Selecting Cables to Transmit 4-20mA Signals

03/05/2008 5:11 AM

Dear Sir,

For Power lines we can select the cable based load current & voltage drop along the line, but What could be the criteria of selecting cross section of incrementation cables to transmit 4 -20mA DC signals and digital signals(on/off status) over a distance of 500 m?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Selecting cables to transmit 4 -20mA signals

03/05/2008 5:30 AM

Mechanical strength of the conductors is the primary consideration.

0.75mm2 is typical.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#2

Re: Selecting Cables to Transmit 4-20mA Signals

03/05/2008 10:07 PM

I join PWSlack and add a few. You can calculate the resistance, and most likely will find not to be a problem. the twisted pair will need to be shielded, If you do not want large noise contamination. And keep it away from power cables.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Selecting Cables to Transmit 4-20mA Signals

03/06/2008 4:09 AM

Quite. Useful additional points.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jan 2007
Location: Berlin (Germany)
Posts: 332
Good Answers: 1
#4

Re: Selecting Cables to Transmit 4-20mA Signals

03/06/2008 4:25 AM

Hi Asitha,

usually you have a configuration like that:

Example:

Given UB = 24V DC
Usource = 2V (thats for UCE, e.g.)
Usignal = 10V (depends on your following input like ADC etc.,
is the maximum voltage at maximum current of 20mA)
Then RL = 10V / 20mA = 500 Ohm
UB = Imax * (Rlead1 + Rlead2) + Usignal + Usource
Rlead = (UB - Usignal - Usource) / (2 * 20mA)
(with Rlead = Rlead1 = Rlead2)

So each of the two leads may have a voltage drop of max. 6Volts and you can
evaluate your required mm².
Having a distance of several hundred meters a twisted shielded wire is recommended.

Regards Uwe

__________________
The sum of intelligence on earth is a constant. And the population grows and grows and .....
Register to Reply
Associate
Hobbies - DIY Welding - New Member Popular Science - Weaponology - New Member

Join Date: Nov 2007
Posts: 29
#5
In reply to #4

Re: Selecting Cables to Transmit 4-20mA Signals

03/06/2008 5:43 AM

In the telecom world we guarrenty the customer 23ma to his phone set. To do this we suply -50Vdc at the Centeral Office so this means we can have a maximum of 1500 ohms in the cable pair if we allow for 400 ohms in the CO wiring, 200 ohms in the phone set and 35 ohms for the house wiring.

Register to Reply
Anonymous Poster
#6

Re: Selecting Cables to Transmit 4-20mA Signals

03/06/2008 3:25 PM

Why not do it without wires, check out www.remotecontroltech.com.

Register to Reply
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); leveles (1); PWSlack (2); Redman46 (1); uweka (1)

Previous in Forum: Selecting Pressure Gauges: Criteria to Consider?   Next in Forum: Distance Measurement

Advertisement