM
__________________
Anuj K. Jain
Register to Reply
Register to Reply 31 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (13); goGreen (1); Nagarajan.Suresh (1); nvmani (1); Reena Mathur (3); Ried (2); Rubber&Polymer (4); shashiaurora (1); vipul.vardhman (4); Yasser (1)

Previous in Forum: Operating voltage for V V F D   Next in Forum: Who Killed the Electric Car?

Advertisement