Voltage Drop When Load Is Connected

02/04/2008 9:30 AM

We are facing a persistant problem.We have a step down transformer 240v/24v, this is passed through a rectifier bridge to change it to DC and the output is used to control a clatch coil for lifting and lowering a gate. The out put is first passed through a relay . When we disconected the clatch coil and operated the gate to be lifted, the 24volts is available but when we connect the clatch coil back and operated the voltage drops to zero. I managed to swap the clatch coil with another that was in operation and also the relay was swaped but the same problem.

I measured the diode and compared with the one in operation and it was ok. I also checked for any breakage in the supply wire to the coil but the wire is ok. The clatch coil resistance is 8.6 ohms and similar to the one in opertation.

The transformer has tappings for 15volts and 33 volts as well.

Now guys what is the problem, i need help on that.

__________________
holla holla
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Aug 2007
Location: Toronto
Posts: 239
Good Answers: 9
#1

Re: voltage drop when load is connected

02/04/2008 9:49 AM

It sounds like the transformer can't deliver the power the coil needs. I'd check the ratings on both the transformer and the load. The transformer output current/power rating should be higher than the load's input ratings. Both should have the same voltage rating.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: voltage drop when load is connected

02/04/2008 9:51 AM

24V / 8.6Ω ≈ 2.8A. 24V x 8.6A ≈ 206VA

Is a useful AC voltage still coming from the transformer when the circuit is switched on?

  • If the transformer outlet volts (measuring AC) drop away when the circuit is switched on, then there is a fault in the transformer, or it is too small.

What happens when an ammeter is introduced to the circuit? Is there 2.8A in the circuit when the circuit is switched on?

  • If not, and there is still voltage from the transformer when the circuit is switched on, then something has failed in the circuit between the inlet of the rectifier and the outlet terminal of the circuit such that it presents a high resistance, though not an open circuit. Measuring DC volts, chase the circuit through to find the failed component. There will be somewhere near 24V across it with the circuit switched on.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#18
In reply to #2

Re: voltage drop when load is connected

02/09/2008 11:06 PM

Transformer rating needs to be checked. (Should be 100Va atleast)

By the way..PWslack...VA is 24V X 2.8 A = 67.2 VA

just a sight slack.....

Interchanging the transformer would isolate the transformer issues.

Keep us posted....

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#3

Re: voltage drop when load is connected

02/04/2008 11:27 AM

You say the diode is OK - but is it the right way round? Just a thought ...

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#6
In reply to #3

Re: voltage drop when load is connected

02/04/2008 4:49 PM

... I assume you were referring to the diode across the coil (?) ...

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#4

Re: Voltage Drop When Load Is Connected

02/04/2008 12:01 PM

On the 24 V, take a 1000 Ohm, 1 w resistor (or roughly that size) and see if that makes the 24 V go to zero also.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Commentator

Join Date: Dec 2005
Posts: 92
Good Answers: 5
#5

Re: Voltage Drop When Load Is Connected

02/04/2008 3:43 PM

The transformer is too small for the load. It sounds like the load is pulling too many amps to the amount VA supplied, therefor deminishing the voltage to the load. Does the transformer also supply the relay?

Register to Reply
Power-User
Hobbies - HAM Radio - VE6LDS Popular Science - Weaponology - New Member Canada - Member - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Aug 2006
Location: Edmonton, Alberta, Canada
Posts: 284
Good Answers: 10
#7
In reply to #5

Re: Voltage Drop When Load Is Connected

02/05/2008 12:15 AM

What is the distance between the power supply and the load, there could be feed line loss if the gauge of the wire was to small. This may be misleading because as the gauge increases the wire gets smaller in cross section but I think that you know what I mean.

__________________
Semi-retired systems analyst, part time Ham radio operator, full time grandfather.
Register to Reply
Anonymous Poster
#8

Re: Voltage Drop When Load Is Connected

02/05/2008 1:22 AM

Dear Friend.

You have mentioned the input and output voltage rating but not the current rating.

There might be only two problems in the best my knowledge.

Problem1. The load coil current rating is morethan your output current rating from the rectifier.

Solution:

Meassure the out current of the rectifier and check with your coil ratings

Choose the transformer and rectifier current and voltage ratings as per the coil requirment

Problem2: The coil is short circuted.

Solution: change the coil

Register to Reply Off Topic (Score 4)
Guru

Join Date: Jun 2006
Posts: 501
Good Answers: 8
#9

Re: Voltage Drop When Load Is Connected

02/05/2008 4:42 AM

but when we connect the clatch coil back and operated the voltage drops to zero.

I assume this means that the transformer is putting out the correct voltage without load.

How long before the voltage drops?

This transformer may have thermal overloads. The transformer maybe undersized or the thermal senors may have gone bad.

