Checking Earthings Without Open Land

03/05/2008 2:57 PM

I visited a factory where there are very old earthings and all covered in the plant area with concrete and plaster. Now there is no open land around it for more than 80 feets. We need to check this earthings. Clamp on meters are the one method to check this kind of earthings. but what if I donn't have clamp on meter? Is there any alternate method?

Pratik Patel

Register to Reply
Pathfinder Tags: Earthing check
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: How to check earthing when no open land around?

03/05/2008 3:44 PM

Hello pret_p

I understand you are properly trained and qualified.

If you are not both, and your Assistant the same, do not attempt this following procedure.

It is easy to do, but you need to check the type of electrical system at your factory, and ensure that no other persons are present, while you do the Earth test this way, have an assistant with you, and both wear rubber gumboots.

I am presuming that your transformer is deltastar connected, with the neutral/star connection at the secondary being earthed properly at the transformer site.

After you have established the transformer connection:

Ensure that no other persons are present, while you do the Earth test this way, have an assistant with you, and both wear rubber gumboots.

I presume your factory Voltage Mains are 230/400V or similar, if not, do not test this way, without further advice.

When testing, take readings quickly, do not allow current to pass through the Earthing Connection Cable for more than a few seconds.

Little equipment is needed:

  1. Assistant, for safety reasons, and to write down the readings
  2. Rubber gumboots for yourself, and Assistant
  3. Tools for disconnection/reconnection
  4. Ammeter
  5. Voltmeter
  6. Standard Heater Element (High Wattage Resistor approximately 30 Ohms

Method:

  1. Turn off the Factory Main Switch
  2. Carefully disconnect the main Earth Connection, at the Main Switchboard
  3. Using a standard heater element, around about 30 - 50 ohms resistance.
  4. Measure the resistance of that element, and write it down
  5. Disconnect carefully at the Main Switchboard, the Main Earth Connection Cable
  6. Connect one end of your high-wattage resistor, (standard heater element), to the disconnected earth connection which runs to the earth electrode/s now hidden beneath concrete and plaster
  7. Connect in series with that, an ammeter
  8. As an alternative to ( 6) above, connect across (In parallel) the standard heater element, a voltmeter
  9. Apply mains voltage to the other end of the ammeter, or if the voltmeter system is used, to the free end of that standard heater element
  10. Current will flow
  11. Take your current or voltage reading quickly, write the reading/s down
  12. Turn off the Power
  13. Remove the standard heater element, meters
  14. Reconnect the Main Earth Connection Cable
  15. Check your Ammeter or Voltmeter readings
  16. Remove gumboots
  17. Now the answer is easy to establish, using Ohms Law, to calculate the actual Earth Resistance at your Factory Site.
  18. Write your report.

The above system of measuring actual earth connection is safe, providing you take careful precautions as mentioned.

I have previously used this method, when no other was available.

Hope that assists you.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
Participant

Join Date: Mar 2008
Posts: 2
#3
In reply to #1

Re: How to check earthing when no open land around?

03/14/2008 2:01 AM

Thanks to provide assistance.

Pratik

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#2

Re: Checking Earthings Without Open Land

03/05/2008 8:27 PM

Hi Sparky. You are braver, than expected, but as I like, you are a DOER!

I have just some caveats. If there are multiple groundings, and others carry significant current when in operation, they will not show up in this measurement, as the whole facility is now without power. I did run into that - it had the very good reason to exist that the facility was big, and the grounding for RF reasons had to be short - so that the facility had multiple groundings. It was fun to watch our Power Engineer solve that! The other note is, that the measurement sez little about the AC voltage on the wire running to the Ground in normal operation. If there are similar grounds nearby, they will induce voltage onto our ground. That is a real bitch to sort out. But for people who feel it it is quite real.

Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

leveles (1); pret_p (1); Sparkstation (1)

Previous in Forum: Will I Get Shocked?   Next in Forum: Why Don't We Break Neutral in AC Circuits?

Advertisement