about electrical basic

02/07/2008 6:11 PM

why neutral not required in delta connection?

what is the function and importance of neatral in electracal circuites?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2007
Location: Reno, NV (USA)
Posts: 608
Good Answers: 66
#1

Re: about electrical basic

02/07/2008 6:50 PM

Electricity will only flow when a voltage difference exists. In a single-phase circuit, the neutral is the electrical path to that voltage difference. In a 3-phase circuit, a voltage difference always exists between each phase, so no separate path is required.

__________________
Aequam memento rebus in arduis servare mentem.
Reply Score 1 for Good Answer
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#2
In reply to #1

Re: about electrical basic

02/07/2008 10:18 PM

Neutral will be there at source. The Neutral is Grounded to Zero Volt Earth at source - only to avoid high volage biuldup/spark/arc/flashover.

Actual energy flow is between the 3 phases-- a poetic -symmetry!

Marvel at the Genius that concepted 3 phase Electric Generation/Transmission/use.

Now giant Rockets too go 3 phase for perfect and easiest control of trajectory.

Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3
In reply to #2

Re: about electrical basic

02/08/2008 5:18 PM

Not quite. Consider a step down transformer bank made of three single phase transformers. If the bank is connected delta on the secondary, meant to supply only phase to phase loads, no neutral will be present.

As to grounding... such a bank maybe corner grounded or not grounded at all, in which case, ground fault indication is required by code in many jurisdictions.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Reply to Forum Thread 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

CSM Engineer (1); MUKULMAHANT (1); North of 60 (1)

Previous in Forum: Sump Pump False Alarms: Solution Needed   Next in Forum: Scanner Tube?

Advertisement