Register to Reply
Power-User

Join Date: Aug 2006
Location: Central Florida in the good old US of A
Posts: 332
Good Answers: 2
#10

Re: Voltage Drop When Load Is Connected

02/05/2008 7:46 AM

Check all your connections to make sure they are clean and tight, and if there are any solder connections, make sure they are sound. I once had the secondary winding lead connection on a stepdown transformer cut our butt for hours when it would deliver the correct voltage open circuited but under load would go to near zero. What we finally determined was that the output cable had momentarily shorted and when it did, it blew the connection off the transformer terminal board but it then touched back and made a pin point solder connection. It would pass rated voltage at no load but would drop it all at that point under load. It was found out when the heavy lift maintenance manager walked on the crane wondering why it was taking us so long to fix the crane (which was rented and supposed to be working the container ship it was boomed down over). He witnessed what was going on for a while, tried some of the same things we had done and was befuddled as us. He finally said he was going to find out what was going on and soldered two leads to each end of a fuse and connected it across the transformer output. Then the system was powered up and the fuse did not blow. He looked behind the terminal board on the transformer and showed us the melted-reconnected lead. We all looked at each other like we were a bunch of dumbasses, but this certainly was a new one for us all. We cut off the wire, resoldered the connection and everything then worked fine.

__________________
Eschew obfuscation.
Register to Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#11

Re: Voltage Drop When Load Is Connected

02/05/2008 10:35 AM

I assume that the system was working before this problem appeared...

You are obviously exceeding the power supply rating. However, if voltage just drop to zero, without any fuse popping or transformer cooking, (you never mentioned that they do...) it might have a current sensor as a protection measure. If so the problem might be right there, and the sensor is faulty or needs adjustments. if they do pop, than did you check the lifting motor for short or stuck gear? Try to by-pass the clutch-relay part and lift the gate and see what happen.

If nothing works, let us know again.

Wangito.

__________________
Never trade luck for skill.
Register to Reply
2
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#12

Re: Voltage Drop When Load Is Connected

02/05/2008 10:58 AM

Come on, colesha, we've been bustin' a gut here trying to give you the help you asked for. Please give us some feedback.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 2)
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#15
In reply to #12

Re: Voltage Drop When Load Is Connected

02/05/2008 2:14 PM

You are very correct. So many are trying to help . The one who asked the question is sitting tight and enjoying. not even bothering to at least give any feed back to the remarks and questions raised by so many.Probably he may not have visited the site again.He has not even told weather this is a problem which came later or is an original one so that people could at least under stands the reason for the problem to provide a solution . Are we wasting our time?

Register to Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#19
In reply to #12

Re: Voltage Drop When Load Is Connected

02/10/2008 7:51 AM

I love this,

Colesha just doesn't give a Sh$%.

Unfortunately, nothing we can do about it. Or, maybe we can? do you have an idea? Does anybody have an idea? How about a Sh$% list?....I am going to put it as a question for all to think about.

Wangito.

__________________
Never trade luck for skill.
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#20
In reply to #19

Re: Voltage Drop When Load Is Connected

02/10/2008 10:21 AM

It's a tricky one. As long as we have an open forum, we have to expect it from Guests - I find I don't try too hard to sort out a Guest problem (unless it really grabs me anyway) - especially if they haven't come back within a day or two.

This one is when someone has registered - so you thing "Hey - genuine guy - let's sort out their problem, and maybe they can contribute something back". We have:

Colisha - from cna (?) -

  • Join date: 4-Feb
  • Total posts: 1
  • Last post: 4-Feb, 2:30pm
  • Last visit: 4-Feb, 3:00pm

Could be extenuating circumstances, so I don't see how we could introduce a list, or really any other measure against registered members. Don't half give me the hump, though!

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Participant

Join Date: Feb 2008
Location: cna
Posts: 2
#21
In reply to #12

Re: Voltage Drop When Load Is Connected

02/29/2008 8:34 AM

Sorry guys i have been having a problem with ma pc and internet,all your suggestions are pretty cool,We had to change some of the wires that were faultydue to old age and had caused the problem especially in the lifting motor connection box had was soo dum due to moisture from an adjuscent ventilation pipe,

thanks alot and sorry.i appologise for that and please accept my appology.

__________________
holla holla
Register to Reply
Anonymous Poster
#13

Re: Voltage Drop When Load Is Connected

02/05/2008 11:26 AM

it may be that your wires may be revers check the polarity and if power supply is to far from gate your wire size to small that is why nothing has blow

nick

qc.ca.

Register to Reply
Active Contributor

Join Date: Jul 2007
Posts: 17
#14

Re: Voltage Drop When Load Is Connected

02/05/2008 1:08 PM

Check for any dry solder or loose contact if not straight away replace the rectifier, it happend some times that the diodes will show correct reading when cold check but will not supply enough current when under load.

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#16

Re: Voltage Drop When Load Is Connected

02/05/2008 9:22 PM

1. Check AC output of transformer ONLOAD.

OK if nearly 20V,

Transformer may be culprit if voltage here is low, othereise <rectifier bridge> is suspected.

2. Have a filter capacitor after <rectifier bridge>?. If not even then it should work, but better to have one at least more than 1000 µF.

Register to Reply
Participant

Join Date: Feb 2008
Posts: 2
#17

Re: Voltage Drop When Load Is Connected

02/06/2008 1:28 AM

hi this is a normal phenomina while using an unregulated dc power supply and solution is use a regulated power supply of 24v. cool

Register to Reply
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); chaterpilar (1); colesha (1); Graebeard (1); Haajee (1); Holmes (1); jmart23 (1); JohnDG (4); krishnalal (1); Kyoto (1); PWSlack (1); shogun7 (1); The_curious_one (1); TVP45 (1); V.I.Abraham (1); wangito (2)